Todd,

 

According to NFPA 20, 2013 ed., 4.26, Table 4.26 shows 4” minimum suction.

 

2022 ED. Is the same.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

   117 Old Stage Rd. - Essex Jct., VT. 05452

                 CELL: (802) 373-0638  

             [email protected] <mailto:[email protected]> 

 

From: Fpdcdesign <[email protected]> 
Sent: Saturday, October 7, 2023 10:16 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Distance to fire pump suction

 

I have a system with a 6” backflow preventer, which reduces to 4” immediately 
after. There is approximately 48” of 4” pipe to the suction flange on a 4 x 3 
pump. All elbows are turning correctly. Is this sufficient? Does the 10x rule 
apply to the size of the backflow preventer or the fitting directly attaching 
to the pump?

 