Typically my first step is to see if the current system is of any value either 
in whole or in part towards protection of the new arrangement.  If not, it 
becomes a demo and reconstruct project.

If the current criteria cannot protect the new rack system, splitting it is a 
moot point.

Craig Prahl | Jacobs | Fire Protection SME - EV, AM, DC, Special Hazards
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Dewayne Martinez <[email protected]>
Sent: Monday, October 21, 2024 1:33 PM
To: [email protected]
Cc: Dewayne Martinez <[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] 1976 NFPA storage question

I am working on an existing building with the sprinkler systems  designed per 
NFPA 1976 standards.  The systems were hydraulically calculated to a 0.60/3000. 
 Unfortunately, I don't have information as to what was the original storage 
arrangement/commodity classification.  There is one grid which is around 50,000 
sq ft in size.  From what I am reading, a system this large was not allowed 
back then.  The current owner wants to add rack storage (W/O in-racks) of Group 
A, cartoned, non-expanded plastics.  I am going to tell the owner he needs to 
break up the original system into two to be code compliant but just wanted to 
check with the forum first.
Thank you,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/<https://urldefense.com/v3/__http:/www.total-mechanical.com/__;!!B5cixuoO7ltTeg!FYjxxS-g45FAuXa9lk9-B37ItGuDNQsuWglv5wLsfn-GzhGYceMjoEvIJFupDi--y9oYg0W6zbvjK9ElwPiir6evoka0$>

[cid:[email protected]]



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to