American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
A newsletter dealing with codes and other technical issues
January 17, 2014
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
NFPA 13D - Well As A Water Supply
"If enough pressure and flow is available from an in-ground well, is there
anything
in NFPA 13D that would prevent utilizing the well as the only water source and
not
have a 13D storage tank and pump system?"
We have reviewed NFPA 13D, 2013 edition as the applicable standard. Our informal
interpretation is that a well is permitted as a water supply.
Section 6.2 for Water Supplies specifically allows a well without a separate
storage
tank and pump. This section says the following water supply sources shall be
considered
to be acceptable by this standard: (5) A well with a pump of sufficient capacity
and pressure to meet the sprinkler system demand. The commentary in the
Automatic
Sprinkler Systems for Residential Occupancies Handbook clarifies that a water
well
can be used for both domestic and fire sprinkler (or fire sprinkler only)
supply,
provided that it has a pump of sufficient capacity and pressure to meet the
sprinkler
system demand and the well is capable of providing the required water demand for
the required duration. A combined domestic and fire sprinkler well may be more
reliable than a stand-alone pump and tank combination, because the pump is
tested
each time it supplies the domestic connection, and any problem that occurs will
be noticed and addressed by the occupant. As such, an in-ground well with a pump
can be used as a water supply.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-Yoxwyja0_JTyUm2Szo3Va-ixA0uDIMqFyGIStDXYtoywZAqx3sAi2v-WNtXkDO3ZMamichl6V-OMoAwpgUbPpaBA0-wNCLOQP5dIEGP_FVNORE_F2VIxXPQsARGsr_HV-XJjZw==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-Yoxwyrr_DRwXnUNRjaq3Hii2oVnKiitxfBesWtLmAC8qrOUuP7Vt6HnBDPC9o-F2QFi396blDSZopOJdLfl0TT-6I0tEZPPellFCTH2f1l4WMtoL4tp0WQaDEP2kAc-9M8Q12UCTJynFiQ4GrawMYX49uQbH3bG0D2ifRHq2qRdPGnDIpLqIn-vyLB86iiL-XkVDKrR3LTj4hqp4Nj4MPv-tH44=&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Feb 3 - 14, 2014
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-YoxwyhXbYdeEZV4VMKLuiHzyKgpBD3a303Hyvs79K-WC5Gpl9p_oUX4mtyV3uudED63TXC-lu0EQb2qLOASC60Jiyx42LL1z0tgCNeOLO8TZld8O05BP1tfC3z2H0iKIOoCYlDki-PyGJGLZQKPGjnYB_umTXJ68zQzIDG6vY8vLQ_Yf4nvDrRPi1TnDXxHNtaamtR2Ghx5TSnNeoCNvrIKHBFUVzTinT2A_Jx06vc6zIeZm-9acaph2Ykbr3NV08ejH9VIA6FW27GS38X4Fsk5joqT4WxjOUoIZ4Q==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-YoxwyvfuiW77fobRQdNorO42RZnaJiXC2lIzhJqcQKk5_JCfBj17zf2FkxNHodUpKeJAuo0rSI8_yEN5qzB9nJnh5xaD7IxaUCAkvxAjUT-6cTmHjnXt0vHtiPhqEbPm0IwFtg==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
"Liabilities & Pitfalls of Contract Clauses with Regard to Inspection, Testing,
& Maintenance of Sprinkler Systems"
by
Terry Victor
&
Joe Canterbury
Monday, February 3, 2014
11:00a.m. - 12:30 p.m. Central.
Free to AFSA members!
This 1.5-hour webinar will be presented FREE to all AFSA members.
Register Button
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-Yoxwyr2BESTLBh_GQHTwqPvYTe8Qg-wcu7pr504C0MV2FKnAl8bPL2Z06Sa8c8fh9bOcIkPiMiwWEKj4EIfg2Kp7AJIjODoan4gXsTmNtBlShdGFozCSnhK-VYKlkSv_4TYSB7fRsWW_UYwhoWNzgEOsiyWTQwUOpnx3RhNqQdU5qBXg&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
Check our calendar
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-YoxwyhXbYdeEZV4VMKLuiHzyKgpBD3a303Hyvs79K-WC5Gpl9p_oUX4mtyV3uudED63TXC-lu0EQb2qLOASC60Jiyx42LL1z0tgCNeOLO8TZld8O05BP1tfC3z2H0iKIOoCYlDki-PyGJGLZQKPGjnYB_umTXJ68zQzIDG6vY8vLQ_Yf4nvDrRPi1TnDXxHNtaamtR2Ghx5TSnNeoCNvrIKHBFUVzTinT2A_Jx06vc6zIeZm-9acaph2Ykbr3NV08ejH9VIA6FW27GS38X4Fsk5joqT4WxjOUoIZ4Q==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
to view upcoming training.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-Yoxwyv2YUY9DSevFJft0XcGKFpNQeHRl0C3vWyBbu_MZxM9ZEQU0j4Fnb3btYbGWRsMw58LB9V8ruP1n1ZfwRsHGED-wMCiaPZwgSezObH7mdC2cnIwcMWh2p9E8wTtx8-sXff2aTt2rs4CvQxB8MpMB5WSHjaGTOmOUBtW8e8TtC2B4&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-YoxwylySVA59H997o-b5SRgktMlu6G8nNQMzH3Eib0D63UzkxuOFuntIvzEArU_SSkjh8r0Ym9SS_MJBBh0O_nzETTv1g7wmU5HflJsN6Y6Wkps1LuH0zIjiueQDOVEzU-0gXkq3bVmAGJ5EeX1E13LxEWnsux3WRTBJFEZl3zuAs0if&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-Yoxwyja0_JTyUm2Szo3Va-ixA0uDIMqFyGIStDXYtoywZAqx3sAi2v-WNtXkDO3ZMamichl6V-OMoAwpgUbPpaBA0-wNCLOQP5dIEGP_FVNORE_F2VIxXPQsARGsr_HV-XJjZw==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-YoxwyhXbYdeEZV4VMKLuiHzyKgpBD3a303Hyvs79K-WC5Gpl9p_oUX4mtyV3uudED63TXC-lu0EQb2qLOASC60Jiyx42LL1z0tgCNeOLO8TZld8O05BP1tfC3z2H0iKIOoCYlDki-PyGJGLZQKPGjnYB_umTXJ68zQzIDG6vY8vLQ_Yf4nvDrRPi1TnDXxHNtaamtR2Ghx5TSnNeoCNvrIKHBFUVzTinT2A_Jx06vc6zIeZm-9acaph2Ykbr3NV08ejH9VIA6FW27GS38X4Fsk5joqT4WxjOUoIZ4Q==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
Buyer's Guide
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-Yoxwyja0_JTyUm2SUpHYuu1lcIvlkVP8O897MpT-BuiEmVQfcMDkcH_DMwdv_tCigZ70aKsAhcaPu3mei-550PNj-EvniaMDJLRCq70EVKE_3W5ybipsDHU_14rhVV1Bn13EJV5ulm6AIxfc9wztINnWlQuIbce8VXamSQ==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
Join AFSA Video
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-Yoxwyja0_JTyUm2Sd-kmv9gdztDTX7kzCeYyLkn5rba5ePHRJyib0f7WZrWE1Dz55pgeqlRdD3-1Am7Omf3Ovf5z5bGKNm9hvJDMUJf-_NjpCN1I8sOl8563HGsdLxAgqkclnwQx7rrXh5S5XcICN2sD4SVdAP5XTa2uhA==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
National
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-YoxwytAL9k2yI7YqXKVj8Krc5a2Z_upVyMH0N_Uy9lJ1eY5ynGFjmmwGXq5fwA9QSCHIEOn7E3v3iPy7Ug215nhqQXWHQKw8J5Gywr9RsSsmEQi6OhQnPQtgWwQ2vqxA7TyY9g==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-YoxwytAL9k2yI7YqXKVj8Krc5a2Z_upVyMH0N_Uy9lJ1eY5ynGFjmmwGXq5fwA9QSCHIEOn7E3v3iPy7Ug215nhqQXWHQKw8J5Gywr9RsSsmEQi6OhQnPQtgWwQ2vqxA7TyY9g==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
OSHA Alliance
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-Yoxwyja0_JTyUm2S1-p8eMvmHUDf80xOW2NLfLnLVE-MqXZjAXBJ-I4sShA7fjE6LMFBYrIpQ3Bh8tIjx4vb6IGhIWDawzMH0QMNofMpteyGt9LkGO_yaGC2w5D1qD7OLtDOy77KnURMoWL5SNlFrzP6jOh4uSAZXDQQCQ==&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-YoxwyuPVyzUFFIEyZTn-EGTLU9Ri-ZLMCmtqXzk1ZIs2vwPRoSP7uqhaeCnTv-tTAea4SOxKd4JCfcSY1Lziy_dDwi6ksMNrj5rtPIgTlEGS7AGcKsgOchs1xjWfrTmWO_37Sy0HMUkzd3Z8&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
Informal Interpretation Request Form
[http://r20.rs6.net/tn.jsp?f=001mSQJZp7MJx2Y1d-55Aq32cZmAcfQ701szihikrj3pRyA6_0-Yoxwyl3kQXVK9Lv6X5MdYIkj-w8EVybtbhbdn8SHf7Y75KvaQQe390Hap7ltCUHl5HNT7OWRCXgwZQunE47NpKUV-F6_Gjm2tboADyWs8j62qU69-k9pe6LJuFKq1YibbZomCd8f5YxTxTYz3uCnt63kvSR_76ikaf1T3U0fWiZYEWt8&c=X4RqAiLbKxSNYBnCokUr3gr8KF5Mf2bebE4TVStDShNQ2Cw9EjgIbQ==&ch=5PlIp-8Y03BiEIuni-TUhfQIwOgxik1xxD1m3jSENmWWfEYO53_O4g==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Join Our Mailing List
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1116277423954
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=7b29129b-01ce-4dfc-8fec-1fcdac9386dc
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=7b29129b-01ce-4dfc-8fec-1fcdac9386dc
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org