Could you use cellophane bags?

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: [email protected] <[email protected]>
Sent: Friday, February 13, 2026 1:37:49 PM
To: 'Discussion list on issues relating to automatic fire sprinklers' 
<[email protected]>
Subject: [Sprinklerforum] Re: Corrosion resistant concealed sprinklers


Back in the ‘80’s, when VCR’s were new, I supervised the installation of the 
fire sprinkler systems at the EPCOT Center Living Seas Pavilion, a 
5.5-million-gallon fish tank in Orlando, Florida. We had many areas where 
saltwater would cause sprinkler corrosion, and we installed stainless steel 
sprinklers (Central brand at the time), but only pendent and upright sprinklers 
were available in that material. Back then, there were lead-coated 
corrosion-resistant sprinklers on the market, but that’s no longer available 
anywhere.



I’d suggest checking with manufacturers, but I doubt you'll be able to find one 
concealed in stainless steel.  Most glass bulb sprinklers are available with 
Teflon coatings, but I doubt the exposed Belville seal would be protected. I 
suppose you could ask if a wax-coated concealed sprinkler would be available – 
the problem is no one would be able to see corrosion problems behind the cover 
plate when doing visual inspections of the sprinklers in the annual inspections.



Good luck!





 [https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]

Bob Caputo, CFPS

President

American Fire Sprinkler Association

1410 E Renner Rd., Suite 150

Richardson, TX 75082

c:     760-908-7753

p:

214-349-5965 ext124

w:

firesprinkler.org<http://firesprinkler.org/>



New Year, New Training!
Learn design, hydraulic calculations, and ITM with AFSA’s best-in-class 
training! Click here<https://firesprinkler.org/education-training/> to learn 
more and register now for Beginning Design School, Sprinkler Hydraulics 
Calculations Course, NFPA 25 Essentials Workshop, and Advanced Hydraulics 
Calculations Course.



From: Fpdcdesign <[email protected]>
Sent: Friday, February 13, 2026 11:44 AM
To: Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] Corrosion resistant concealed sprinklers



My day for questions. I am working on a project with a therapy pool that will 
require corrosion resistant sprinklers above. The Architect is insisting on 
concealed sprinklers. To date, I have not found anything in manufacturer’s 
literature that matches. Would a clean room sprinkler (concealed sprinklers 
with gasket) provide corrosion resistance?



Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080<tel:860-535-2080> (ofc)

860-554-7054<tel:860-554-7054>  (fax)

860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to