I agree with Benjamin, except for using vertical sidewalls.  Vertical sidewalls 
installed outside the building envelope will expose wet pipe to freezing.  You 
will need to use dry horizontal sidewall sprinklers.


From: Ben Young <[email protected]>
Sent: Monday, November 3, 2025 2:15 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: standard sidewall on dry system

I would say anything past horizontal is too far. Use vertical sidewalls instead


Benjamin Young


On Mon, Nov 3, 2025 at 1:32 PM Matt Grise 
<[email protected]<mailto:[email protected]>> wrote:


We are looking at a dry system for an unheated building. attached to the 
outside of the building is a canopy/roof eave that extends more than 4' away 
and will require sprinklers. We would like to use standard sidewall sprinklers 
as allowed by NFPA 13 2022 8.2.2.2 (4) "horizontal sidewall sprinklers 
installed so that water is not trapped."

The canopy slopes down away from the building, so the sprinkler head will need 
to be angled down to discharge downward along the slope.

Question - how far can you angle a sidewall down to match a slope and still 
have it installed so that water is not trapped?

If you angle it all the way down (like a pendant) - it would trap some water 
and pendants are not allowed. but how far is too far? We have a 3.5/12 roof 
slope, is that ok to match?

Thanks!

Matt Grise

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
Disclaimer This email message and all attachments are for the sole use of the 
intended recipient(s) and may contain confidential and privileged information. 
Any unauthorized review, use, disclosure, or distribution is prohibited. If you 
are not the intended recipient, please contact the sender by reply e-mail and 
destroy all copies of the original message. Content cannot be guaranteed to be 
secure or error-free as information could be intercepted, corrupted, lost, 
destroyed, arrive late or incomplete, or contain viruses. The sender therefore 
does not accept liability for any errors or omissions in the contents of this 
message, which arise as a result of e-mail transmission. If verification is 
required please request a hard-copy version.
Disclaimer This email message and all attachments are for the sole use of the 
intended recipient(s) and may contain confidential and privileged information. 
Any unauthorized review, use, disclosure, or distribution is prohibited. If you 
are not the intended recipient, please contact the sender by reply e-mail and 
destroy all copies of the original message. Content cannot be guaranteed to be 
secure or error-free as information could be intercepted, corrupted, lost, 
destroyed, arrive late or incomplete, or contain viruses. The sender therefore 
does not accept liability for any errors or omissions in the contents of this 
message, which arise as a result of e-mail transmission. If verification is 
required please request a hard-copy version.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to