Sprinkler Placement in Attic at Roof Hip

"Under a combustible roof with a 4 in 12 pitch with combustible members less 
than
3 ft on center, Table 8.6.2.2.1(a) requires a maximum spacing of 15 ft parallel 
to the slope (up the slope) and 10 ft perpendicular to the slope (along the 
peak).
 A hip roof always requires a 10 ft by 12 ft spacing with a 20-psi minimum.  Is 
there any way to space sprinklers for a hip roof to avoid the 20 psi minimum 
pressure?"

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that a minimum 20-psi pressure is required for hip roofs when 
using standard spray sprinklers.

The requirements of Section 8.6.4.1.4 and Table 8.6.2.2.1(a) work for gable 
types
of roofs for sprinklers under roof or ceilings in combustible concealed spaces 
of
wood joist or wood truss construction with members less than 3 ft on center and 
slope having pitch of 4 in 12 or greater (attics). There is some confusion on 
how
to apply the sprinkler spacing in the attic near the eaves at the corners for 
hip
or Hipped roofs having pitch of 4 in 12 or greater. Section 8.6.4.1.4.3 requires
 standard spray sprinklers to be installed so that the sprinklers installed 
along
the eave are located not less than 5 ft from the intersection of the truss 
chords,
or the wood rafters and ceiling joists. Literally applying that requirement, the
 sprinkler has to be located exactly 5 ft from the intersection of the wood 
rafters
and joists. Then Table 8.6.2.2.1(a) requires a minimum pressure of 20 psi from 
the
sprinkler since the spacing is 10 ft perpendicular to the slope. An alternative 
to this approach is to use specially listed attic heads.

The issue of sprinkler spacing for hip roofs was brought to the attention of the
 committee for the 2013 edition of NFPA 13. Proposal 13-195 recommended 
increased
spacing at the corner of the eave for hip roofs. The committee rejected the 
proposal
and provided a statement that this was a complex issue that needs time and 
attention
to review and discuss. No technical supporting data was provided to increase the
 spacing and recommended that this to be submitted to NFPA's Research Foundation
 for funding of full-scale fire tests. The Report on Comments provided about the
 same result. Thus one is left with complying with the current requirements of 
NFPA
13 or applying specially listed attic heads. Another option is to get an 
exemption
from the AHJ to allow for increased spacing at the corner of the eave for the 
hip
roof or locate the sprinkler 4 ft from the intersection wood rafters and joists.
 Lastly, it is not uncommon for sprinklers to be within 6 ft of each other where
 baffles are required to prevent cold soldering.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-hBUdtzfzAfl6b5VuKm2tiapX-Y2m1q92t4l5WYzth6MtFjZXMKQ2YXPC4BxwUC_LmsVDLKcsyOviR8ZDLo8UlYSWXrq1XgZlhZc1EIgO6xAhxH7bAqh2xM]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-iqPhSthd64_dDnczrdLNVSctbsO3p3mf3Z1PJoCgNd5CPyF0xvu6duqj95SkC7zifbvWNeg3le939HI-_JmHE3rpp9CA5fGdahYjWKU3EO5fsediQyQF2y7_z2AwKaG8zmVq2P9lPQaptHpytEtcP3d1KGmwq1qxW4O9HogSbwPLs2aEmnwdeYYfXO5HC0JT4=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
May 13 - May 24, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-hdbADVg0DjOGxx7vFoQdBRFpEgzQnWSKvKNd9IErq0ePoj3pjCMiyiYs51JgN1MPaPqXytwmUnqs_kOp7yJaBLvWP9ThBddez0U2JxHmEHkTxkCn-2u2_KIydM4h1Zbn7IVoq2VUTOnvwJ4Pj2VhQGQld5f-AS54fda1FX_oIHnOZXkZyP3WW8cwY4roAuw4af820ZjtlAhsFiUf_7zkr7I7rjqjorQAsFkwEQ4nEDhiRgc7a-ZBEbah21H9Qb0PwIACP4bFpk3gJgZTkTO3wI].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-jEJd5shecaVOJ2UIqCTJP3GXZ6wIWnNm8KoUOwU-LLeWvCWoVygSJPSmFWskwOb2wrljksWBoRspdhALdfimLoIVpM3YC7fbfw8MbMfVhpawxljBS4uboo]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Webinar
Bob Caputo
to Present an
AFSA Webinar on
"Technical Changes from the 2010 ed. to the 2013 ed. of NFPA 13
Part 3 - "Residential Sprinkler Requirements"
Wed., May 29, 2013
Free to AFSA members!
Register Button 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-jVmCsb0jkUSS0s6c5M7F9FdtDWWQ2H-fjTBvwQHmYVuKqb7PGRWvVLzIudKJgXe_qjRk8_OVQHW9wib4XMm1jPXiFB4vYYazrw3V6rmFRHq07K03CWQ4QW72pc3s7yYMw53ZOFCpVHpOD_2DIGaEjnowFQqpqD_5Q=]

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-hdbADVg0DjOGxx7vFoQdBRFpEgzQnWSKvKNd9IErq0ePoj3pjCMiyiYs51JgN1MPaPqXytwmUnqs_kOp7yJaBLvWP9ThBddez0U2JxHmEHkTxkCn-2u2_KIydM4h1Zbn7IVoq2VUTOnvwJ4Pj2VhQGQld5f-AS54fda1FX_oIHnOZXkZyP3WW8cwY4roAuw4af820ZjtlAhsFiUf_7zkr7I7rjqjorQAsFkwEQ4nEDhiRgc7a-ZBEbah21H9Qb0PwIACP4bFpk3gJgZTkTO3wI].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-g_PRfO6o8UCg42bz_AhLmX8djAwT4C0bpZloGMEjYvmO0K94cJineJSCau_rLatlhFj9gakE4mbPSWLjfof4Vrg0kItdoOHyBEt2FIuUkxKU_ssRO2JwpoEmooTdwd5rOydSaHGF2OuqV9QWSF399jguwTv49X9Lg=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-hDiSOaLvw5ZGgywqTgbCfBo6SaqZIoFnyT2dNVGovgd_KCz2dREbokpnmsTYFvbLXPnV0t5-gEZbKyFGrOu_FNtv-cBJ_-aa_O_csRumxmU1k_vroAGvQbbsMr3Uk4DtBGjlPjD6CLesxBcghisK7QWXfco5JtUK8=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-hBUdtzfzAfl6b5VuKm2tiapX-Y2m1q92t4l5WYzth6MtFjZXMKQ2YXPC4BxwUC_LmsVDLKcsyOviR8ZDLo8UlYSWXrq1XgZlhZc1EIgO6xAhxH7bAqh2xM]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-hdbADVg0DjOGxx7vFoQdBRFpEgzQnWSKvKNd9IErq0ePoj3pjCMiyiYs51JgN1MPaPqXytwmUnqs_kOp7yJaBLvWP9ThBddez0U2JxHmEHkTxkCn-2u2_KIydM4h1Zbn7IVoq2VUTOnvwJ4Pj2VhQGQld5f-AS54fda1FX_oIHnOZXkZyP3WW8cwY4roAuw4af820ZjtlAhsFiUf_7zkr7I7rjqjorQAsFkwEQ4nEDhiRgc7a-ZBEbah21H9Qb0PwIACP4bFpk3gJgZTkTO3wI]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-h6bWUo2gVNn-4BjMMiM0i-QCV4iMuOTd1D-5GT7ddQzvgN9MCbveo2uLUZZqHiZ0sVKgPBBfNY_-SPLAYbH2cNLzI_fkyQIuAGbx4B8jb1gNtcxDOYZvvoR-GDZBrbvZ1jt0Ci3MSzk4nOTcia5PZW]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-h9H5KmHwDvFMnoo1XnJHw8GLiiFjL1rA3mCAPs6oHh6YNfSyzBop7u72LMywy4kpfGsiC1j0hZKBKiKgLUBAwlL1T39TZrtg2TO8nrFRyfipP_siLFvNsZgEkXiNFjFFTHPGib26Up7kIQ8jpARuW0sZo6QEfKv-s=]
National  
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-ijQpUhPvhJwRyNLaZgvhvliuURMyGcytFTCtF28bl6d6oA8Dh_No_bS_RWqc4iG-7X086xPqz7z0OhfxB6dmEzmRl1y9SDsBRQYmA3p3Nr7MydBrWt4s_D]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-ijQpUhPvhJwRyNLaZgvhvliuURMyGcytFTCtF28bl6d6oA8Dh_No_bS_RWqc4iG-7X086xPqz7z0OhfxB6dmEzmRl1y9SDsBRQYmA3p3Nr7MydBrWt4s_D]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-hH6mr5_bwyqk6BArx1glopVAEaAe4jGNvkji5qUSKLjMVtRtTj8Z960RNfhNzHS8pS1ERvVReU23lLtIx8BxscU6VJ29_sKayS1NJ7DRlXB1SQNs25WsgOMugf_70UuhaW1mgvhQVgZEa2FoOVJTmd]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-h1E3KDEEoE24WT-FjHg-6OSKkrzI1goZklLrFTsnYlL6p1qv2OD1bOOPlnIq9rvk721PLEeeJZToFeYopDCTNekZO60fsICxw9b5CaxmrBDT0D4_I7tlC2DBpImwqtMKKfaS_KfMwPkQ==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001plpQMWWsI-j-ne6FUn3bg_intelrohT0y-EmUJ2_cxPXfLhKi5lHErEtgj4KoyU3ZV3RDT3TQGMBYMG8t_FhHfSG6rX-_yH3MQ3TDQxSf-5ODylFMp8b4hHEZuKjgmeOkKEFgHCLkg6rEfMtL23NCB8IApoXAOFYQ48elhpCLWsM84r-RzyUGA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1113289182171


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001oWxEozA_HsKWYkH7uTGvOA%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001oWxEozA_HsKWYkH7uTGvOA%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to