Agreed. The devil is in the details with that level of wording..


Matthew J. Willis, CWBSP, C.E.T.

Ferguson Fire Design, LLC

D: (602) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249>

[email protected]<mailto:[email protected]>



________________________________
From: John Denhardt <[email protected]>
Sent: Wednesday, October 23, 2024 7:49 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Nut & Bolt / Bottom Joist

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
Keep in mind, “meets UL XXX” does not necessarily it is Listed to that 
standard. Allows verify listings with the listing agency and the manufacturer.


Thanks,

John


John August Denhardt, P.E

Vice President Engineering and Technical Services
American Fire Sprinkler Association
301-343-1457


Are you a member with a technical question?

Don't forget one of the most valuable resources that AFSA provides is Technical 
Reviews by our Technical Services Department. It’s like having an FPE on your 
staff. Visit 
www.firesprinkler.org/technicalreview<https://www.firesprinkler.org/technicalreview>
 to submit a question today! (Member login required.)

On Oct 23, 2024, at 10:46, [email protected] wrote:


It's in the Fire Sprinkler Catalogue..

<image.png>



Matthew J. Willis, CWBSP, C.E.T.

Ferguson Fire Design, LLC

D: (602) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249>

[email protected]<mailto:[email protected]>



________________________________
From: Craig Hanson <[email protected]>
Sent: Wednesday, October 23, 2024 7:38 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Nut & Bolt / Bottom Joist

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
Eric,

the hangers you are showing are not UL listed for fire sprinkler piping.



Craig D. Hanson, CFPS
Fire Division Manager
West Coast Code Consultants, Inc. (WC³)
Meridian Satellite Office
C: 253.225.9977 | E: [email protected] | www.WC-3.com<https://www.wc-3.com>
Teaming With Your Community to Make a Difference


On Wed, Oct 23, 2024 at 7:23 AM Eric Rieve 
<[email protected]<mailto:[email protected]>> wrote:

Brian



nVent Caddy also makes a listed hanger for this situation if you are concerned 
about using common components.



https://www.nvent.com/en-us/caddy/products/nvent-caddy-truss-t-bar-joist-hanger-bottom-chord-0#catalog-applications<https://www.nvent.com/en-us/caddy/products/nvent-caddy-truss-t-bar-joist-hanger-bottom-chord-0#catalog-applications>



Just make sure the structural engineer is ok with the potential loads.



<image001.png>



Hope this helps!



Thanks,

Eric Rieve, SET
Rieve Fire Protection

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to