This is my first time doing a powder coating operation. This is a continuous 
batch system where the product is suspended from a chain system that transports 
it through the process. As part of the process, it is run through a 400 degree 
F (max) curing oven, which is about 20’ x 30’. The construction is all steel, 
the products being sprayed are steel and the only potential combustibles would 
be anything from the uncured powder. The consultants for the company that is 
installing the furnace had evaluated it based on NFPA 86 and determined that 
sprinkler in the oven are not required.   
  

  
Per NFPA 33, this occupancy can be protected as OH2. However, my question is 
does the presence of the unsprinklered oven present a shielding hazard that 
would bring the requirement up to EH2, or does the lack of combustibles make 
this unnecessary?   
  
  
  