August 28, 2014
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Drain Riser Size for NFPA 13R
"We have a four story apartment building that is supplied by a combination
standpipe
system. The combination standpipe supplies a 2 in. floor control assembly
(control
valve, check valve, flow switch, 1 in. test-n-drain and gauge kit). The 1 in.
floor
system drain is connected to a common 1 1/4 in. drain riser. The field
inspector
is mandating that the drain riser to be 2 in. He states that the standpipe is
larger
than 4 in. so that the drain riser must be 2 in. Is it permissible to install
the
drains as indicated with 1 in. floor system drain tied into a 1 1/4 in. drain
riser?"
We have reviewed the 2013 editions of NFPA 13 and NFPA 14 as the applicable
standards.
Our informal interpretation is that the drain riser size you specified is
allowed
by the NFPA 13R standard.
This is explicitly addressed in the NFPA 13R standard in Section 6.9. Each
sprinkler
system shall have a drain on the system side of the control valve according to
Section
6.9.1. Section says that the drain pipe shall be at least 1 in. nominal
diameter
and shall be arranged so that it can drain all portions of the system. The
drain
riser provided exceeds the minimum size by indicated by the standard. The drain
riser provided is for the NPFA 13R floor control assemblies and not the
standpipe
system. NFPA 14 has it's own drain sizes specified in Section 7.11. NFPA 14
requirements
stop at the control valve for the floor control assembly. A drain riser for the
standpipe systems is required only where the standpipe is equipped with
pressure-regulating
devices to facilitate tests of each device. That is not the case for this
application
thus this does not apply. Main drains for standpipes are addressed in Section
7.11.2.1
where it indicates that a main drain shall be provided on the standpipe system
side
of the system control valve in accordance with Figure 7.11.2.1 and that the main
drain connection shall be sized in accordance with Table 7.11.2.3. These
drains
can be combined or be separate from the NFPA 13R drain riser.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKWoCKhTbytDTVzFugqrscpmm_lCTfwlxvXfXKICwjS6ma6r2yoAiHvPfzEdKy8Ibi0dfCf3-KFxAgbYSOHhWEoVey3Kwe6SopsttDk7_xa3_WOKpvtd_Qp79GucZfmVtCw==&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKcCVnkF7hrt0NjdAIoWG5lF-wbJFaZmrLUivFe5xfbzK7ld9qCPaDlJYHs1xXXgKoVoQVSlT8HpIiv8LrvPhepKLKwG4dSnjQ-WT5A1IOl35W1-i7tRC6XgjPdliJG0pwS6Ts3P07a9ti_Ay9IBWI7nGvQ9LOUVS94wDUgs_zLmEc07ygopOi6VYT_aBiJ1jTT9O_0cyFfmZOW-3mW_jlF4=&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
AFSA Webinar
Kenneth W. Wagoner, CFPE, CFPS, SET
to Present on
"Seismic Bracing Layout"
Wednesday
September 10, 2014
11:00a.m. - 12:30 p.m. Central
Free to AFSA members!
Register Button
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKWrmAF-tZDwZdW9mY8qfths9eFd1g3uB4iagJFRkbyGz-NfW-ziD6bDpRMvRrueGHcmKfdX_Tg6OYYKk9hUQENSrBvQyacFrOSchRN4xnUTiLYA400liO5OBE9yGDLkJYxU-Z_GSvop9lsuhpwro3UsZLs7LNaV5cwEEvugEPo3I&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
New Class Added!
Nov. 10 - 21, 2014
More Information
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKT5div0N57_EaQdtA4UgKL3m0hxLbzaOwCC-g8F-OkfBZBWOja-tHfP2L9n4BUBMi8-oJdcyfLurj64tm8YpCvwuvGomKw-uKpK48M4hPPqdBUJnriw77K5D-fnVpJZRLmk0-nGw6N1bak9Ra1oGfjCKSr7YRNkWWKwuKo1Ooxg6aOgZC6IXtyc=&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
Oct. 13 - 24, 2014
SOLD OUT!
Sept. 8 - 19, 2014
SOLD OUT!
July 14 - 25, 2014
SOLD OUT!
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKQySXcIzRhdrNoZW-lYu5nEuvmzyrCgiZlTKA-t0dOSj2vvGs-yg9b9QrxvGgJl4MmIlWvvpGeGA2rcUWTbMEhsqq6mw09ZYUatqvTCprBB2xAtzLiZ1Ln4p3uFFQ3E7e5arFn5jo1PtsWnAA6b_V7Algfqns9pLJJfUwGFO53ok8esqHBdVzuGORMTAZ07KkQr9VQ4-mf57PnBi5856qaGdKhNmMtVBwpdaZhYbLwxB8mqpKAOwpm1omgzLiTVsbrMjgSvU-DTW8mZVYAfOjWbEkUFF2dFfSA==&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKbrLIUSOsFVhMwzwYVD6LjPusdwRJvhqtkqtMtXoSmnN0R6dqjR-_a5ZLVbnnuMLfPJcLfIc2SE9xLxl9Sm6OJVDURFVoy36yqMPLHfyYYVLw27wcB0L2o1XHbwMaktWyA==&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKXbUa-LhGuu7R2V4s5teVHYHkg6E2ITLY9lQspGeUgOgS71qy95OlXS5MrC9pbhQkTGkbqBp-wBCAftcuzj5H4BWHIHeDRLlz-hKs5eeIGJWng9t2IYF-wZEFLVRAdubUx6v9LywIx6CeJBvD2J18-MOt7bM2JnT7g1DocEWKnBb&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKSPSUSw8boGezYZZG1SIW690HLQPo72FOLVdtM-1W3Z0w9KVoiD0zWNfb0wgR_hmbFygP1I9-ESpkzWGuciv0Q_ZvDu5cVl8Ckj1jkNYs4dNPeYsOeojb5Yrc2Toe-By5gUApEEuJ3EZ9G4-LsubTKcI2GL37xeW-qwh8PfA-HuE&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKWoCKhTbytDTVzFugqrscpmm_lCTfwlxvXfXKICwjS6ma6r2yoAiHvPfzEdKy8Ibi0dfCf3-KFxAgbYSOHhWEoVey3Kwe6SopsttDk7_xa3_WOKpvtd_Qp79GucZfmVtCw==&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKQySXcIzRhdrNoZW-lYu5nEuvmzyrCgiZlTKA-t0dOSj2vvGs-yg9b9QrxvGgJl4MmIlWvvpGeGA2rcUWTbMEhsqq6mw09ZYUatqvTCprBB2xAtzLiZ1Ln4p3uFFQ3E7e5arFn5jo1PtsWnAA6b_V7Algfqns9pLJJfUwGFO53ok8esqHBdVzuGORMTAZ07KkQr9VQ4-mf57PnBi5856qaGdKhNmMtVBwpdaZhYbLwxB8mqpKAOwpm1omgzLiTVsbrMjgSvU-DTW8mZVYAfOjWbEkUFF2dFfSA==&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
Buyer's Guide
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKWoCKhTbytDTAByRY30Xa3N2d5nXoPRxWB3aUo9dYN4Yv-hyjIsP6ep4Lzf3e5zikwr9Lexi-gXr3vP8M2YygQ23LBRT15m0gZXp5laV4nZ0C-Zffa0SzbZLURwANzNvlGhEzybVpnjZwbiKnbu5WmVrOk0E8h2NWA==&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
Join AFSA Video
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKWoCKhTbytDT9IIEcW3NN0pEyjH6TVxJfgvlSZAC62DmH3vguLpaFskkfO6JZPbNRD7jjHdx5mKn5oMbdkOMV-ypmyZef2cpNrOYc2W8xtN2sHhLZCXqqwgBbtpuLUGsWf3ZMFSYUR-qDC7aaW_M_x0TpAVtaP3f0Q==&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
National
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKS7sKUwcyGltI4VjIpwwnaMFXOtv6zwjvYaMb93Gd4JLvo-HTcAUwAoJEaSMDhZT5YjPe3bQmm-IeBO1KkUqNBs0zUtI1kYynkiFPdrugXiL4NfknursElal2gROJsJwQg==&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKS7sKUwcyGltI4VjIpwwnaMFXOtv6zwjvYaMb93Gd4JLvo-HTcAUwAoJEaSMDhZT5YjPe3bQmm-IeBO1KkUqNBs0zUtI1kYynkiFPdrugXiL4NfknursElal2gROJsJwQg==&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
OSHA Alliance
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKWoCKhTbytDT1djs87MVh3mJs6IkYPzPFc0OXjgGBCgcWoa9gy3L3zYkYcjKlGYkuE-NhJqlLEtDFsiWWAz7C-EaTZPdwlLDmMuIkiQdbB5-7ajyymCoi0OrvXiWfIIz9blL9ATdQHlhX53voZd20lVEXe85A7_q4A==&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKSwFS7CSrJbdeQ5iJLslbsksXNMaEo4NJJN-ZT5205PvMKlUtgHOIMuwoBnX4UBu1Od_DGhLOIUMN3yVqR7mIzoMtwW81yOUoSFylkj2Rt5MPec2NsivZXSjbns-GyNCN9YGP5hi1tiM&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
Informal Interpretation Request Form
[http://r20.rs6.net/tn.jsp?f=001DjCnpJ0i6kwn5WcgQZSPUatpn3xkjvNYuMfZHw6n_qVo6UdidUYOKc3UX81FALd0PyvV85-2UcSwa6rhIAWsPt9SChqt2G_R-IUK9oxJ8PGbNhoBbmKa49Y0aJVofCWKe7YR4BK5r3nicl4GRly65bwStoizEjoB4j1UHobHEvfxUJdJDIyojjcPTzRJmiql_LVjj958bwh9b2kl-bz6WNr_avIbOu68&c=hxxyQI_xJEiukb9cvgho2XgV-QzcNBsQy8NRwD_AeXHmPLGW7hv0kg==&ch=u2rxwnNn2D0Nzc6rP9Vs0fOJ5K-IjSqbKReRDrP7vY56qdufjKMGYA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Join Our Mailing List
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1118287180129
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=104d69b8-1df8-4e8d-8642-5db9fa4a7b11
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=104d69b8-1df8-4e8d-8642-5db9fa4a7b11
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org