I have always used the suction flange size of the fire pump.  The suction
pipe size and backflow preventer size can vary.  I will look at NFPA 20
when I have a chance and see if I can find a reference for you.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org


Sprinkler Hydraulic Calculations Workshop

AFSA’s three-day, in-person workshop provides a deep dive into the
principles of hydraulics, including the different types of pressure,
calculating changes in pressure (elevation and friction loss), and node
analysis. Click here <https://www.firesprinkler.org/programs/calculations/>
for details and to register.


On Sat, Oct 7, 2023 at 10:52 AM Fpdcdesign <[email protected]> wrote:

> Fire pump is a 250 gpm at 60 psi
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-554-7054  (fax)
> 860-608-4559 (cell)
>
>
> On Oct 7, 2023 at 10:48 AM, <Tstone52 <[email protected]>> wrote:
>
> Todd,
>
>
>
> According to NFPA 20, 2013 ed., 4.26, Table 4.26 shows 4” minimum suction.
>
>
>
> 2022 ED. Is the same.
>
>
>
> Regards,
>
> *G. Tim Stone*
>
>
>
> *G. Tim Stone Consulting, LLC*
>
> *NICET Level III Engineering Technician*
>
> *Fire Protection Sprinkler Design*
>
> *and Consulting Services*
>
>
>
> *   117 Old Stage Rd. - Essex Jct., VT. 05452*
>
> *                 CELL: (802) 373-0638  *
>
>              [email protected]
>
>
>
> *From:* Fpdcdesign <[email protected]>
> *Sent:* Saturday, October 7, 2023 10:16 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Distance to fire pump suction
>
>
>
> I have a system with a 6” backflow preventer, which reduces to 4”
> immediately after. There is approximately 48” of 4” pipe to the suction
> flange on a 4 x 3 pump. All elbows are turning correctly. Is this
> sufficient? Does the 10x rule apply to the size of the backflow preventer
> or the fitting directly attaching to the pump?
>
>
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-554-7054  (fax)
>
> 860-608-4559 (cell)
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to