Standpipe Calculations
"I have a Class I manual standpipe. Where is the 500, 750 or 1000 gpm applied?"
We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal
interpretation is that 100 psi at 500 gpm is the demand at the most remote
standpipe
and the calculations include the friction loss through the hose valve.
The hydraulic calculations and pipe sizes for each standpipe shall be based on
providing
250 gpm at the two hydraulically most remote hose connections on the standpipe
and
at the topmost outlet of each of the other standpipes according to Section
7.10.1.2.1,
at the minimum residual pressure required by Section 7.8 which is 100 psi. Up
to
the 2007 edition, an additional 2.5-in. hose connection was required to be
provided
at the hydraulically most remote portion of a Class I system to facilitate
testing
in Section 7.3.2.2. One outlet could not be expected to flow 500 gallons per
minute
so two outlets are necessary to flow 250 gpm each to obtain the required flow.
There were changes to this in the 2010 edition that eliminated the wording for
Section
7.3.2.2. Thus, the standard no longer requires an additional 2.5-in. hose valve
to facilitate testing. The additional hose valve can be used from the floor
below.
The additional hose valve can still be added for convenience. Also, note that
a clarification was added in A.7.3.2 that states, "Only one standpipe is
necessary
to serve the roof regardless of the travel distances in 7.3.2.2; it is not the
intent
to extend each standpipe to the roof level." It is not the intent of the
standard
to require each standpipe to penetrate through the roof. Considering these
requirements,
the most remote standpipe is sized with a demand of 500 gpm at 100 psi. This
size
is applied for the remaining standpipes. Again, it's not necessary to calculate
the 500 gpm through a single 2.5-in. hose valve. What is missed at times
during
the calculation, the water flow must be taken through the hose valve. The
hydraulic
calculation procedure in Section 8.3.1.2 indicates that calculations shall begin
at the outlet of each hose connection and shall include the friction loss for
the
hose valve and any connecting piping from the hose valve to the standpipe. The
flow must be a minimum of 250 gpm per hose valve at the outlet at a minimum
pressure
of 100 psi. Additional standpipes have to be added according to section
7.10.1.1.3
that indicates a minimum flow rate of 250 gpm per standpipe, with the total not
to exceed 1250 gpm or 1000 gpm for buildings sprinklered throughout.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUgT_K4cddHV_2NjPwtskw8TqmQrD-EIlhAjZUi1t4F5f-WgjoqsaZVMlYEPRkKAYMM8qfxY9rHAqqw_Xn7I1DXyftRP7lQkMXSC9lLM9cAxRUIVvy7C0Ghnqq8-PTZLX9Q==&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUuLIbVIO3UTIOAHvDjTpoizZNrptsvzLWF--sOBOUJB6WFpBbM3NzUwqISi-VIPXR3pRUPOlVUzhmobnnN8kgiOlEXsosDc0aiwQaZU_YkEYDvzISgqSgbq6sGDbWiTzJ6NYadXGU_V-dC5eZfXtXNAX6NZdL6gsKOkwwJWQwBn15TlhvUhZUJcuvwmC9ispoheQO2q-25tqgnMlpKKbhhA=&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
Oct. 13 - 24, 2014
Sept. 8 - 19, 2014
SOLD OUT!
July 14 - 25, 2014
SOLD OUT!
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUqPZAB0XNtrGIpvopAcg0rx_Sbx3kBeni8Dlzza2cja4SFtw8TvZW52pO103sU-AamtyylrjUndmAq6sgLwkqyqsuJSSDDGjqIfsauZH4uVQuiwNAMlVzC19ML8E4xvfp-U2Vy63UNQF0YP10eG0oQ-eAi2IrePhDWdhca1PCqm2hkPOhbELd72c6NlwVCaxHGFpgOD9VkWrLf2PyACXFqBxABKxTUZt9lx4gugvFoy41vaewAb2W5fhM9YdI-G8l1B5BLeh2XA13O_1nAOcnPu6mBHOdZlVkQ==&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUrnL9jFsqD75VdQMmxYjz4nx77e8hUsbw24W_ifC0K3W54Iy210A3gMaPKf88i7kWDPVfB05yzXCFjBKFSaFsVE7XMcUW3c5d7jT-1q6skacUMuSnvE3K-mm0r_fCRvJJQ==&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUv6Ix4uPSpvL8UsgTYyVQH6msM84GU20QnWYMOLU4B_AwymiH0KTkmQJAL_j6KPu0pjohW5sjiROqX18DGQ-SL8ogHf0NA2YQY6GrL9ExgyiDps8w7kKLKIMcwNTaqKrKptZUDTWpahhvApMC-JTNW7wg6tsuvL9FGoqllesb9vC&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUqhyKp7X-atk_T3zQAG2neQh7onUxontDj3Ng4QbNAn5vAqbz2V0F4wY1VFY92SWW72maJzZrau66CcmWq7PbLLsDCHxk3xdk1vl0U14ORdNHdaLHeiR2xP6BSLSGr95xivB9Q-XJQA834rcHTI7cWQVORrp4DCxk2DiLkCc3GXj&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUgT_K4cddHV_2NjPwtskw8TqmQrD-EIlhAjZUi1t4F5f-WgjoqsaZVMlYEPRkKAYMM8qfxY9rHAqqw_Xn7I1DXyftRP7lQkMXSC9lLM9cAxRUIVvy7C0Ghnqq8-PTZLX9Q==&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUqPZAB0XNtrGIpvopAcg0rx_Sbx3kBeni8Dlzza2cja4SFtw8TvZW52pO103sU-AamtyylrjUndmAq6sgLwkqyqsuJSSDDGjqIfsauZH4uVQuiwNAMlVzC19ML8E4xvfp-U2Vy63UNQF0YP10eG0oQ-eAi2IrePhDWdhca1PCqm2hkPOhbELd72c6NlwVCaxHGFpgOD9VkWrLf2PyACXFqBxABKxTUZt9lx4gugvFoy41vaewAb2W5fhM9YdI-G8l1B5BLeh2XA13O_1nAOcnPu6mBHOdZlVkQ==&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
Buyer's Guide
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUgT_K4cddHV_brkwT28UwjOUnIh-LUoP_GNnQCwOLTNCRKaBmiV7QXCX2K6Ii5Q_SuJTIoT7PUMbiL1B0E2ZnO5GlhBqBHZApWzkW0_agaBwIcWeHiO0EtGqwSEuyhY_2jScJK4u5i4awd6FA_aj5YwXKT3dpVAQbQ==&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
Join AFSA Video
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUgT_K4cddHV_dr33boXCiZopu7ju34f-treM6xMh5h2ewISdmViwUCnLdmCyv5r0WXZ8hwALE2msESJkGu-NCtnzIkedRkdBzoWnqw2SNsHuSIjtTqjR1PmJPJtQ_EtY3j4VmlsIThMia3rNe2VNEN1Hadciyy2WFA==&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
National
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUkxdPi5Xr9CkSS7d5y1317gGBxRsDmjYTshcFXRZnGqKEQGStA5B1kPpkKoKRecfWt9vd9mQAUjXm-D2C2PhUWfLossF0seV4W5zaNW8wlXCt_XWr7pFnyX2EV-LI15uvQ==&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUkxdPi5Xr9CkSS7d5y1317gGBxRsDmjYTshcFXRZnGqKEQGStA5B1kPpkKoKRecfWt9vd9mQAUjXm-D2C2PhUWfLossF0seV4W5zaNW8wlXCt_XWr7pFnyX2EV-LI15uvQ==&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
OSHA Alliance
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUgT_K4cddHV_DoSO-qWNdn0TP-yK7pPsI88sm-tf53dJ6Vqxf-efdzNztafUYTilKQUVu9nvMYhzcORHvsth5b5OHDkHIS-5YrGyVAeHSYYFP59nBy93dzbSwbYZS-g6TxuF9DrJJX59bTCqr3rBTz-ByVWT_iJZzQ==&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUslIPzltt60Npi0ghJpggIMxwK8aPNEtfT_O0dlAkuBfhVCTjEbqcrlym2vAzX2RSWf6Zm9TOz_AB-QhkwXswxttsZIj1MiqX6DSLUMcOq4H0wUabgUsNv6CmjVn-FLNDwd-t43pxotk&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
Informal Interpretation Request Form
[http://r20.rs6.net/tn.jsp?f=001219A4GDcCknqS_GWWDyQQ84ZTSfGA4SCBbRc6pFsrtf-G5SWQc-hUrXVNhKAHplRWzHfGMbL9aRUiv1pR7HRGjx0peSTYxcm6YN-CO_nrT9MeFFbtdhbRUCM2fvnWUQ2MESozJFPL42_Wfk9ePp2-fxUjV-ozCdtq_RiCKeN05gH12shzWQB1AlmJVvehTRhMDH3OsgJvvJm8SfG0pvaMC0D1ljKg6TH&c=YZ5OXjFbtuXqcsMsznLE340NwqQjio4VjTOzbKR1jQSKNrogpBEOwg==&ch=YR_HhcpTztiQALuFP1rjUPr-i2fvCH_eiy-sjxv2ufYqK1qgPcTdYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Join Our Mailing List
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1117961011674
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=aca029ed-5829-4468-995d-7ba653146d40
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=aca029ed-5829-4468-995d-7ba653146d40
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org