American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

January 10, 2014
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Listed Antifreeze - Not Yet

The 2013 editions of NFPA 13, 13R, 13D and the 2014 edition of NFPA 25 standards
 require the use of listed antifreeze solutions. Listed antifreeze is not 
available
yet.

One of the listing agencies, Underwriters Laboratories Inc. (UL) recently 
released
a bulletin to manufacturers announcing the availability of the Outline of 
Investigation
for Antifreeze Solutions for Use in Fire Sprinkler Systems, UL 2901. The outline
 covers new requirements for antifreeze solutions intended to be used for fire 
sprinkler
systems. Do not expect to immediately see listed solutions. The manufacturers 
have
to prepare their solutions to pass the testing criteria. The solution is then 
submitted
to the testing agency where the product is placed in queue until the agency has 
time to test the product. With that said, the earliest a listed antifreeze 
solution
that could be available is no less than 5 months.  It is estimated that a listed
 antifreeze solution will take longer than the 5-month time frame.

Here are the references in the standards for listed antifreeze solutions.

NFPA 13 - 7.6.2.1* Except as permitted in 7.6.2.2, antifreeze solutions shall be
 listed for use in sprinkler systems.

NFPA 13R - 5.4.2* Piping in areas that cannot be maintained reliably above 40°F 
(4°C) shall be protected by use of one of the following methods:

(1)*Antifreeze system using a listed antifreeze solution in accordance with NFPA
 13

NFPA 13D - 9.2.2.1 Except as permitted in 9.2.2.3, antifreeze solutions shall be
 listed for use in new sprinkler systems.

NFPA 25 - 5.3.4.2 Except as permitted by 5.3.4.2.1 and 5.3.4.2.2, all antifreeze
 systems shall utilize listed antifreeze solutions.

In summary, NFPA 13 and NFPA 13R require that new systems use listed antifreeze 
solutions. Until one is available, use an alternative type of system (dry pipe, 
preaction, listed dry sprinklers). NFPA 13D and NFPA 25 start with a base 
requirement
for listed antifreeze solutions with exceptions for the use of pre-mixed 
antifreeze
solutions. These are located in Section 9.2 of NFPA 13D and Section 5.3.5 of 
NFPA
25.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOgDTJt8uXAtla-80kLNdeB39qDtEJV9rqQ7s3gSOPJ1Lb9InDSVF3WWx2h1BSb_S6tUh0hCs_LD_t_JBME76TaGXpTfMkwoKWmoPvnaXbmBSKVnMYsaDBAnpV1vYdZTQdw==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOnNdILoHy-vTLCKP6NDkxcoF_ey3YT-qi0CfXNK_HIThtHATOtjQW7SkydK8JNwkmctB9QdBG_lIZxcKF3ej4huSdOFwU5CBFjrUTL1KUyxFyvrwOrpKqF4Q-RRuVr0OKxHc0MkUUkFpWpPpqiTVFpcewkNMDq8GzCUy6p4E70NRlGlT5Mx6wBFsaxxackORF-I3Vz07Xp_4sdHtLlUxpMQ=&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Feb 3 - 14, 2014

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOmM9bjpfX7XDzm8u3kkFVa5DgVRw0SHV7p1c1jZ36isyXk7ygcy_TRNEjRMWvNriTKkLfjGujJtXfaDp72VqloRicxut3lUizcdExRSURfz33BIKHCsgKkjwUGMatGzB8xXWnK-f2GDGNAex9cdHhSfN7OUTxOpIy9IxWmco7UjJpxiKrvvu_OXrEwYIUvxybNFVdyHvYDAj7spmt7PPS0CWuGBDL78l4gK1cZGmW2-p_o64kuNvSx6pcbN-H-dU1vUhp_rT3NQQXS_eqYWTygkHZ9WHV74VKA==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOj1p71qRx2LNq76QRqqtBe3qwXmK7kMXOUf1tGu8tetbwdTFrjXQ29flUrugAVj_kLGEFMWwrDN1FxZemd_jgwDW4KDQ7NrFUTJxrL7bdUnlpDTOhwULS-rhp3g5p0yb7Q==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

"Liabilities & Pitfalls of Contract Clauses with Regard to Inspection, Testing, 
& Maintenance of Sprinkler Systems"
by
Terry Victor
&
Joe Canterbury
Monday, February 3, 2014
11:00a.m. - 12:30 p.m. Central.
Free to AFSA members!
This 1.5-hour webinar will be presented FREE to all AFSA members.
Register Button 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOmOxGVtg1YBjag4sLGXzHw-IKJlN0FIdCLk1CPHrWpRd5Zqd6gYJc8D_KXOaMvhONcaSmI8flPdcB-Gs-IvyY-DeOfCi-Odsvluq4cSLc_WvnLVulzREXWvPAyY63s7Q6wNEcBWKBdHVAQpkFEu5cvqofGLW_yd4tXXs5rJi36t2&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
Check our calendar 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOmM9bjpfX7XDzm8u3kkFVa5DgVRw0SHV7p1c1jZ36isyXk7ygcy_TRNEjRMWvNriTKkLfjGujJtXfaDp72VqloRicxut3lUizcdExRSURfz33BIKHCsgKkjwUGMatGzB8xXWnK-f2GDGNAex9cdHhSfN7OUTxOpIy9IxWmco7UjJpxiKrvvu_OXrEwYIUvxybNFVdyHvYDAj7spmt7PPS0CWuGBDL78l4gK1cZGmW2-p_o64kuNvSx6pcbN-H-dU1vUhp_rT3NQQXS_eqYWTygkHZ9WHV74VKA==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
to view upcoming training.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOuahEVmsKb5oqPYQ9_4cmdqCmMl9MTYaWJqb85WIgAjkVyWs_SPkGGQBDHT7ZtlpdMEibVywpUcKgWZtkL32BkoUVB7NGA9GnFsVPdOK8WhwZXjYuAEuQJikLyg_gfTbvcuYJCmq7vm_TQobXIZoSRG-45yTYmLmaN9Z55m5kN6x&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOqfKQ6xDN_-Lb8L4FIruka2cThcjHLeXkbULbB_z8Bdcad4gJvE_z4K397GbXLp764Y4T2W_uu6M1xY6pP1UxfJQI1BmhPY4OMne-j0lxivjhm2cRvy-I6kV-jWGXv2Z6Zb9ut8sX2eONCRZOvkXxACWtMUgL0AvGnyfc-LzonSW&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOgDTJt8uXAtla-80kLNdeB39qDtEJV9rqQ7s3gSOPJ1Lb9InDSVF3WWx2h1BSb_S6tUh0hCs_LD_t_JBME76TaGXpTfMkwoKWmoPvnaXbmBSKVnMYsaDBAnpV1vYdZTQdw==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOmM9bjpfX7XDzm8u3kkFVa5DgVRw0SHV7p1c1jZ36isyXk7ygcy_TRNEjRMWvNriTKkLfjGujJtXfaDp72VqloRicxut3lUizcdExRSURfz33BIKHCsgKkjwUGMatGzB8xXWnK-f2GDGNAex9cdHhSfN7OUTxOpIy9IxWmco7UjJpxiKrvvu_OXrEwYIUvxybNFVdyHvYDAj7spmt7PPS0CWuGBDL78l4gK1cZGmW2-p_o64kuNvSx6pcbN-H-dU1vUhp_rT3NQQXS_eqYWTygkHZ9WHV74VKA==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOgDTJt8uXAtl0L6nodLBAzw0D4g-uvZZlnoLx8w5arhRfB2QOiNHRgX__kHfKt2tcDoIXyUszDssgjvvdHYbYIQqghdnAP2K4ZiTWaa3B09rLMafrKXzc6rnZpCkclidvo41KI2U7HxJtwYVOVIR36YPDn3IahONtg==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOgDTJt8uXAtluDBQTJJNmn94gvnsFfR3Ht0kHEZ93zQ_Ag0TdgnnXoTjnofDePuc-cAYZ1ccpmiqwIBKGTt53xgmLNNiDOPbhv3Z3sa4ISddNCs6PZuV1nMw_sGrmah3EuIhf2bIOA_z3RNERJxng0VCYban4hJH3w==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
National  
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOsk5ihlUNzacO8M7EzIJWKVrE6iNtkc_m4WnMIKksIb_BE4eL9QkB4Z_4PszmMT1woJryIDPDFoDuiTXKXwgJ7T0tHZTcFbA73pJiz6SdfsmeDZhcGrRPzSIryshEOSpGQ==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOsk5ihlUNzacO8M7EzIJWKVrE6iNtkc_m4WnMIKksIb_BE4eL9QkB4Z_4PszmMT1woJryIDPDFoDuiTXKXwgJ7T0tHZTcFbA73pJiz6SdfsmeDZhcGrRPzSIryshEOSpGQ==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOgDTJt8uXAtl8z_GLCOPukmWP2rOlllcdfWBqaJzUv-_GdtqWZUeJ-JDb3CG8LfDU_JU_nBjTDyAdYjdLbkNs2PC_KAJAYSVA-mLE1ksC6NwhXsizn8MXuEAMr6bqYj0qyGR62yP8oWt4xKsMRjZ1G09InUYU7b3WQ==&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
Technical Services 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOoCZzUKl0y5qNfVC07EaaZJAUjDS3ClfSJ8JlMJ29I9K2Bk5PMZu2qiNJ1fCuhx-IwIfzJgOCC1kAP_XSHvbzqW9-0W1BwJAWVVrXENTx_OfKZkOynZBSpZ5hc6AYAUo1vF3PobLThx0&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?f=001VPmZNsY6ZMS6TrJheZhpd4H6u-d4UBbx_c11iUJ0bEdT7znv9VQcOnc2kM9fzTrWqfRstxfJXmSacQ-kRJ-guDMCzFhigY8q-oE8Wsj4J7rPlh-_fs56Jy2y6AmvWzJb5xb6ZA0X4Sz5Xz_LhKhPwrxTNJr-ZP-h2Nz3PMyRxHt_yD0yHjj1tmdg5702oBXekDAH26RYJh8ALSeh_sXtIKkfmeCzL0Op&c=eQ6aEg-jYbbJ2iGd3ZfJ_2ssFQ9N_YK4DYE2iF_Tf2ZAx0Q6EhvE7Q==&ch=UcCJANu2bcH4k0BSUG1LbocLU8ZoaDNrFi1KECXi43k5QKP2jocJag==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1116214125735


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=a3df7676-cd8b-4d6a-bbad-3486a3b05e15


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=a3df7676-cd8b-4d6a-bbad-3486a3b05e15


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to