Steve-
Thank you. Problem is this place has all gwb ceilings which might be a pain.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Steve Mackinnon <[email protected]>
Sent: Thursday, September 07, 2023 10:44 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Hydraulic Placards

Hey Brian,

I use to do this for a couple companies... I only surveyed the "remote area" 
and main piping back to the alarm valve.

The AHJ is just looking for a replacement Placard, not plans or calcs.

Good luck!
Steven
From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Thursday, September 7, 2023 10:07 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Hydraulic Placards

I'm sure this has been asked before but here goes... An existing apartment 
complex was flagged by the AHJ for not have Riser placards. The building has 
changed owners a couple times so nobody knows who the original sprinkler 
company was. Is it realistic to think the entire system would have to be 
surveyed and enough laid out to run new calcs?

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,tZ2MYiu_03VN6YttyipbbtTwexBHkm1ecWpyOybQO9RapWhvsDYEsJqPc500-SLCW5nFnpR9L9SLXS9UuqQwbP7k-jEc-CAsiKceOeMkvqXnpA,,&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935