I would say anything past horizontal is too far. Use vertical sidewalls
instead


Benjamin Young


On Mon, Nov 3, 2025 at 1:32 PM Matt Grise <[email protected]> wrote:

>
>
> We are looking at a dry system for an unheated building. attached to the
> outside of the building is a canopy/roof eave that extends more than 4'
> away and will require sprinklers. We would like to use standard sidewall
> sprinklers as allowed by NFPA 13 2022 8.2.2.2 (4) "horizontal sidewall
> sprinklers installed so that water is not trapped."
>
> The canopy slopes down away from the building, so the sprinkler head will
> need to be angled down to discharge downward along the slope.
>
> Question - how far can you angle a sidewall down to match a slope and
> still have it installed so that water is not trapped?
>
> If you angle it all the way down (like a pendant) - it would trap some
> water and pendants are not allowed. but how far is too far? We have a
> 3.5/12 roof slope, is that ok to match?
>
> Thanks!
>
> Matt Grise
>