American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

June 20, 2014
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Pressure Limiting Controllers and Relief Valves

"Is the new text 4.18.1.3 to account for failure of the pressure limiting 
controller?"

We have reviewed NFPA 20, 2013 edition as the applicable standard.  Our informal
 interpretation is that the relief valve is provided in case the 
pressure-limiting
device fails and allows the fire pump to run at full speed.

Section 4.18.1.3 says that where an electric variable speed pressure limiting 
controller
or a diesel pressure limiting driver is installed, and the maximum total 
discharge
head adjusted for elevation with the pump operating at shutoff and rated speed 
exceeds
the pressure rating of the system components, a pressure relief valve shall be 
installed.

Variable speed controllers contain a device that controls the speed of the pump 
based on the pressure of the system.  The failure of a pressure-limiting device 
would be a rare event.  If the device should fail, NFPA 20 has a requirement for
 an automatic bypass for the variable frequency drive in an electric controller 
and to return to full speed through a governor control on a diesel engine.  This
 will allow the fire pump to run at full speed.  Section 4.18.1.3 requires a 
main
relief valve to be added into the system to prevent an over-pressure in the 
system
only if churn pressures would exceed the rated pressures of the components.  A 
relief
valve would not be required if the maximum total discharge head adjusted for 
elevation
with the pump operating at shutoff and rated speed does not exceed the pressure 
rating of the system components.

Section 4.18.1.2 says that pressure relief valves shall be used only where 
specifically
permitted by this standard.  The Fire Pump Handbook commentary for this section 
indicates that there is no section in this standard specifically permits the use
 of a main pressure relief valve.  The use of a main pressure relief vale on an 
electrical fire pump is to be considered poor design and should be avoided.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 25 Accepting Public Inputs

The Public Input deadline for NFPA 25, 2014 edition, Standard for the 
Inspection,
Testing, and Maintenance of Water-based Fire Protection Systems is set for July 
7, 2014.

First Draft (previously Report on Proposals (ROP))

Submit your inputs online 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsWOE8qq7wReVOEZFB2SbBESFRpNTcSaeyckAT3SoXUZVNXwCnpAZmfRZwTH4KDoIcOjywykgF3WyMpU-SO2POPxYVyWrpsOiRmSCsHebxBcD32MX5aiWl0qKyNxPu0YNhEikCQ-1zBR850RBegRSpJh]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsVbwLUrOklkJrG4nKZqTHZwoOdzBI4xSHE=]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwjeY1qTViE9LAVXh-l09f4sdFjXW9IiUNasfLa1mHb0sxQMn4w-E3EAC4XID-1EZ0fW7XQT9qKCI-r1L7Om2TokeHivkljHEJigrmP2rIbxQOW8vnjKsSWAX72FYhJtnaQavmR84Xtgk=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
Oct. 13 - 24, 2014
Sept. 8 - 19, 2014
SOLD OUT!
July 14 - 25, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsXwUkUfD6MD7Z9fkanVnhkO45ZgP-IWy1Y7ORPIJe5NRS2jjeaHce9hXDBjnup31twgc8RwCe-YgEDKh7RYDi3RLp-kvPKsubiJmI7TcsHMstjlw5k5YbwtmtibQZlWKlEinzr-zetu9rCwJ1D_11-sDKXYTgcI3iTBRFJtOZajX-_hrLkWkPy0hUJoC5tv5vJt9N9tTFrS8Q==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsWYNdfbEnjusJOBTYTCqFwfb08fMuR6XmDGEM6fcw9fNQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsVbwLUrOklkJrG4nKZqTHZw_7mt1Ef2uVgNmg408VfES_ALEBO0jp1ECg4ZGEhpt-OLSM_-GJYD-6nraIb92X_-]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsVbwLUrOklkJrG4nKZqTHZw_7mt1Ef2uVjdYelek7I2pUeU8ZvrwvQPps2GNAWs3kwU_2xOrSuZoAWw6e1Fo81j]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsVbwLUrOklkJrG4nKZqTHZwoOdzBI4xSHE=]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsXwUkUfD6MD7Z9fkanVnhkO45ZgP-IWy1Y7ORPIJe5NRS2jjeaHce9hXDBjnup31twgc8RwCe-YgEDKh7RYDi3RLp-kvPKsubiJmI7TcsHMstjlw5k5YbwtmtibQZlWKlEinzr-zetu9rCwJ1D_11-sDKXYTgcI3iTBRFJtOZajX-_hrLkWkPy0hUJoC5tv5vJt9N9tTFrS8Q==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsW0MR9aqMekE7IG4unkKqP2dZ1jL2tq_xJLLyjI4enfCMXUb2Ap9gF0vMhP8Ej5cQgu38w8mEW2hg==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsUcL9apv6zWQsNCeWxiVVBOl_5d8XxD4qdfY4UX90r_O_OIY-R86zcNXAcXV5_IjxaQg_T4CPmO3g==]
National  
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsWmcfVC9b3kedCN-C0Lo178vGTbMFj3v6Fv9RsbWrY6IQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsWmcfVC9b3kedCN-C0Lo178vGTbMFj3v6Fv9RsbWrY6IQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsU0d7TVRs6gX4F7fWkdUwJszFOJzsTjalUBQ4adDw6IOdy0n35Ar0nPfZig-DsplL7BWiIDAm1ywA==]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsVbwLUrOklkJrG4nKZqTHZw_7mt1Ef2uVgDmF6JrpdTsLlRgdaFOQak]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001SogBY8NbtxeEE87cbosJeelGW7l5mq1_yJmepAQOEgtAlvB6FZXH0P0GdrtH1IOwfT7F5HtdPsVbwLUrOklkJrG4nKZqTHZw_7mt1Ef2uVjLAFhejPOrjQwc3X7fmTmUo60khehHyYzQxIjs638qTWl0q2WlQIyK]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686&id=preview]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1117712407326&id=preview


This email was sent to [email protected] by [email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001YGnPsaPMfBw9Fmf8w8ZLTg%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001YGnPsaPMfBw9Fmf8w8ZLTg%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251

THIS IS A TEST EMAIL ONLY.
This email was sent by the author for the sole purpose of testing a draft 
message. If you believe you have received the message in error, please contact 
the author by replying to this message. Constant Contact takes reports of abuse 
very seriously. If you wish to report abuse, please forward this message to <a 
href="mailto:[email protected]";>[email protected]</a>.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to