I suggest a careful reading of 6.6.6 in 13R.

While a 13D system ignores storage in attics, 13R does not allow the same 
considerations.

Appropriately, I think Todd means, if the area becomes a “Story” or not as 
defined in IBC.

Then it would be treated like a dwelling unit.

Otherwise, you are running into an area outside the dwelling unit and get 
kicked back to 13 for Design.

My observation on limited data.

R/
Matt



Matthew J. Willis, CWBSP, C.E.T.
Ferguson Fire Design, LLC
D: (602) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249>
matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>

From: Dapr Jones <daprjo...@gmail.com>
Sent: Sunday, July 28, 2024 8:52 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: NFPA 13R - Multifamily with attic access

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
Thanks Todd, much appreciated. Yes, it would still be 13R I agree.
When you say " it would need to be appropriately protected" do you mean the 
attic would need to be sprinklered?

It would become accessible to the tenant and they would likely use it for 
storage. Does 13R  allow omission of sprinklers only for attics not used for 
storage?

On Sun, Jul 28, 2024 at 1:42 PM Fpdcdesign 
<fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>> wrote:
As far as access, attic access could be allowed unless prohibited by Building 
Code or other restriction (ie zoning approval).

However, since it is accessible for living space or storage, it would need to 
be appropriately protected. Even then, it could be considered 4 stories instead 
of 3 and it would still be 13R.

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559



On Jul 28, 2024 at 1:31 PM, <Dapr Jones<mailto:daprjo...@gmail.com>> wrote:
I'm working on a project that is 3 stories with attic, multifamily residential, 
type VA construction.

We designed the system to NFPA 13R, with no sprinklers in the attic.
Now the architect wants to add access to the attic for the 3'rd floor tenant.
(note, there's only one tenant on the 3rd fl. of this building)

My question is, can the architect actually allow access to the attic for a 
tenant in a multifamily as far as the building or fire codes are concerned?
If yes, would sprinklers be required in the attic in this case?
(considering tenant will likely use it as storage)

Thanks

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
 To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to