Interesting.   Most FD's understand that it's way better to BYOP.

Okay, so your building FDC is going to connect downstream of the fire pump, and 
the SP system will be supplied by the FDC and pump in question.   If it was me, 
I would branch off of the fire service lateral that's serving the building 
after the (assumed) backflow and before the building service entry, then pipe 
to the dock with its own PIV/FDC and "riser".   The specifics of the how and 
where for those components notwithstanding...

The choice of manual/wet or automatic is solely at the discretion of the 
responding FD, so if they love pumps so much that they'll pump a mid-rise, 
maybe they'll want to pump the dock.   But if they prefer a manual (and we 
heard from a LOT of fire departments that have waterfront operations in the 
task group we formed to create Chapter 13 in the 2019), then you obviously 
don't want to take the water supply from the building standpipe system.  We 
queried fire service about whether there was a need for Class 2 hose boxes on 
marina docks, which was the legacy solution.   We also asked about Class 1 and 
the overwhelming preference was a manual Class 1 system.

The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.


Steve







From: John Irwin <jir...@solomonplumbing.net>
Sent: Tuesday, July 30, 2024 1:34 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe

Local requirement.



John Irwin
Florida Fire Sprinkler Division
Solomon Plumbing

From: Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>>
Sent: Tuesday, July 30, 2024 4:30 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe

Why are the standpipe systems automatic?

From: John Irwin <jir...@solomonplumbing.net<mailto:jir...@solomonplumbing.net>>
Sent: Tuesday, July 30, 2024 1:28 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe

While the building is a midrise, the stand pipe systems are automatic.

John Irwin via mobile device.
Fire Sprinkler Division
Solomon Plumbing
727-282-9243

Typed on tiny keys just for you. Please forgive spelling errors, typographical 
transgressions, and grammatical gaffs.
________________________________
From: Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>>
Sent: Tuesday, July 30, 2024 4:24:22 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe


Not coming out of, but sharing the water supply with the building.   
Simplistically, if your building standpipe system is manual, then you can place 
your FDC on the service lateral and then split to separate building and dock 
systems.   Again, maybe the local AHJ will buy it coming off the building 
system, but if it's pumped for whatever reason, I'm a hard no on the 1,000 gpm 
water supply.   Boat fires are different and so are response strategies, 
including joint response with a fire boat.   If they think they may need 1,000, 
my first pass would be manual/manual and design the water supply so they can 
pump it.



This and the preceding emails on this thread represent my personal opinion only 
and are not intended to represent NFPA or the NFPA 14 technical committee.



Steve L.







From: John Irwin <jir...@solomonplumbing.net<mailto:jir...@solomonplumbing.net>>
Sent: Tuesday, July 30, 2024 1:18 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe



Ok understood. I mean that's an argument for me doing what I want to do with 
the stand pipe system.



John Irwin

Florida Fire Sprinkler Division

Solomon Plumbing



From: Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>>
Sent: Tuesday, July 30, 2024 4:16 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe



2023 Florida Building Code, 8th Edition:

[F] 905.8 Dry standpipes.

Dry standpipes shall not be installed.

Exception: Where subject to freezing and in accordance with NFPA 14.





From: John Irwin <jir...@solomonplumbing.net<mailto:jir...@solomonplumbing.net>>
Sent: Tuesday, July 30, 2024 1:10 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe



Probably not doing that.  =)  Florida Building Code and Florida Fire Prevention 
Code are as far as I dig.







John Irwin

Florida Fire Sprinkler Division

Solomon Plumbing



From: Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>>
Sent: Tuesday, July 30, 2024 4:08 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe



Evuhbody needa reeda IBC ยง905.8.



From: Fpdcdesign <fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>>
Sent: Tuesday, July 30, 2024 1:01 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe



Far am I to challenge Mr Layton on a standpipe question. However, my first 
reaction was why not. Pumps and underground are shared between buildings, why 
not between a building and a marina? Connected to a 1000 gpm pump, it would 
most likely end up automatic wet instead of manual dry.



This opinion is based only on information previously received. There may be 
other circumstances that could make the preferred outcome different.



Todd Williams

Fire Protection Design/Consulting

Stonington, CT

860-608-4559



On Jul 30, 2024 at 3:06 PM, <John Irwin<mailto:jir...@solomonplumbing.net>> 
wrote:

I have a situation I have not come across before. New construction of an 8 
story hotel at the marina. Plans also call for a manual dry dock hose system. 
This will require, one, maybe two hose valves. The dock is located on the side 
of the hotel opposite the street. Civil plans call for an underground run from 
the front of the hotel, all the way around the property, along the sea wall, to 
the dock.



I have a stair well, with a stand pipe in it, about 20 ft from where the dock 
hose valves would need to be.



Can I delete the manual dry hose and feed from the hotel stand pipe system? Or 
even directly from the fire pump would be preferable to all the underground 
work. Can I change the FDC sign on the front of the hotel to include the dock 
hose valves? "Hotel & Dock FDC"



My pump is already 1000GPM. Would adding these hose valves effectively make 
them part of the stand pipe system? Is there any reason in NFPA 13 or 14 that I 
can't extend my stand pipe system out horizontally?



John Irwin

Florida Fire Sprinkler Division

Solomon Plumbing

www.solomonplumbing.net

Cell: 727-282-9243

Office: 248-486-1600 (Corporate)



"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten." - Benjamin Franklin



_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>