Micah,

Looking at the spec sheet from Zurn I agree with Travis that you use your 
expected residual pressure while flowing the full system demand of 750gpm. I 
haven’t installed this valve myself, but you’ll notice on the residual pressure 
charts that the bonnet type curve lines stop well below 175psi. So, while you 
may pick a 120psi outlet pressure while flowing 750gpm, the extra play in the 
curve should allow the valve to maintain an outlet pressure below 175psi when 
being tested individually at 250gpm.

Hope this helps!
Eric Rieve, SET
Rieve Fire Protection

From: Micah Davis <micah...@gmail.com>
Sent: Tuesday, October 31, 2023 6:53 AM
To: SprinklerForum <sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Pressure Regulating Valves Residual Pressures

Good morning, Forum!  I hope everyone is having a great week!!

I think I got this right, but someone is questioning me.  I have an automatic 
standpipe with factory pressure-regulating valves (i.e., Zurn 4000).  When 
calculating residual pressures at the inlet of the PRV to be used in the sizing 
charts, the question is, how much water should I be flowing in the system?  One 
suggestion is only flowing 250 gpm at the hose valve you are sizing.  The other 
suggestion is flowing the system demand flow per NFPA 14.  In this case, that 
would be 750 gpm (250 gpm at each of the two most remote hose valves plus 250 
gpm at the top of the only other standpipe).  We are in agreement that the 
calculation should be a source calc to determine the actual pressure provided 
by the system.

Thank you,
Micah Davis
Ferguson Fire Design