Craig,


I’ve always used 250 gpm per hose valve as a ‘rule of thumb’ but if you think 
of it like you would a test header, NFPA 20 says you can flow 2000 gpm thru 6 
valves, so you should be able to do the same for testing a backflow.



Cliff Whitfield, SET

President



Fire Design, Inc.

940 Summerbrooke Dr

Tallahassee, FL 32312

Ph: 828-284-4772





From: Prahl, Craig <[email protected]>
Sent: Wednesday, July 12, 2023 4:37 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Forward Flow testing valve arrangements



Providing an array of 2.5” hose valves as a test header for testing the 
backflow preventer.  Sprinkler System demand is around 1800 gpm.



So, here’s the debate, when determining how many valves you need do you 
consider each valve capable of 250 gpm or 500 gpm flow?



Nothing in NFPA 13, the debate goes on………….



Craig Prahl | Jacobs | Fire Protection SME – Special Hazards |  
<mailto:[email protected]> [email protected] |  
<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
 www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS





  _____


NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.



--
This email has been checked for viruses by Avast antivirus software.
www.avast.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to