We don’t do a ton of these, but we’ve always done OH II to my knowledge.  NFPA 
33 really applies to the spray application area only, which typically we do OH 
II above and inside the spray application area (or under the parts of it that 
obstruct the ceiling as they’re typically not fully sealed enclosures as 
they’re usually similar to what you describe a continuous line) and the parts 
with powder are negligible from a fire hazard perspective.  Arguably the powder 
is a combustible but everything else involved is metal in the curing process as 
far as I’m aware.  Outside of the spray room my only “double check” would be 
that the general type of manufacturing going on wouldn’t require a higher 
density since really it’s just a room with equipment that is part of that type 
of manufacturing occupancy at that point.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]
[cid:[email protected]]

From: Fpdcdesign <[email protected]>
Sent: Tuesday, July 11, 2023 10:30 AM
To: Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] Powder coating oven

This is my first time doing a powder coating operation. This is a continuous 
batch system where the product is suspended from a chain system that transports 
it through the process. As part of the process, it is run through a 400 degree 
F (max)
ZjQcmQRYFpfptBannerStart
This Message Is From an External Sender
This message originated outside your organization.
ZjQcmQRYFpfptBannerEnd
This is my first time doing a powder coating operation. This is a continuous 
batch system where the product is suspended from a chain system that transports 
it through the process. As part of the process, it is run through a 400 degree 
F (max) curing oven, which is about 20’ x 30’. The construction is all steel, 
the products being sprayed are steel and the only potential combustibles would 
be anything from the uncured powder. The consultants for the company that is 
installing the furnace had evaluated it based on NFPA 86 and determined that 
sprinkler in the oven are not required.

Per NFPA 33, this occupancy can be protected as OH2. However, my question is 
does the presence of the unsprinklered oven present a shielding hazard that 
would bring the requirement up to EH2, or does the lack of combustibles make 
this unnecessary?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to