Calculation of In-rack Sprinklers

"The only requirement that I have been able to find in regards to calculating 
in-rack
sprinklers is that for Class IV Commodities stored up to and including 25 ft. I 
must calculate 7 heads on the top two levels (16.2.3.4) and they must discharge 
at not less than 15 psi (16.2.4.4). Does this mean that K-factor and density for
 the in-rack sprinklers do not matter as long as the discharge pressure does not
 fall below the require 15 psi? Or do the in-rack sprinklers have to maintain 
the
same density and k-factor as the over head system covering the same area?"

We have reviewed NFPA 13, 2010 edition as the applicable standard. Our informal 
interpretation is that all the required information is not located in chapter 
16.

The in-rack sprinklers do not match the ceiling sprinklers for any of the 
characteristics
(k-factor, thermal response or discharge). Unfortunately you have to go to 
section
8.13.2 to find the rest of the criteria. As you already said, you have to have a
 pressure of 15 psi. As section 8.13.2 states, you can use a K-5.6 or a K-8.0. 
At
15 psi, these will discharge 21.7 gpm and 31.0 gpm respectively. Both are 
equally
acceptable so why have the larger K-factor? Actually the 2010 edition added an 
even
larger K-factor (the K-11.2).  This is for the storage greater than 25 ft that 
requires
a flow of 30 gpm instead of 15 psi.  At this flow, the required pressure is 28.7
 psi for the K-5.6 and 14.1 psi for the K-8 (and 7.2 psi for the K-11.2). Also 
note
that even when the ceiling sprinklers are standard response, in-rack sprinklers 
can be (I'd say should be) quick-response.  Although it may sound odd since they
 are protecting the same floor area, the in-rack sprinkler criteria is not 
impacted
in any manner by the ceiling sprinkler criteria.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Proposed TIAs for Antifreeze - NFPA 13, 13R, 13D, 25
The following Tentative Interim Amendments (TIAs) have been  proposed to NFPA 
for
NFPA 13, 13R, 13D and 25.  They are being published  for public review and 
comment.
 Comments should be filed with the  Secretary, Standards Council, by July 2, 
2012.
 The links to the TIAs are in blue text below:
NFPA 13
TIA 1066 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13/ProposedTIA1066NFPA13.pdf]
NFPA 13R
TIA 1062 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13R/ProposedTIA1062NFPA13R.pdf]
TIA 1065 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13R/ProposedTIA1065NFPA13R.pdf]
NFPA 13D
TIA 1060 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13D/ProposedTIA1060NFPA13D.pdf]
TIA 1061 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13D/ProposedTIA1061NFPA13D.pdf]
TIA 1067 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13D/ProposedTIA1067NFPA13D.pdf]
NFPA 25
TIA 1068 
[http://www.nfpa.org/Assets/files/AboutTheCodes/25/ProposedTIA1068NFPA25.pdf]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAGgTt06r6zdmclHeA290BmIJnUEav4fL1pmRUagFTEC9gE9jhDHNskSmhIOuQ4H8bKD6OJBSPOKMcSz0iT50FkHE8jyupYtaPfpu6AGuy_uWg==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Printable Copy
PDF Version 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAEnQ7gFf10fFKxuJyXg7qrjY11W1UxBAe4DYfuHqnMsT2a6VSwiYOthU3Qih4kmVbUxOvL8Ng4HroWuJt1adZzRl5z7cq2ltjXolCazDoHHcjvTA8nIn02XmcE5Lknggojpa1klsiFEzz8OLl0YEui2gySFVZU35CRJqU7FeERoyZdi_jBS0NUr-MbOyOVpvGw=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Mark Your Calendar!
Beginning Fire Sprinkler System Planning School 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAHGszfip8wDM34RRwwpk4T9zZDMutDtp7-liESyN6ITMyIuS8Go7BaS6eJpivTluXYA7aDc2sl1Ik1OP0G9KX7shEjdNmzpaH1TlKBiKtB5OLzTpWXhI75VhUz_cOvMoVbfRg8O9mfS7Z7YHnYOzqT7nxQ3QHG0JUbyHlziN2brMg==]

July 23 - Aug. 3 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAHGszfip8wDM34RRwwpk4T9zZDMutDtp7-liESyN6ITMyIuS8Go7BaS6eJpivTluXYA7aDc2sl1Ik1OP0G9KX7shEjdNmzpaH1TlKBiKtB5OLzTpWXhI75VhUz_cOvMoVbfRg8O9mfS7Z7YHnYOzqT7nxQ3QHG0JUbyHlziN2brMg==]
Sold Out!

Nov. 5 - Nov. 16

(click here for details) 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAF2WvqGKEZG_E81-OLrubaOjAD9uxjzAe1sbAOkgzE7jGdgzeOXt39tbH4o3EKNaAneVwjstnUCCIZ1NeFo2HYAB160HBTKR427zM4GH4s9oLbT2vwd_kH0kcTGbrxsAdtuha862HSGOTZTj7IHYW_EIfD0wSnhjfo=]

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAE87tiHjURrU_LvvukuNW7ySk4VmnXyYMlmoupDfURVSqS6ezXWfkg1Vh1AkDTrFmfhDgbGZ00XagqEFLrt0G91Xdg-jtBbTCKmyonXfOeyJrSvNozd0MerqHhUbHp_WQofXrRMq9d8O7B4nCC6Im-3kI7XP_tzatwwZVn-tSPTAXF91hq-yq8_K5MZgXsu9FpRcfaRivRLSHBM0IoYpvww3kfrjdObsz4RlY2WTQPqzn_XU8WBP3bt_9JSQvWa4K3zdk5PhY8T1tIt-MFeYh8W].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAFxL2D_JAJZfYfFgUvsZQt70dNJz6v2QGYA3mAgYZFW--GJXss4O5FnP3SSxwmXS2q2hDdpGPFU1xmkjGuq5SYTuA6Cs1uLqTudxZ9oK64UOiCOTRv9Dg5m_k3K8ONN0Id4MWpLdnorOOAfoD_e287eutDdHbKgkTQ=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAELMSuAuWZr6RBLjHFr5gHG9yxwibiZaBUA6OPGk6zl93KAYOdMWM9w9C4WV8HM0qxBhH79gJn7kTUCPELXxvrDBI2nD-HK60VX72CiwF_xI6ezoyf89LzbuWSL1g7nLuiW6k2JsV5LNeFCCuXTVmUsEAF0UgeX_EQ=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAGgTt06r6zdmclHeA290BmIJnUEav4fL1pmRUagFTEC9gE9jhDHNskSmhIOuQ4H8bKD6OJBSPOKMcSz0iT50FkHE8jyupYtaPfpu6AGuy_uWg==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAE87tiHjURrU_LvvukuNW7ySk4VmnXyYMlmoupDfURVSqS6ezXWfkg1Vh1AkDTrFmfhDgbGZ00XagqEFLrt0G91Xdg-jtBbTCKmyonXfOeyJrSvNozd0MerqHhUbHp_WQofXrRMq9d8O7B4nCC6Im-3kI7XP_tzatwwZVn-tSPTAXF91hq-yq8_K5MZgXsu9FpRcfaRivRLSHBM0IoYpvww3kfrjdObsz4RlY2WTQPqzn_XU8WBP3bt_9JSQvWa4K3zdk5PhY8T1tIt-MFeYh8W]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAE2IRvR9UVne6rI-E6NKaCl_Szjk51oqtI6PcpQ-Ra4kNjZrSGS_1-0LSd8moNMHYWcsFmN3CCUOJkRsKH5vXFlEJq54tZmmtIY8NBTOzelJcTLrd4Si9v9eGOXqWLO-7zdanpIOvs_dg==]
Fire Sprinkler eCampus 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAEnQ7gFf10fFFzECn5dMCMPUT5_1lh41nfFxmnokis4jiqtKqEfD-9J3H84bABJUZZrhcDOVBRwanK80hf4LdpZeeTdgZV2jlLHD059EOxOe6vRr99I96jO]
   Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAGnsRM5mVV0wbW-mNCijf9uJfznGTSQuprGSMmsj5icg1F4qEJvcZYi9XfXgUKRoiXK7oAHH6qC5UeJTy50oxB_mWkXeni300k6nQWVhmiZjHlT9O7CR_tjnhQ2PxyLO8azycmhlW_xRnFU4mEC9SWX]
National  
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAEjaRqTzQ6qycuvsL_YvOvaobO7gk2mZshRPhR1iTSFit1kaLczK3ukIyee8sD_cGn7mfh-0JzNnqW6clqYE1z6iaI3musVAmZV8LWNYxvfeQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAEjaRqTzQ6qycuvsL_YvOvaobO7gk2mZshRPhR1iTSFit1kaLczK3ukIyee8sD_cGn7mfh-0JzNnqW6clqYE1z6iaI3musVAmZV8LWNYxvfeQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAGPGySOqrRzdqRYHcNQFSrITLrRPuRQn_FmXVtLTU8aXitwHUOWWKqeGBYqkmBUabSqp7OQy-bxxNG1Y13wugs8Ck3SBUGU-g5nDt7o0fvTnl0LegoS7k6YhiHagT49Vw26lYAp_VWl4f6FoFe_m_x_]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAGr_PyxVMlamOHEjm8Ci0vZPInJJgHjqZqFSRBPqCqawl5zUW5-DYbhjcgNdAVI7WL-Frpkwyss_pmX_77MggXX_zJMkSBGH7cJwGaann11b_qoJ0QfD_bmGBUsEQhfKm8=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001Xbre5Ll0yAGPC_IEwAPjb6AWHxw1JLpoH4qO0M3eP8cYbKTiuVc23bq6dIofgjaqBt7ov3CuYB4auV06GrgSAGIcUL7UWNyk5IAiKQp5Sxzl-iGh3EiyOkjYqoQZgkY2fZowCTxU6OqG4ClIgnUavWEx7KIk1QGlZTNfi1iiIxo=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1110298042576


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001oLGsbCaE1tPAuQDMvW6xSg%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001oLGsbCaE1tPAuQDMvW6xSg%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to