Other Trades within Concealed Spaces

"In concealed spaces entirely filled with noncombustible insulation where there 
is duct work, plumbing, electrical, and other piping, is this still considered 
not
to be sprinklered?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that the systems from other trades are expected within 
concealed
combustible spaces when applying the requirements of Section 8.15.1 Concealed 
Spaces.

The purpose of the insulation is to fill the concealed combustible space with 
noncombustible
insulation as an alternative to providing sprinkler protection according to 
Section
8.15.1.2.7. The combustible concealed space is expected to have pipe, cables, 
wires,
and HVAC ducts. It would be rare that a concealed space would not have other 
trades
using the space. The purpose of the noncombustible insulation is to prevent fire
 spread within the space even with components from other trades within the 
space.
If the standard meant that no other trades could use these spaces, it would 
state
as such. Note that a change was made in the 2013 edition for this section where 
a maximum 2 in. air gap at the top of the space shall be permitted. This was 
added
to allow for air movement to help prevent the growth of mold or mildew 
conditions
within the concealed combustible space.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEneiHeTUSQVzyzINfRH3gesGcoVC-H2N592zqkDhVUSTw3EYCuE_30JXCqDF5rfRzBUX5J2mgsgTqJFkEAMV7zNRsmZdJYIOmPfsTYaK2oMXDJaIQBwhQtNGLPzxHj3TKgKQ==&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEneugF62DRuM7njUuXRjAXXOQUhEviLR7tUzm3iJRztoH5I5ZUaM_vXWdYfjE6j0t2hUh3_4S3NPzX6ulfGd0iqPi5W0wVo3D-Q1X9KQfc5nzwaB1BZTn6nnCzkN56kJ7gx4rQ0oyX1HZkDow5B774gsywlNv9ehYGkJNnq0hDNXB196i5RBf6tay7OU6TmQcSuXGQ0cB9qPLD45GmArqcukY=&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Webinar

Kenneth W. Wagoner, CFPE, CFPS, SET

to Present on

"Seismic Bracing Layout"

Wednesday

September 10, 2014

11:00a.m. - 12:30 p.m. Central

Free to AFSA members!

Register Button 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEnek_Azob-WMTc203Omk56Qg07InK0nV3c3AnxTJS_S8Kgra765rrI_lOhRqCCbgktwEWvONWDsJO-JAfFRdvl6kYN573taJlVYv2rw_gmnBgrm-iem4DFUTi5XZuT-ZdnqYrrJqv_1rzLZWRJ7Ol6DBsFs2dru3xVTRjLnyabAIiZ&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
The 2015 Schedule will be
Published Soon.
More Information 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEnehjZ8FVOiBnRBS9g1UPPygCiA3EMQb3DxRN-NCVSNFwSVwrO6ygoQsRewixLj1wPAtB2L_E5ZDioZuZKgG0OlrFX2iF4fSj0YdOrd-rt50678FHX91WXsMNKKaGwQYf6vbQ72NnyalZmUdbsbKaSmKaUPFey_Zy9XQzg3U8otAsV1RYPYPX72Fg=&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
Nov. 10 - 21, 2014
SOLD OUT!
Oct. 13 - 24, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEnek5iY_ru98c8dqEzZ8dky0kXChZOaC4TiiUKmSQga_EOM01K00iJasZrUTOm_n-XyhOWHqYAEN9WS-WUlcOS9UQJ_JCVFR6v4653xY3IEI4mmPj4ikqM6qDSfGY3bZdDWCHqkT_W2mbow4-M-AkPrCoGVrx_jjjSNsg0NSVYfc7Wtbiza0fw1nYvTctIXoWbX6b03klPYFDiHlWzgJnQM3ln676V-gUSQvqyZPgsW89-DJItYoRIMY6OxTmWGAg-9dTVUwVNchHrpauyBM4dIj-ehrF7p7OmQw==&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEneruq8tgUuAUy40hKEFaX1SuPrQHhGQFVc3RNMxfNbO3rvUZcT6-_eAKbx29VWVUPj5t-9j5280mqCU1GGIBgAOF9UaXeWYF6_BsxcEYTw3s4TZrXcMD6-sQrMmqLId0Djw==&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEnek1htE4LZtjRPL06p9222X51qasb8hSQbUs3mZ8xEUUvQezkagVZe1vBvYxt8L3sFL1X1nBcz9EakNnRiH_eS9idSBZpgZbL_Nio02VQjvwGKjahNH0AZ2W2QbI3Pv6DvxY0SzfYZ-bhg3Z9m4PRtAv7XqcAx8PwD5Mdt6iwI8Mj&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEneoh-NAbbQ2IGKa1kGQEdvZl2N7EXngzYC09uM10X4XHwhVnMBpBNhMnKSdeCfFSV-vV-zL8EDOsBRsfQLANKR4jzLdePIqPoFE4Xp2s9sF1X_tTgjNIOVQrxfIHOB1AiGR_Ej1qeM537jkGAzw3hrv6mSoplqKJnQbN9JlEisjWZ&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEneiHeTUSQVzyzINfRH3gesGcoVC-H2N592zqkDhVUSTw3EYCuE_30JXCqDF5rfRzBUX5J2mgsgTqJFkEAMV7zNRsmZdJYIOmPfsTYaK2oMXDJaIQBwhQtNGLPzxHj3TKgKQ==&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEnek5iY_ru98c8dqEzZ8dky0kXChZOaC4TiiUKmSQga_EOM01K00iJasZrUTOm_n-XyhOWHqYAEN9WS-WUlcOS9UQJ_JCVFR6v4653xY3IEI4mmPj4ikqM6qDSfGY3bZdDWCHqkT_W2mbow4-M-AkPrCoGVrx_jjjSNsg0NSVYfc7Wtbiza0fw1nYvTctIXoWbX6b03klPYFDiHlWzgJnQM3ln676V-gUSQvqyZPgsW89-DJItYoRIMY6OxTmWGAg-9dTVUwVNchHrpauyBM4dIj-ehrF7p7OmQw==&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEneiHeTUSQVzyzUnaF1zoE0r2ak4OV5W5GoP-VUyVciBCZE2wqzKtNOPsF7lFaBfB1oDtDI8PecrU1euo2bHC4jicovTq1xKSB3E8WHjX1GYBO1clAo1p4Nxeb3Ys9Eiai2qJNLkkZ5UaUtox7eLIVLrPPuPtHGLqjmw==&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEneiHeTUSQVzyzM3g46TuYqKNqe8OHqAnJJ0lqerG_egvd_zYiXw2yopXJdkWhogkewm8ukeWB-RtIUSQPfLpMb7Ii4O7npSQN3u5E1Y1MF7OiY1fk5PLTwokA___-P8HZ9Xvf9J_ywQW5Adjph18SGWDHf6KzS4shMA==&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
National  
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEnep-FF1rJdl1wHRX6au2kxL15SU-sg3lMSUgWUJwKNOfKFvWn7gS7pBwuiv8iLUFB_FWKueXBB0KwFm8s1m9z24ewNFjULhwQzN_9x1uZtUpOaZaFYZK-zeREQ2BqDucKCg==&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEnep-FF1rJdl1wHRX6au2kxL15SU-sg3lMSUgWUJwKNOfKFvWn7gS7pBwuiv8iLUFB_FWKueXBB0KwFm8s1m9z24ewNFjULhwQzN_9x1uZtUpOaZaFYZK-zeREQ2BqDucKCg==&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEneiHeTUSQVzyzsDa7audQrgkOJvLroLGoxcnj_wnrAYSR3_KtscIOVmmCgwgSVlrGYcTQYV7sWEEyt9ex46zx-9CJzcDqH_bACJkXq1W0F9ybJTevuxFu2i7lL4KnFjkk_vsh14eAkFH78ecGyPIg0zHei6lF-NDetQ==&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
Technical Services 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEnen488Qjx5n88NrRprTLOczVERZobmFPwFnDy0S2urXN4eQdIu6ILu7m42j5XajbTpFoNAHTWp1451ngo2X6OIR_OpYxY7Crom8tm6vmY1Zo4cHOurDOUjbVPE-Ku0L0ChYQD8TdmN-RA&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?f=0010mtnjNNz5WzOlNDj3pq1sV-HZZIeGHzXyy4mPD8oOQCGUJkX1tEnehrYZytmHppJE_B6iyjUt-AkSZKDxRSPcmxd8_K764hLyI-3BOXxokPXJBRrrB6VO-p1kKDvpAqXMlshYqHgMN3Ng4BV4Q6dqQRHk2m2mghPwwxLMZbegnOAMM7sh-W-WhaWFHs02hF9A7R4rhTIuhc-JcTfyWNEy5FFdW8C8SeW&c=YR_KXuvTz8UqcZJTB1s2rjSvImbLzQ87qRT8b-rt9K6BEmlJEPjpOA==&ch=ZSB39EeDEmZf2PJeFsC6qjmEHud7tBPKsp_37vPOU4pzjZZ-6ln1NA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1118350345430

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=344f76dd-ff66-4015-812a-d51848358bd4


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=344f76dd-ff66-4015-812a-d51848358bd4


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to