Sprinkler Protection for Interior Cloth Canopies
"We have some aesthetic canopies in a chain grocery store that are 3 ft wide and
 4 ft in depth.  The canopy surrounds a lowered ceiling area with sprinkler 
protection
above at the roof deck level.  The canopies protrude down from the lower ceiling
 by 17 inches in one scenario and 7 inches in the other scenario.  Are 
sprinklers
required under the canopies?"

We have reviewed NFPA 13, 2010 edition as the applicable standard. Our informal 
interpretation is that sprinklers are not required under the canopies.

Section 8.15.7 addresses canopies but that is for "exterior" canopies on a 
building.
The standard does not address interior canopies but the application is more 
suited
for obstruction rules. Section 8.5.5.3.1 indicates that sprinklers shall be 
installed
under fixed obstructions over 4 ft wide such as ducts, decks, open grate 
flooring,
cutting tables, and overhead doors. Sprinklers are not required under the canopy
 since it is less than 4 ft wide. The fabric that is provided in the awning may 
melt or burn away when the fire plume occurs directly below it. The fabric will 
then allow the fire plume to escape whereby damage to the structure may be 
limited.
Since the heat plume is lost, it would seem to be difficult to activate 
sprinklers
under the awning. As such, it seems reasonable to space the sprinklers to the 
area
of the permanent ceiling and ignore the area under the canopy for combustible 
fabrics.
The upper ceiling sprinklers will address the burning canopy. For fabrics that 
do
not melt or burn away, the sprinklers can be spaced to the outer edge of the 
canopy
observing the ceiling pocket rules and sprinkler obstruction rules such as the 
"Beam
Rule" in Table 8.6.5.1.2 as an example. The application of sprinklers is 
questionable
when fabric ceilings are involved and is beyond the scope of NFPA 13. Thus, the 
issue should be brought to the attention of the engineer on record for the 
project
for direction or discuss this with the AHJ.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5pWXXnNmimxdxpbGSWZE152ZW8L_hrjnv2ais9d5gih7ODQDH387xmbIYELAlnQwCk_xIccdKoXIFbswE10iWu5bgHDc0lkdiflNYfGmN0AsA==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Printable Copy
PDF Version 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5oDDJ_3izU_gTxGJxwijbKpB_fdrVyFd2Q7bO1RguIeawO8FfvmiGqTmBHw8Nhv5vSN8q7f3YlqRguwP6JhrR09tcLOXoB-fEUqNjxxVh1G6vlDdEsuAyAEHelDfvO6D_zAmG9TDEMbOfWjnD18B1j-DNO4UNUMU7wz4I59q4I68J67bl0RYjzXzmEct0LLUeY=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Mark Your Calendar!
Beginning Fire Sprinkler System Planning School 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5qxAo6BYFxEekwgy_lTJahoryZh_g65VFo-QR2B9SOdL7d20ZME_konxa27a7rke5xoGuFfjuNlthNOK174cVrjs3kdfLIheAxGTjWnkL7kTY3xlglg2BhDB9zuV7I8xyohgEl8z-J1jQrAAXx2RkCjIqvpOMrmva0NwxBSm6Ce5w==]

July 23 - Aug. 3 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5qxAo6BYFxEekwgy_lTJahoryZh_g65VFo-QR2B9SOdL7d20ZME_konxa27a7rke5xoGuFfjuNlthNOK174cVrjs3kdfLIheAxGTjWnkL7kTY3xlglg2BhDB9zuV7I8xyohgEl8z-J1jQrAAXx2RkCjIqvpOMrmva0NwxBSm6Ce5w==]
Sold Out!
NEW!Sept. 17-28th
New Class Added

Nov. 5 - Nov. 16

(click here for details) 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5pyb7tZIJomXEtSsQ-aiKzltTg__vbXGhpebhfs40hkd1RO7fIhKBF2vDZOnSy_UqEfRwsAc7NsQny4Ho6GyiW3pWy7BjSP-QZ2yPFl27Qzr_PT-GXBHGqAjGs43SUPY9voUEyVqRJyPFApaFgJsmm4VUwsWRirEGs=]

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5rDANOCJBBrHDM1zp8yt6Vhdcif1odmnjGpKDxREpeh_gF5xj5eTxGwVFnkqrw0ZVrEI7DEa1pOJzdlxMsaBP6I9eWUmeTuaKvggG-8ZTkD-wXsGB6lbuvfQEv3U8rVrSG5sSNJfMb9t7TsFXheR-SlEwlWZFAP0FgrMOAiNSx3OMTAFUfc4I7baQNbUgb1yDZWl27lJTHbCxJvuod19K1PTp7c3_kt_5Omoilwb3WVqAlq3QgfOjAhkkhXb06wLrH4CtULj1plzeGrhuCKwaZG].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5o5WIFJBL0XkUz2d3PfVGq92genxMazZgoue9Mz6LsrIK0vNMa6ELI1MM7wnoXRiMbTsET2Wu4DWA05jf8WozhpLZdoTPhl2cu6dphiGZeaUPlVI9fa7YCyDLf9_n6FAbdsyf-MBvy9ssGaQS9TkRcOJ5FRRYfw3Oo=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5oh7eztGLzxqIUUQrLam7ZlvWW7wQjLHmRujqE65ZQIRCCWwfO9ko3J_JBbpHqCrlNGufZXI_PWkA8nMYNPEOWLjQCn8NybhK_c68rbvidRBeKy0QBvnIeUwBrJxCzs386ScVvKxXGF238pehS3eDgzPtzM_Lg8CRM=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5pWXXnNmimxdxpbGSWZE152ZW8L_hrjnv2ais9d5gih7ODQDH387xmbIYELAlnQwCk_xIccdKoXIFbswE10iWu5bgHDc0lkdiflNYfGmN0AsA==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5rDANOCJBBrHDM1zp8yt6Vhdcif1odmnjGpKDxREpeh_gF5xj5eTxGwVFnkqrw0ZVrEI7DEa1pOJzdlxMsaBP6I9eWUmeTuaKvggG-8ZTkD-wXsGB6lbuvfQEv3U8rVrSG5sSNJfMb9t7TsFXheR-SlEwlWZFAP0FgrMOAiNSx3OMTAFUfc4I7baQNbUgb1yDZWl27lJTHbCxJvuod19K1PTp7c3_kt_5Omoilwb3WVqAlq3QgfOjAhkkhXb06wLrH4CtULj1plzeGrhuCKwaZG]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5p-P75Y_-5vmVaNp44pS-FRLXsmxRTjehdT9x_JdGxqTGuNSSUalNmg9cDY3XWhtE-LF--RUmA84COXwJUHCzx2I92mOPJ_kd-_UNRB_8skpAOBFpHoKZ_CWDWpnHmFwxJ_YFKWKgAGZw==]
Fire Sprinkler eCampus 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5qsnhz3XTF98kFQWWlYiQzScKIx0-UUOWbGi_kE6fqV_DY--dUSrsmWM86numY8MLQA5lcCANQgeO9VOIFpRRvqOoiBNYdY7Udhp9r5HZzZByvkTTSs3XLu]
   Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5o53jehaQ02rbXpEI3JmEdZchhHMCbQ6JErrs5y4jVG9HqdHcce2A5yGlCD-n4d4oGa-GSAUZpQGvCwJfmEyL6pRcV5l6Dy3oKJeQwSiHOyIQsrnd14GA9pBGbINuyVXMuABv3eNCbCOFTh13co73X8]
National  
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5rtYVTQwvuxdrex3ihIVac4JPTvc914qlF26p0OSuCuYL7VbyJyO1ZlKt_GPY-A2ZrzWlBJfm4YL2f719B8FCh1UpmIg4Bhevg9pl3deu_vsQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5rtYVTQwvuxdrex3ihIVac4JPTvc914qlF26p0OSuCuYL7VbyJyO1ZlKt_GPY-A2ZrzWlBJfm4YL2f719B8FCh1UpmIg4Bhevg9pl3deu_vsQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5qDYV-rfngHiU98Zh8pZ4FT9p6-_opvWvMFjcONy7wcWwaAPbrN-5RGV2ux_9kmD4Xf3nzRt7lIidMgYPl3Kl0JMj7Hkjw6PqN1OB0Zgj4S703spQBD7TVciRqKfADSpZPrclUskDOxAS_SNINaFfcz]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5oMSaqj8MIURNFYjs7BB742ytiTJm6pDcHrWEqzy0tTSPUlJeGk7naaCC4EmA4XiIM7ervUuqcWLahTpr95KH5e9wHtyFnOgwKrn730gnrHgwNLcp_N-xyNq4IRX4YUUCg=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001fTnOpEmAU5prd346Ut_tq73rAtbcHXKU-H_2B0qlp8BzbUx85VM9zuQOBUUZ91JAV_R8vsZsmHJ2gmgvzbgejoC7lsi9loOZOSPd7IlFia20rgif_kMj99CdYiedLpkE2WG2Rk14_SOp1MBamYZPfSPMeWwD1k4FRm5qpIodKcw=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1110434382404


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001bhj_KZpjdRulZ7FzbRQfxQ%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001bhj_KZpjdRulZ7FzbRQfxQ%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to