"I have a project were the entranceways into apartments off the corridors have
an
alcove of 1 ft 6 in. deep and 4 ft 8 in. wide. I am protecting the corridors
with
residential sprinklers. Is it imperative to protect each alcove individually as
well as the corridor or is the over spray of the corridor sprinkler enough
coverage?
In NFPA 13R, Section 6.7.7.1.5.5 says that small architectural features are
permitted
to be unprotected if the criteria is met. Annex A.6.7.7.1.5.6 gives the
explanation
on why these are permitted. However, section 6.7 only is dealing with within
dwelling
units. Could the same be used for corridors protected with residential
sprinklers?"
We have reviewed NFPA 13R, 2007 edition that you indicated as the applicable
standard
as well as the 2013 edition of NFPA 13R. Our informal interpretation is that
shadow
areas are permitted in the corridors.
The standard does not specifically restrict shadowing in the corridor. The issue
of shadowing for residential sprinklers was specifically addressed in the 2013
edition. Section 6.4.6.3.3.1 indicates that shadow areas shall be permitted in
the
protection area of a sprinkler as long as the cumulative dry areas do not exceed
15 sq. ft. per sprinkler. This is not restricted to the dwelling unit. In
addition,
Section 6.4.6.3.3.2 indicates that shadow areas in corridors up to 2 ft in depth
and up to 9 ft in length behind sidewall sprinklers shall be permitted as shown
in Figure 6.4.6.3.3.2. This figure shows a corridor with alcoves as shadow
areas
that are 2 ft maximum deep and 9 ft maximum wide. Thus your application meets
the
intent of the standard without additional sprinklers in the entranceways
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbdy89L7Doi6P7j3JJmxWTF47QiXZ5x1AwO9VTcvzcqWHqQMmYgfThVriVjpkVIc1SNjkskMA8hkuaJ4ODFbI9jGnM0eedG4udiGmj1pNUn6kPqfFQuVm5De-MeVImMaJeAA==&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbd77EE8n4V2YIaj_r13tsPkR6UuYG9uKIeDNiQdG3Was3c-Fkpov_fTzwDqugOyS8JFdzDAPW3ywSARIYfPTfsyVT6w2ER2t6_4LQa9jLzqeHX8kuTK1qzKI6__Kw1AoJzSL7W22KQ2utcJxQjn37Cau-21mV9Sct78GlqxLI0PhDAny_fCm0W8CQ1yfnALl4W4EuChETFQ_1w6JsiTDXl6o=&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
AFSA Webinar
by
Josh Tihen
"Corrosion Inhibition of Dry and Preaction Fire Suppression Systems Using
Nitrogen
Gas"
Wednesday
April 9, 2014
Free to AFSA members!
11:00 a.m. - 12:30 p.m. Central Time
1.5-hours
Register Button
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbd3A-iY0kWrZ5biewBKAXAxhz9OQArqF0g7vGbV-YBywBdEHTitTqA319cWgRwYBMI6Brhh8QOynf0u02BP_TRBnCVxHt048k5GmePe4x6D_3DuyP8euHqyzRfnjqJ2khSYwEB8OLQpYX5RaaRTQsdUojB8flfVjs9oZshlcE9enf&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
July 14 - 25, 2014
SOLD OUT!
Sept. 8 - 19, 2014
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbd0WkxdPovRUbEfkSU-9gFxo0fayBlbkuVU75Pvc9dfC1iuWtM7wDfeHv8pF-6ROjKDlYPYdOOw7YslI7KIw67j4IRU_DqlOUtuoSEj-6_ntgheXbErAto5jV0Dz1nUPxmn68CMb6c5EfR0QeEOJiXtRTc-qZ8zRqnIr7JpBpawIR3smU1zdbPFW0T2BJirjeq8W-gsE0J8VjyETDXqBYHdJ5mh4yMH-3yKiMjYkfALJ9n1iuCap41Qs8HZ_zL6T8_2Rl201q3yPfGbglKZXVpB6eOcwB_GS9Hw==&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbdxpaY8T0I1SYMbAzQdq5tTlj0-VqN2AivjwEPIgLjtByrIBUT3cJNmj9Wt-gWNJdA7bZB4vhpcAtP0tgMM2gRbB6w7hRd2c6yPxogWL8UtZAiBv7Qgyr3o2qIV5ienoeEQ==&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbd_GYo9AbVIpE6xoiJO4vAbyi1Xfojp9ci_mNAw3pNojFc3fXhNUR8_7QEV-PbCRWFzwaqtrlcaqlPSRT3mi3qelDVXuWRTSlaxv5S6-wY_HTtfw0L7WauTpzPQ6ceIgEfMLrl64X0K6MeXJkenlYJiKZSv2dXDRxGtX2ySaejWIO&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbd5eFxVEM9BB5qArKE2C0jEAlA9UDPiSURy5EtAHOf0CMZC1FQTtoDLsGlzSvwdwQcfxj1Ap7aYsw5imiK5DRtETwgk497f036-wQcRchH78EWo3G5DQlT8sgaBjLEYvInfahTanGZ8r0uM123CflD1f2LTDb-yOfr7uGHoq8n8Zj&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbdy89L7Doi6P7j3JJmxWTF47QiXZ5x1AwO9VTcvzcqWHqQMmYgfThVriVjpkVIc1SNjkskMA8hkuaJ4ODFbI9jGnM0eedG4udiGmj1pNUn6kPqfFQuVm5De-MeVImMaJeAA==&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbd0WkxdPovRUbEfkSU-9gFxo0fayBlbkuVU75Pvc9dfC1iuWtM7wDfeHv8pF-6ROjKDlYPYdOOw7YslI7KIw67j4IRU_DqlOUtuoSEj-6_ntgheXbErAto5jV0Dz1nUPxmn68CMb6c5EfR0QeEOJiXtRTc-qZ8zRqnIr7JpBpawIR3smU1zdbPFW0T2BJirjeq8W-gsE0J8VjyETDXqBYHdJ5mh4yMH-3yKiMjYkfALJ9n1iuCap41Qs8HZ_zL6T8_2Rl201q3yPfGbglKZXVpB6eOcwB_GS9Hw==&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
Buyer's Guide
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbdy89L7Doi6P7OUXL56wW1fQxLhT0sUYDbhBwLAAy-SNBPGt_B-Uts3NI5wChK5j9sM3dRYfsB7DOjcAKp6UOjFEq2P71TcymqaReonLbFNPIDTq3sBhXz0Um_oAzmd32IPHBYqq7ojTO35nYRWEZ0TAYHfJjJAeVHg==&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
Join AFSA Video
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbdy89L7Doi6P7R6R2iaXKWauuvuO6Jz9HGWEmQrt-dNTrps1JeViDkrK86fBXTQkIUwzDS-ya-EOaoWD_xpw-Fr0wnbqiB7bKl8OGf0GTYunbD4rTQPw6aSHD1_7KOE6FvUPR4hJNzJvekIyTZ8zgiXpHguz9VQSKtg==&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
National
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbd97ZvmR1zxpAtW8-vZJof7EAZI7ftTHxp8ZN4J7zbmXfiAwWgrTg2CJOL8vH1l-LhHVk-V_IHauO5kLq9r0f_ShwqYJsupEmfI9Stp4Z0DM0INXWkv7vGs4uUCpJLRbH9w==&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbd97ZvmR1zxpAtW8-vZJof7EAZI7ftTHxp8ZN4J7zbmXfiAwWgrTg2CJOL8vH1l-LhHVk-V_IHauO5kLq9r0f_ShwqYJsupEmfI9Stp4Z0DM0INXWkv7vGs4uUCpJLRbH9w==&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
OSHA Alliance
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbdy89L7Doi6P7-Y6x2cW2ZVkrBiL8OriC250C_ahlGsNXrsTKuQz1heDAtYNuW-Xojop5N6pCVMyhE0Ip6ltEk3HzXerBX-MQKIU56-QIhwm2N7DZmY7xWLJJfNuPO-hEyXMOUdgD3ExxoX-3bWjjDdJAJLdjW1DGKQ==&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbd591lt5-F-5wlt5-ttobKVk2rRKHViQ4CQ8hKDBpmfgjrLE9sZKaZZIw1m9gPdbDUD9lFivjcvedXp8eRY7IxUqQEX_hxWXlzBLU0w5oeyQ9GWU668Y8139MThd6-l2_p4pAP6KXwqW2&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
Informal Interpretation Request Form
[http://r20.rs6.net/tn.jsp?f=001p6yDW3yzyX1t0yJBHMYezLseOZJhz9RC3feGaAlikr8Es_g1xkkbd1o29iZD3vZiCs0yr0CrJDXOdpUgIXIJ0fHTq7G1QmAWMZsWfAyvh6bEG2Zz-3tcGBIsvhyhupNMippkknBwKmSnUpnuLBKNsKT-8OMWPMSn-kkOC3TCwscrZGKRyCuFNVDOaXllcWBWomOjZltb7Dr1p36EER9yUg2eejhv7tgW&c=PuO7tW-9yiww7fOdcSFJsvWh3nZGHzZ4XMyn1U1E9qY9gyUjYX4cnw==&ch=Z6pABjQdU1UM05u_6dLA4mTHYBGAqce6mAwGLWmDbMM7RAZcEnEJPg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Join Our Mailing List
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1116864928365
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=0b94b3ed-87cd-4a61-bb3a-194dabcd6de6
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=0b94b3ed-87cd-4a61-bb3a-194dabcd6de6
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org