NFPA 13 2021:
16.14.5.1.1

A 2 1∕ 2 in. (65 mm) hose valve shall be provided downstream of the backflow 
prevention valve for every 250 gpm (950 L/min) of flow rate required by the 
system demand including hose allowance where applicable.



Mike Morey

CFPS 3229 • NICET S.E.T. 123677

Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company

7614 Opportunity Drive • Fort Wayne, IN • 46825

direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]

[Image]

________________________________
From: Prahl, Craig <[email protected]>
Sent: Wednesday, July 12, 2023 4:37:01 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Forward Flow testing valve arrangements

Providing an array of 2. 5” hose valves as a test header for testing the 
backflow preventer. Sprinkler System demand is around 1800 gpm. So, here’s the 
debate, when determining how many valves you need do you consider each valve 
capable of 250
ZjQcmQRYFpfptBannerStart
Be Careful With This Message
The sender's identity could not be verified and someone may be impersonating 
the sender.

ZjQcmQRYFpfptBannerEnd

Providing an array of 2.5” hose valves as a test header for testing the 
backflow preventer.  Sprinkler System demand is around 1800 gpm.



So, here’s the debate, when determining how many valves you need do you 
consider each valve capable of 250 gpm or 500 gpm flow?



Nothing in NFPA 13, the debate goes on………….



Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to