Inspection Forms and NFPA 13 Deficiencies

"We perform NFPA 25 inspections per the scope agreements with our clients. The 
reports
are forwarded to the local jurisdiction for review. The jurisdiction has 
complained
that the inspection forms are lacking information and details. We are being 
requested
by a local jurisdiction to use different forms and also include additional 
information
such as NFPA 13 deficiencies to our sprinkler inspection reports by referencing 
Florida's 69A-46.041 Inspection Requirements for Fire Protection Systems. Is 
this
the intent of NFPA 25?"

We have reviewed NFPA 25, 2011 edition as the applicable standard. Our informal 
interpretation is that NFPA 25 does not require that NFPA 13 deficiencies be 
found
or noted during an inspection of a fire sprinkler system or that specific forms 
have to be used.
The intent of NFPA 25 is only to address maintenance issues with an overall 
objective
of ensuring that the system is mechanically operational. When an inspection is 
conducted
in accordance with NFPA 25, it is assumed that the installation met the minimum 
requirements of the installation standard when it was installed. As stated in 
Section
1.1.3 "This standard addresses the operating condition of fire protection 
systems
as well as impairment handling and reporting and applies to fire protection 
systems
that have been properly installed in accordance with generally accepted 
practice."
The NFPA 25 handbook commentary explains that the intent of the standard is to 
require
inspection, testing, and maintenance of all water-based fire protection system 
regardless
of the quality of the design and installation. The intent of the scope statement
 is to relieve the inspector of the burden of continually re-verifying the 
design
and installation of the system. The scope statement basically means that the 
function
of the inspector is to look for signs of normal wear and tear or aging of the 
system
and components, not to re-verify acceptance criteria. Thus adding a section to 
the
report that the system is correct for the occupancy or hazards may expose you to
 liability issues as the company completing NFPA 25 inspections. However, when 
NFPA
13 deficiencies exists and are known, it may be prudent for an inspector to 
inform
the owner by separate correspondence. Noting these items separately shows due 
diligence
and may ease concerns of liability for the inspecting contractor. The problem 
with
this is noted in the handbook commentary that the inspector performing the work 
is not necessarily trained to make this evaluation, nor is it cost effective for
 such an evaluation to take place each year. The owner and the local 
jurisdiction
should be aware that NFPA 25 does not require NFPA 13 deficiencies to be 
remedied
when found. It only requires that the system be capable of operating properly.

Regarding the jurisdiction's comment on Florida's 69A-46.041 Inspection 
Requirements
for Fire Protection Systems, they appear to take issue with the inspection form 
submitted along with the lack of detail. Number 7 of that document indicates 
that
the contractor or his or her permitted Water-Based Fire Protection Inspector 
shall
complete in detail the inspection reports as required in NFPA 25, as adopted in 
Rule Chapter 69A-3, F.A.C., that outlines all points of the inspection, test, 
and
maintenance as required by the applicable NFPA standards. A copy of the 
inspection
report shall be provided to the owner at the completion of each inspection 
performed.
Number 8 indicates that the inspection report shall include a detailed 
explanation
of every deficiency, and indicate if the inspection is a weekly, monthly, 
quarterly
or annual inspection. The inspection report shall include the name of the 
permitted
Water-Based Fire Protection Inspector, the inspector permit number, the 
inspector's
signature, the date and time of the inspection, and the signature of the owner 
or
the owner's representative. Since NFPA 25 nor the Florida rules give specifics, 
it is focused just on NFPA 25 requirements, not potential NFPA 13 issues. NFPA 
25
does not require any specific forms or minimum information that is to be 
included
on report forms. This is at the discretion of the contractor or owner. Section 
4.4
does reference records that shall be made and maintained. The annex A.4.4.3 
references
sample forms in Section B.2. These forms are not required to be used, especially
 with the increasing use of handheld inspection reporting software available by 
several vendors.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1C8xsSEhsFqFR-Wl16a9wFBGU-EVx1-fdDOdnlUJNMPzu5yV5-4Z6yyyQyecwu099ONhWDC86qZDRmT_mL3W75HEDbVaEDkK6nv3cfVoFwZaw==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Download the PDF Version of
Technical Update
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1ATB-osH-VR2H7iFJ6MOayEzv20tRgIeGDcT57fcT_FW-7v-nzbCLZKGaeNRkXeOAhkzg1ye9PfjzWlosYOz8DSRKyRNRBkFu2u1Hl0I-WJ5LOIJ6MrzEaCDEPRUX7rxLsRnUCfAeqcSbKsUPm3TB4kvlBFmQDaqcFz1CtgRSI8NP1AJN3srxHDc--_lmMWltE=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Mark Your Calendar!
Beginning Fire Sprinkler System Planning School 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1DXGvpKZeo7APfSBJHNsJgUIoQTVl5iIcVaSfoGTxvtgVfEL98cJHGLkxafcRcyqT96qQmCYRJE6KdhEQUdgzcIiwAZ_a9fRAnKaGyhx44amFv0N9-LP5JGUfvmaSqleUObMiY-HY04knyDfA4wQc8_ef8uJt-AhhJo9o-uQjSKcg==]
Last Class for 2012

Nov. 5 - Nov. 16

(click here for details) 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1C_cjoNSmy3v0enZ4ckvyVG3QeyX4_M5jacmDAwgtHujm_WVAbm9i9BkdD77yQ0-XpVmFENYZkunXHn4R3q6CdvqsZX8r4Z11cc70XzXfLdB3QohBTPDA_y9m2yZ-RmNC4lYBV9DA7WZc0X0juIP6_Z8QRJOPAw5Ts=]

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1AW8A1xJvgM62Dmj59_HtMp1C1emh4UC7NkIynvqH8icNE3h6JtJxs6Sg1a_6sPDhANnXmmZXFw6PHXmlItz0E3RTifgXFIWIJgUJP4ZScLEXq-nZHmFLvQWAMpPicNgGY2stZ2RuyDXlQg9oDHYlxj5fE93EnIv03fghwN9SB5KgnhE89GgdGzh9UpAxaQH4q-HwAwLc-hUEX2LHwbC0XWFwAv6JpT2WJnko0badgAFgW7CzKXnjzGveuAkVJTBa4XjQEzCAhgqhR5Imrcpz8i].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1BJUQXmuMOI5kx_b0G9LKFbUhxg_J05pYuCXhRJhZ4FPEIOpJNjq_Z8nqqHtVLyrkPjKkI0cMFg3ijfxVv2a9a_woXVkoSXzYw9k_0xV2Pf4tJKS3bKs5F_]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Antifreeze TIAs
TIAs on NFPA 13, NFPA 13R, NFPA 13D, and NFPA 25 on antifreeze issues. It is a 
single
document covering all of the TIA's and is located (along with all the other 
information
previously released by NFPA) on the NFPA website at:
http://www.nfpa.org/antifreeze 
[http://www.nfpa.org/itemDetail.asp?categoryID=2064&itemID=48038&cookie_test=1]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1AiLJX344otpMfX0b9WXXmdHY1vCUODMCxLXkg05MxB3QDtyxoAbs7RbUbQ4345au8txZ9ddBCXePWMeHwHcCO7rVloxSVHLDGAhMWinIzV0XsWaJSvrbsNlBEIzXSU5mFbNxAF8En5vMHQKpaSrz4XXDvvAwjqh0g=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1AK0arA-Ychd5MyFCMvAtnw4DKoj8C6BJnhksBGQdry8xpJgKPGuQ5h8PuxwMqhsK5MghskwtX35nmz1UWVK9HTYsr_fBfAKMhivY_3jPDnsJwiXYGuixkFzZ4U-qtqj33RAFtHHLfdUHKryFjuhGeMN-s1mngopgU=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1C8xsSEhsFqFR-Wl16a9wFBGU-EVx1-fdDOdnlUJNMPzu5yV5-4Z6yyyQyecwu099ONhWDC86qZDRmT_mL3W75HEDbVaEDkK6nv3cfVoFwZaw==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1AW8A1xJvgM62Dmj59_HtMp1C1emh4UC7NkIynvqH8icNE3h6JtJxs6Sg1a_6sPDhANnXmmZXFw6PHXmlItz0E3RTifgXFIWIJgUJP4ZScLEXq-nZHmFLvQWAMpPicNgGY2stZ2RuyDXlQg9oDHYlxj5fE93EnIv03fghwN9SB5KgnhE89GgdGzh9UpAxaQH4q-HwAwLc-hUEX2LHwbC0XWFwAv6JpT2WJnko0badgAFgW7CzKXnjzGveuAkVJTBa4XjQEzCAhgqhR5Imrcpz8i]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1D7BNaJfqhPkqtd1FlilYn9jrMF4LC0PHpZx7lsVOthOBvDdvWOn9HkcMg88p6Bl_d1p4Bg9YehTWNFYFakODm-X3Y5aQ5mZ1D7TN6Ghwd1oN-hb5gECTxmxN6GcBW9r1-pcASKtEKYbg==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1Aa_LARANizZk6sQBUC5P8FKmxbOHiCaAYyuKshj7ozvpxN4xUUqdzjWnfa989_17sW1q2F9ik6vB5ocWsZ_B_RT7Es_RxVESis9zmBVR2xYKE1V8QCqiA6fi2Zn4fDVuENKEFqzw2459_sikrBht30]
National  
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1Al0NVVH4CCC9J5dPzFYAUpmJDnEUERSFhSaLbvcH8KMXEereIybrExFBHFSPfcoinV-kmlB5jkkhKeojfTdSCr6dP1hN2L5ZQ5yXMnCNl9tw==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1Al0NVVH4CCC9J5dPzFYAUpmJDnEUERSFhSaLbvcH8KMXEereIybrExFBHFSPfcoinV-kmlB5jkkhKeojfTdSCr6dP1hN2L5ZQ5yXMnCNl9tw==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1BuSO6cUuiBuyT5Yi-P5-6XJ-yw3RWq9_WvsBP6qvqrrUXpR0TSq-5KXNQRT5mxguqCgfIQi1Cdj7lXE7Oie-YVsa5C5ruHxTNkoZ-t4iFYNXaM_pTUVqrb4Uz_AVJQUONVJpLEji8l7CT-PNB4a1pt]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1CmOZu1BrOpV-38tGWDAMg7x-qcjs2UKp5uolDfN2lsMGWvYE_hZ745P7Mbxq2QnfggB9p-nlCFpivcu3ZD1hcUTnaqqzGVbAYKrWiHl0_wMCYRh1SJagZOHmHgxV4zTM8=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001NNuGbJ_GP1AaEscChJfOMP9-LHzdgJ570jJO029SQJCZoLIg983Qg7XFId3-C7tdB_Wx80a7GRjc9HxRYyRQ17b0ktcSyY5YmDpBJoTTr7KGv17gCkBWotO_diBBx6aqT1xPTo2-k6PMyLA9vR5PZkeidRKMYDOMJV1N5sLTyMo=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1111224413990


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001Ji1hHWejizIMvxll0rhO2Q%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001Ji1hHWejizIMvxll0rhO2Q%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to