American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

July 3, 2013
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Return Bends for ESFR

"Is section 8.15.19.2 applicable to ESFR pendent sprinklers connected directly 
to
branch line piping on a wet pipe system fed from a raw water source?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that return bends are not required when using ESFR 
sprinklers.

A clarification was added to the 2013 edition as Section 8.15.19.5.  This says 
that
return bends shall not be required for wet pipe systems where sprinklers with a 
nominal K-factor of K-11.2 or larger are used.

The Sprinkler Systems Handbook commentary says that the purpose of return bends 
is to prevent collection of sediment in drop nipples.  Return bends should not 
be
taken directly off the bottom of branch lines in wet pipe sprinkler systems, 
particularly
where the systems are supplied from water sources that could contain excessive 
sediment.
 Return bends are not necessary on wet pipe systems that use a potable water 
supply.
 In this regard, water supplied from a swimming pool is not considered a raw 
source
requiring return bends.

The substantiation used for this new section in the 2013 edition said that the 
requirements
for return bends predates the development and use of larger orifice sprinklers 
including
ESFR and CMSA sprinklers that have large enough orifices where sediment should 
not
be problematic.

FM Data Sheet 2-0 dated April 2011 has a slightly different approach to NFPA 13 
regarding return bends.  Section 2.1.3.1.4 is for non-storage sprinklers and 
Section
2.2.3.1.4 is for storage sprinklers.  Both say to provide individual return 
bends
for all K11.2 or smaller pendent sprinklers that are supplied from a raw water 
source,
mill pond, or from open-top reservoirs.  The size of the return bend can be 
either
the same size of the branch line that feeds the return bend or one pipe diameter
 size smaller, but not less than 1 in.  The storage sprinkler section clarified 
to also provide return bends on vertical pipe drops supplying in-rack sprinklers
 from these types of water sources.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwluq5kXis5E3AwrqFOBhjfwiWUcIwi_R1rvO6GtXwxR6TuPMjWFG9rpQp9WRYrs_Bb0w9Z-LqG0boXOocAqO-Eb5V4Qm0f7FWsfrF71vDxLWnNdSi1MDGg3]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwlGtE68SY2mD64t3JgCp_0QLGqHs-iOusYETVQ6q16OfLNkWjgrdOcndB0KechGoAO7Ngf6WwnCA1Xsw6bcXHIY_Qy02EWSJmgwvrknaWjqN-OsOgnBlgEK59SBAaJA9hDjCgZIs2LdmJO1rLZB5UAwxnFkNcwxquW0KV8MsVSIMkE8yLHaLyfQ2VYeLtH17B0=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
July 29 - August 9, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwkR6kTGxxNTM0oOwJx0tEHxAg-XBtXRYYY-OJI2C5qX1kn34HVPFTq4RRy6dM5YGgV3vZ16eT5VCGF1zyt-qtZg1UDQGE68L-HWjSsd-I7oL4BQVRnYZ9YNN2-hzPcjFJzDvt6sk0i-3ata-5QQRJp7o3lHz3cMLeCEL1PAGOb7xVd5-qJxtwLOWtMKuDJNcTrui3A3cG3B1NAOyx_oR3sbXAkJSDB5np9oNCtYz20lE5oraLTCuC-w5f__vxJx3HmIepNZjvWkFFmfefiNnXhv].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwmcR2vm6Jb45ecGvIZAPb4Q9K-YJLf-6JIO9gWCq4EpeJu4E1OlNG76ZtJpPDXglmywgxuaxqZYWSovRU480ukDigUCrYnEm6v6W7a9wtPKoNieBNrSatlB]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwk86W8ej_1N2U7bQXN1q_2SjvOOdLGK3Gekjs7M3VRIa8tuwOYRlKdxyV36rUdDeEFqxFXVMOgYYOZhN22bVbU8laEPXAt6ZNyDbDgadfjuR7DGOFrlx7MJ8QNhaHVdLjSTaK8RDYZLBXd9MB7duiS08t7v-dYGRpw=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwnHGhL-l5SjaulH_SmCMTSggGWgjhMlu89X12R4RsI9Y4fythyTgCGNKbeCuq_Wx7q9u4j0Rx7vBiu3Ht0oOfb5Mf42RNc5kIcY4581nehVmN9y86PYxVa4o1LXRqqaIwqELel_k951-6EZaEHH4RjVuHGOFmKbvxI=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwluq5kXis5E3AwrqFOBhjfwiWUcIwi_R1rvO6GtXwxR6TuPMjWFG9rpQp9WRYrs_Bb0w9Z-LqG0boXOocAqO-Eb5V4Qm0f7FWsfrF71vDxLWnNdSi1MDGg3]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwkR6kTGxxNTM0oOwJx0tEHxAg-XBtXRYYY-OJI2C5qX1kn34HVPFTq4RRy6dM5YGgV3vZ16eT5VCGF1zyt-qtZg1UDQGE68L-HWjSsd-I7oL4BQVRnYZ9YNN2-hzPcjFJzDvt6sk0i-3ata-5QQRJp7o3lHz3cMLeCEL1PAGOb7xVd5-qJxtwLOWtMKuDJNcTrui3A3cG3B1NAOyx_oR3sbXAkJSDB5np9oNCtYz20lE5oraLTCuC-w5f__vxJx3HmIepNZjvWkFFmfefiNnXhv]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwljn3Sra283uWVFTd5qbuDaOgTY45-Njsp4jzIWd6ncvwffP_o9F_CCDti4GF8K_9nag8EE8c4mWtTNjPTQcXKrHBY-EObpRjQE0BldTsSHzvYuMRX9bxoILqbLBdSGICjTpnnbdIy9LQFevOWQiOU9]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwmOyWATh3LLZr_tYq1aDIl1Fqn77ysq2XJFn6PrQ9hRNsnjSal-NmhYJH7XTKMS6XoeLzI-Q9bFqKPZ6yuKUncMSkKewLUTrkhVOhK-7LzFEZFYuRFL0y8n_5X5ket-9ICxoNLAyeIUywaMrqQF_drU6XQj2Z6iPT4=]
National  
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwns1Se8XrCnuoEz4NGzsRhSLjWvwHbW2Wsfpt0w8wtik1H4qqJLINOZeWtE9bTp2cmUl6udMVaYvCcHwDvGvTKtVseBm7-mEkcLNLW9SvaswhJJ_TrAiSk_]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwns1Se8XrCnuoEz4NGzsRhSLjWvwHbW2Wsfpt0w8wtik1H4qqJLINOZeWtE9bTp2cmUl6udMVaYvCcHwDvGvTKtVseBm7-mEkcLNLW9SvaswhJJ_TrAiSk_]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwk_ZMpJGrRWLRxbNtLomnBy5Kvlq2MhlvddlWPF0UdV_Xwb9prGcn53IB9Z12yv7IfsjF_rPPCeqNNiq5PlBCoeTOukb4mJLAaqPlchJOGjrTTWPeGb83Z0mSWvDVJqyiFt8z6dxtThz6PqOG7Hx1oi]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwn0a7bKQp4sTFYPXyjqz1oWqDRCOwqTW4pt_a74o4FDbmeBtSgc_cKiGSNA1R68hB9vq-qkbC7O1uvWK6C3vG_F6Z9AvJUgl3YvhHXbWfTLAQfozu_XX6u0NXIiA1805mWs4SSCxoTz1Q==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001yboOkPrdGwlP0JhHxulq2FmgFtPfeWKOzo8qNtvAcqhRl7aDDaGIv1HICDTflzce-jKUuFnVikCRVHXKrkKY1kFug0Q1_wcq4COiu7Dm5or_JF2j1OpgFW-Uf-PQZmL69Hlz4LvbP2dQgrI8qNwrP60PE9YjF8Kj-axJHfSSRYxFNV5ngSSbBQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1114016223706


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001ywaSaTgvBz0FEV-l-YUdOw%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001ywaSaTgvBz0FEV-l-YUdOw%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to