Currently only piv. Want to remove piv and just install main control valve
at riser. Piv didn't close all the way. Been underground a long time.

On Mon, Oct 20, 2025, 12:36 PM Parsley Consulting <[email protected]>
wrote:

> Tim,
>
> I won't copy what Craig and Tom have said, only to offer my own thoughts.
>
> If the backflow serves only one sprinkler system, the OS&Y valves there
> function as a system control valve.  Indeed §16.9.3.3.5 in the '22 and '25
> editions of -13 specifically permits them to serve as a control valve to a
> sprinkler system provided they are listed for fire protection.  And the
> supervision requirements of §16.9.3.3 would apply as well.
>
> Why are you adding a PIV, and installing a control valve at risers?  Is
> there more than one system?
>
> sincerely,
> *Ken Wagoner, SET*
>
>
> *Parsley Consulting 3002 Younger Drive
> <https://www.google.com/maps/search/3002+Younger+Drive+%0D%0A++++++++++Harrisonville,+Missouri+64701-3909?entry=gmail&source=g>
> Harrisonville, Missouri 64701-3909
> <https://www.google.com/maps/search/3002+Younger+Drive+%0D%0A++++++++++Harrisonville,+Missouri+64701-3909?entry=gmail&source=g>*
> *Phone: (760) 745-6181 *
>
> *Visit the website
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>
> *
>
> On 10/20/2025 10:54 AM, [email protected] wrote:
>
> We are trying to remove PIVs, and install a main control valves at risers.
> AHJ is saying we must have a PIV. Also, we have BFPs before the PIVs. Can
> anyone help me find in NFPA 13 or 24 the section about PIVs?
>
>
> _________________________________________________________
> SprinklerForum mailing 
> list:https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to [email protected]
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]