If it becomes 4 storey, you might require a standpipe.
Tony

On Mon, Jul 29, 2024 at 7:10 AM <matthew.will...@ferguson.com> wrote:

> I suggest a careful reading of 6.6.6 in 13R.
>
>
>
> While a 13D system ignores storage in attics, 13R does not allow the same
> considerations.
>
>
>
> Appropriately, I think Todd means, if the area becomes a “Story” or not as
> defined in IBC.
>
>
>
> Then it would be treated like a dwelling unit.
>
>
>
> Otherwise, you are running into an area outside the dwelling unit and get
> kicked back to 13 for Design.
>
>
>
> My observation on limited data.
>
>
>
> R/
>
> Matt
>
>
>
>
>
>
>
> *Matthew J. Willis, CWBSP, C.E.T.*
>
> *Ferguson Fire Design, LLC*
>
> D: (602) 337-0721 <http://(602)%20337-0721> C: (307) 236-8249
> <http://(307)%20236-8249>
>
> matthew.will...@ferguson.com
>
>
>
> *From:* Dapr Jones <daprjo...@gmail.com>
> *Sent:* Sunday, July 28, 2024 8:52 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> sprinklerforum@lists.firesprinkler.org>
> *Subject:* [Sprinklerforum] Re: NFPA 13R - Multifamily with attic access
>
>
>
> *Caution:  This email originated from outside of the organization.  DO NOT
> click links or open attachments unless you recognize and trust the sender. *
> ------------------------------
>
> Thanks Todd, much appreciated. Yes, it would still be 13R I agree.
>
> When you say " it would need to be appropriately protected" do you mean
> the attic would need to be sprinklered?
>
>
>
> It would become accessible to the tenant and they would likely use it for
> storage. Does 13R  allow omission of sprinklers only for attics not used
> for storage?
>
>
>
> On Sun, Jul 28, 2024 at 1:42 PM Fpdcdesign <fpdcdes...@gmail.com> wrote:
>
> As far as access, attic access could be allowed unless prohibited by
> Building Code or other restriction (ie zoning approval).
>
>
>
> However, since it is accessible for living space or storage, it would need
> to be appropriately protected. Even then, it could be considered 4 stories
> instead of 3 and it would still be 13R.
>
>
>
> Todd Williams
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-608-4559
>
>
>
>
> On Jul 28, 2024 at 1:31 PM, <Dapr Jones <daprjo...@gmail.com>> wrote:
>
> I'm working on a project that is 3 stories with attic, multifamily
> residential, type VA construction.
>
> We designed the system to NFPA 13R, with no sprinklers in the attic.
> Now the architect wants to add access to the attic for the 3'rd floor
> tenant.
> (note, there's only one tenant on the 3rd fl. of this building)
>
> My question is, can the architect actually allow access to the attic for a
> tenant in a multifamily as far as the building or fire codes are concerned?
> If yes, would sprinklers be required in the attic in this case?
> (considering tenant will likely use it as storage)
>
> Thanks
>
>
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to