American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

June 7, 2013
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 13D - Length of Dead End Branch Lines

"Is there a limitation put on the length of a dead end branch line on a CPVC 
multipurpose
fire protection system designed and installed per NFPA 13D?"

We have reviewed NFPA 13D, 2013 edition as the applicable standard.  Our 
informal
interpretation is that there is no limitation on dead ends for this type of 
piping
arrangement.

Since you are using CPVC piping on this application, there is no limitation on 
dead
end runs that supply fire sprinklers only.  This is illustrated by Figures 
A.3.3.11.3(a)
A.3.3.11.3(b), A.6.3(a), and A.6.3(b).  As explicitly shown in Figure 
A.3.3.11.3(a)
there may long dead end branch lines that can also supply multiple sprinklers.  
The standard does say for listed special fittings, 1/2 in. non-metallic pipe and
 1/2 in. copper pipe in Section 10.4.2.2 for network systems, number 3 says a 
water
distribution pipe that supplies a sprinkler shall not terminate in a dead end.  
This does not apply for your situation since this is not a network system.  A 
network
system is defined in 3.3.11.4 as a type of multipurpose system utilizing a 
common
piping system supplying domestic fixtures and fire sprinklers where each 
sprinkler
is supplied by a minimum of three separate paths.  Thus a single pipe for 
network
systems cannot supply a sprinkler.  A multipurpose piping system is defined in 
3.3.11.3
as a piping system intended to serve both domestic and fire protection needs.  
Since
you are using a standard multipurpose system, there is no limitation on dead end
 runs supplying sprinklers.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Public Inputs
NFPA closed public inputs for the 2016 edition of the NFPA 13 standards.
Other standards accepting public inputs with later due dates:
NFPA 20 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=20] - 
Standard
for the Installation of Stationary Pumps for Fire Protection - Close date 
7/8/2013
NFPA 291 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=291]   
Recommended
Practice for Fire Flow Testing and Marking of Hydrants - 7/8/2013
NFPA 14 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzsxBCacp2dQgdggrjWlRdRh3YmaUCGXmNZ9rn_70brnFukq_e6fl8ZhCO_gtAa-aZxp1wg57UuJcrGAyfwdN_EluMX5UgonaxXuUvk7mdbqMSg==]
- Standard for the Installation of Standpipe and Hose Systems - Close date 
1/3/2014
NFPA 15 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzswlAwKUzFKvtESUzJx086T5ou_7KVoUSypYz-vHusFiui5oRwYEXjWlTPU9I_Y829ckScibVz-ARSdEpvR5qJArmyDPd8YsesWSxcS7gGCVqA==]
- Standard for Water Spray Fixed Systems for Fire Protection - Close date 
7/7/2014
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzszoP1SKumvqpN-9icbYeNA5b3qzDHV-_j8rJTk3GuJF5SlCygK9rWJ5tCkJn60gEwJH2_DyAE78KPV70XVZqeyEJeVkItUE2oits4BUEkpGQrh83MijCWeo]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzsxtyenkJNynM2-sup38dlF4CLX-9hO37Ef7BpxfzUfXTujwyNc3wxl_kGIPYpJFvApw6GNa-YzUqnhh_JzNRGkg37lm3H54O0zml9xRviL46YfwmXWovsyKQAddFGrX_S3XsAumqn6cdab9RRreYG9KfX8dDwKtcqTUE4G4SKY61VkKEm0JiDH0A7hoQ4yWd0c=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
July 29 - August 9, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzsxyC6jYQD2nuhMDI7Nu9isBNwG6dfSfh3wcxmxIw91hymVxKgS8nv9Xvfzj9m2BooHMEBN2To6gG0oGlGkKz8VOqKQjq1kcdgTKSXUsJJz9_GJ0WVsQ5qjIIb74ZzhSePKl1y8Rc-sVfwjEZekycTZHq0YPK7UYfO1jAB9AeMPBKgu_TQotuXTnZg9XBZIgbIzhhSHHvRuQhQIZgSelIa5Q_COZRQoidC2QXsvVIqydurzye56t0niuCLU6vGnGVlBrJyzaEdQ9005MP78NFXN0].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzszBn2wzN-AnGoOUujY38g0Tk5krnhSY5GevncMBXJDo-pLRITKQQKpQ_6peL6f2JgGpQtiFpWrSYj8NtrORlEmsX3khCzudQYzImudJVVDAC1x9LUo2NLdr]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzsxY_R6G3zuuYL_eUVQITQVU1i7pi2yocJVs5Zrb3vFsJHFMsxxcSsVSKrOJwHRyndUhCAj3slmN89_ONdaW4ACCzky2ZZI10qm1DsrlsYIl3slv0gsLf3H4wi5w4KmgeQyd43gNbEPLlpR1kbp8No6iYq8dJpDcw7U=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzszqGqjYWIQv9PQCWLSSThjx-OdSdohsbS5OhRg5HrzgRbYMhT7hEpfYza2K3SvIAHAHTWD_DUSKe6cRDE18LoBBAXoIC_hFftDSFXcTTbzDnOaamQUXzXFIwAg3bB-jqIqnSPAoxTBITRPSojbFxd1XDCo9nCXZqGA=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzszoP1SKumvqpN-9icbYeNA5b3qzDHV-_j8rJTk3GuJF5SlCygK9rWJ5tCkJn60gEwJH2_DyAE78KPV70XVZqeyEJeVkItUE2oits4BUEkpGQrh83MijCWeo]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzsxyC6jYQD2nuhMDI7Nu9isBNwG6dfSfh3wcxmxIw91hymVxKgS8nv9Xvfzj9m2BooHMEBN2To6gG0oGlGkKz8VOqKQjq1kcdgTKSXUsJJz9_GJ0WVsQ5qjIIb74ZzhSePKl1y8Rc-sVfwjEZekycTZHq0YPK7UYfO1jAB9AeMPBKgu_TQotuXTnZg9XBZIgbIzhhSHHvRuQhQIZgSelIa5Q_COZRQoidC2QXsvVIqydurzye56t0niuCLU6vGnGVlBrJyzaEdQ9005MP78NFXN0]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7Gzsy3f-7Ml9ihbQVz8EyxQD9VNkF_LTm10u5HcedvDCuzhTEd_8zgZ-tIncPF9sJHiAujLNmOIA85JF7N-ubiFj2xXjOKE6CEdJoYCh8soWLYuKRdrVXHz93DX-0JTxF-VpoJbUDoVneIs4kYfQmcblXb]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzsydSA9T5Jn8ljK0hdDhzyZSE6poIT9JGRY9MO353QMO08YsWQ0igY1CptZyEPxKYAnArsp5eZyCY9hepCEyyBeyBBxsMd2TBkg_lDkDWI_etqZ24BFr6NKvkJ0h9I8B2IENC2YOfNrpyazRwlCn4zFVW3nJmYhflPU=]
National  
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzszUjuriVmBbdJkt1m3QVr_TO_8CRxCWWP8ay8pQxrH84t7ZpZjmn8wo7hiHlwP5NliSa3zRhHqTkssNETybBDR1MNTOegdlvQJc5ABJ6HgK6f-kZkL1fHln]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzszUjuriVmBbdJkt1m3QVr_TO_8CRxCWWP8ay8pQxrH84t7ZpZjmn8wo7hiHlwP5NliSa3zRhHqTkssNETybBDR1MNTOegdlvQJc5ABJ6HgK6f-kZkL1fHln]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7Gzsx2KcSMrKDHGKrRAYJRlPXREkwDrmqhe2sLXXcZ04tw_OM7jAjqyvMIsWJJaNtNggFoxEUJFGDxDk5CU8GOUd9MS6t34FSyh8KTpSl61h4NMM9ul6_o-BH4o80PGawfWQKQf7GtUMu1t0unQ3sf5jjW]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzszgWRjBLBIlEaziqMliA_GFwIop8rZiGpybsWZ3vH-WRZrFhfWa4SoO5NKBZAOM236SiEKPn1KS42MQJfXe0t-hf18eIdYVxMgKdacZ1tYKRUecIjWculnoqIUo8yxeVyBp597_6eDlKA==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001wQFT-p7GzswdbH6mRYoBfVWLi4MukyLaRabLctAHBc-uFvb2fQeV2LjBAtGR4-QqC_H8UPNRr_spDDXpHmg9fq5_h5hUOQiifxdPAOYcXLwC07s_3ls0w3FFrwAnCtR1vL8uroh9yhLAx3lYoHXJInUbemOw8kiblKztWtJS1ASYtU3GMeSmQA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1113710681833


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001N48Mlb3PXaoKouBSbqJ0bg%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001N48Mlb3PXaoKouBSbqJ0bg%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to