If the original installation was approved under permit and the occupancy / use 
isn't changing, I think one could argue that all is well.

From: Dewayne Martinez <[email protected]>
Sent: Monday, October 21, 2024 1:33 PM
To: [email protected]
Cc: Dewayne Martinez <[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] 1976 NFPA storage question

________________________________
[CAUTION: This email originated from outside of the organization. Do not click 
links or open attachments unless you recognize the sender and know the content 
is safe.]
________________________________
I am working on an existing building with the sprinkler systems  designed per 
NFPA 1976 standards.  The systems were hydraulically calculated to a 0.60/3000. 
 Unfortunately, I don't have information as to what was the original storage 
arrangement/commodity classification.  There is one grid which is around 50,000 
sq ft in size.  From what I am reading, a system this large was not allowed 
back then.  The current owner wants to add rack storage (W/O in-racks) of Group 
A, cartoned, non-expanded plastics.  I am going to tell the owner he needs to 
break up the original system into two to be code compliant but just wanted to 
check with the forum first.
Thank you,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[cid:[email protected]]


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to