Occupancy Classification of a Bar
"Are bar areas in restaurants considered Light or Ordinary Hazard occupancy?"
We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal
interpretation is bar may contain a mixed occupancy of seating, alcohol
serving,
food service, mechanical, and storage areas.
In determining the occupancy of the different areas, you have to start with the
definitions in Chapter 5 then use the examples in the Annex to clarify the
ambiguous
terms such as low combustibility and moderate quantities in Sections 5.2 and
5.3.
Although a bar is not specifically listed, the seating and alcohol serving
areas
have uses and conditions similar to a club and restaurant seating which may be
classified
as light hazard occupancy according to section A.5.2. The food service or
preparation
(restaurant service areas) and storage areas may be classified as Ordinary
Hazard
(Group I) according to section A.5.3.1. It is likely that there are areas used
for some storage. The commodity of liquor that is 100 proof or less is a Class
IV commodity when palletized and a Class III commodity in glass containers
according
to Note e of Table A.5.6.3. In order to still follow the occupancy hazard
approach,
quantities and arrangement of the storage cannot exceed the limitations of
miscellaneous
storage as defined in Chapter 3 or be over 12 ft high for Class I to IV
commodities.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs6mdTetgER49G7JZAIKdVvDNeD59gdzHq-ZwXiHuVE_vUp3-wzN4NvHTUyUCRgeznRoJ1FJqGUZABni3N5YNJZpfGy-1yyfPDKOuEtPdIonq8UdeIq88Zf9F6EW0r5ElZw==&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs54w2UR3v3a6VM_svkoZdH0Sxi2BrGMFjJvj2aulXSmCrM6HRBxE49yfE9aFH0q1ekSRsSPaHPr1cTH_JjfFNL_5pfGzUaU99JgQOftyvZD4wnJQGG07R2wbamhgmG3wKz7EyeFfra2JB01VKdEBFyqz4chYNBfFV-QV2RBxai7cHo0SgtW3iM13JywtbzeHW02wglcFW1Mz-ywbJ2tLLSw=&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Oct. 13 - 24, 2014
SOLD OUT!
Sept. 8 - 19, 2014
SOLD OUT!
July 14 - 25, 2014
SOLD OUT!
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs8kSp3lZ84azcE0CReTgtjsQNHYyaugfW8b7YgrhJj8r8jw63cwOj4athoG-yT5EkS-nne0MlhPlPfcoaGUTKjhIswOwgG1rxJdPyJ60MhX2UZvxz6VCHpEP5ZegGLLgBJY4jQGZYTujEjooc3sPmk8dnab42RWSTFGRpOFnozpm6MlSieJFPiILFQAMIkQY4BParAPORT9vSqvYN1V_b3Yf6Rrilg1t7Mqac-CsR4_ON1xjxdvz9GAii1N3I7FbJJmKM5RxQFIJ1GDeGi-nTWZiuEH_po4zhQ==&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVsxdRsxrYRzhdcS1XkQzSiViplJH6EqKAR8bcv9uRHtiKxmOfqiRZ3FdB2C0oG0NuUFdwnT_CEvdK1IaIooQ2lBPsqZa5I-_1jX567vr60YTfkNYMGYH55F3uTx5KqbMsYg==&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs3Y2VxLTae7c8c0ifmXbtNzISHFUql6zKuIeFooS0WXz4hxLkSv0Xx6NWJqmhemZAODqDe0BjFRGEgV9069MDpGj7WA159U2pfYb5uXZkWGVtt3RKMIGfIRQqddWuZiMdMwY9dZHTTzvhI1oO73LdoRIst5tSEzsqyv57eX1TwzA&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs2ZrcTVsyGZ4_q7cIIFB9hAaL6-ad04GoiL73bzgiLqgoQHPgG_xGCkCw1iITp6Sc9UDtBImzmzRoNF_LRBczPMNGFCPVT3827a_pSOrwOhbdRCXYgNByfS9_TSRXAUlrFRjzVNhuepJJBPtV8_Jly5Wr4vqjyI_agJNyuWvkJpl&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs6mdTetgER49G7JZAIKdVvDNeD59gdzHq-ZwXiHuVE_vUp3-wzN4NvHTUyUCRgeznRoJ1FJqGUZABni3N5YNJZpfGy-1yyfPDKOuEtPdIonq8UdeIq88Zf9F6EW0r5ElZw==&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs8kSp3lZ84azcE0CReTgtjsQNHYyaugfW8b7YgrhJj8r8jw63cwOj4athoG-yT5EkS-nne0MlhPlPfcoaGUTKjhIswOwgG1rxJdPyJ60MhX2UZvxz6VCHpEP5ZegGLLgBJY4jQGZYTujEjooc3sPmk8dnab42RWSTFGRpOFnozpm6MlSieJFPiILFQAMIkQY4BParAPORT9vSqvYN1V_b3Yf6Rrilg1t7Mqac-CsR4_ON1xjxdvz9GAii1N3I7FbJJmKM5RxQFIJ1GDeGi-nTWZiuEH_po4zhQ==&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
Buyer's Guide
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs6mdTetgER49ZfJ3dVY0t3pZhuaM2HFjRuKQ6Pi7o-tNxJkD32j_HgukUWngKLbrOykzY1AYSudknFzqZ_1Rx0MEO9K84hMZz7691fzCOVyRISrn_FZAPfuCyOJd5me3hiy0kDR2pKMYtMF2daqIdG4cg3PYQ7DIig==&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
Join AFSA Video
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs6mdTetgER49ITuYxaO-OnOnI1XyiOIOxqR3XB65YQ2WTJ1NkLvRRS_KI7dWd199PwwWLr1qqar7jcqX8uk7aq-EIAYdVNmAkRV5y3cVbi6r5isB2UOUVEFxmFQ8UTaOytD_tccIYEQwfur2AQLQ2ZpEtKL9IFYp7A==&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
National
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVsx1jt2ozJvD4RX0Lr_iZkHnT_cJLh9S0qmQwUfwbLSDYrFdzeZF1HWQew6hFpwxarYUmjZwB1UNGh8wJD2uGu22_WCAWFBUgo_EX4mrcQOhDGKNtbwLB2VHKDb9j-vNoaQ==&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVsx1jt2ozJvD4RX0Lr_iZkHnT_cJLh9S0qmQwUfwbLSDYrFdzeZF1HWQew6hFpwxarYUmjZwB1UNGh8wJD2uGu22_WCAWFBUgo_EX4mrcQOhDGKNtbwLB2VHKDb9j-vNoaQ==&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
OSHA Alliance
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs6mdTetgER49piBJ_FhRkT9tNcgCXzkXstJtnTqz-QWXbVYsmVM5k0DJj8fK8ONHoA3ysX9qQTAbcHTPrDBD2zAOsp9RyKfuGzpfwymIU2XXYo-Vt6xoQjTD9f-lYhd4bB52rUe3RUlao-1wrKPWhm5CgYutZJmEbA==&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVswQJbBOin4LuRCZOkk2OOjoVQY3R3BI_5wQZt9IRXohVGY7Q3nwgRr2EiFbi70pQEtxeFH3zExNuD-v0t4FJBA9JwjWmsU_DXyFRjFfHUwVsSegoUnzAfPpBSuXkGQsIn37X5cESZcXo&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
Informal Interpretation Request Form
[http://r20.rs6.net/tn.jsp?f=001Z-FxrFD3A3_1m5PEeep7lUIgw8e5MbtwYJcP_d0PvjZ55V52qoiVs8u0HHGNNiVKqRfzpQlPse29N58fTF43Xw1acxxcXSHk4i3jxA63fjAXmLHmbjRcU4yIdvy3A5pvNHi1XQ6BAPxOGLr9Z4hg7JrJlOBYavqR9_F9X_DYq4nTU-n70yIzrTX2IBvBNx7dC90mgLWe-F08YZtLm4dMm9G-u7_PHqti&c=Wlb9mdms-4WFtk1oH00XnVBMcSWJjx0q4oduy63500CV-b5YSovz4Q==&ch=KgmRujbwuGlbgYcwdWqmZ8cih-hcU1bVfyEUiINkGImf5HxR53A1vA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Join Our Mailing List
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1118033666438
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=4279f8b7-9a5e-471a-a0a0-c325dd3cc802
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=4279f8b7-9a5e-471a-a0a0-c325dd3cc802
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org