Mechanical Closets on Balcony -
NFPA 13R

"We are designing an apartment building complex with each unit having its own 
mechanical
closet located outside the dwelling unit on the balcony.  These closets open 
only
to the balcony and there is a fire damper located at the wall where the ductwork
 penetrates through to the living space.  Is it the intent that all closets that
 contain heat producing equipment whether inside or outside the dwelling unit be
 sprinklered with or without unprotected openings to the living space?"

We have reviewed NFPA 13R 2007 edition that you indicated as the applicable 
standard.
 Our informal interpretation is that the protection requirement is not 
applicable
to such equipment in closets outside the dwelling unit on the balcony.

Section 6.9.4 indicates that sprinklers shall be installed in any closet used 
for
heating and air conditioning equipment.  This addresses the closet that is 
inside
the dwelling unit boundary. Section 6.9.7 indicates that sprinklers shall not be
 required in closets on exterior balconies, regardless of size, as long as there
 are no doors or unprotected penetrations from the closet directly into the 
dwelling
unit.  That is why Section 6.9.7 addresses penetrations and requires them to be 
protected.  The 2010 edition of NFPA 13R clarified this position with additional
 text to read, "6.6.4* Sprinklers shall be installed in any closet used for 
heating
and air-conditioning equipment except as permitted by 6.6.7 (6.9.4 and 6.9.7 
re-numbered
to 6.6.4 and 6.6.7 in the 2010 edition)."  As such, this clarifies that Section 
6.9.4 does not apply for closets according to Section 6.9.7. Although the 
potential
for fire is the same for all fuel-fired equipment, the assigned risk is not the 
same for different locations and the standard explicitly does not require the 
protection
to be provided in exterior balcony closets.  The 2013 edition of NFPA 13R has 
the
same wording as the 2010 edition.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 14 - Comments Close on Nov 14th

The first draft 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOPsnPJiJWdZchhOb5axY7zbYY7p9TKkMM0CTBg9DBu7rdE3o6ZlBP6dpMX5fSkx4nZDPUiGP-1f0vkd26pHg3zXpr122wrWJOivSg8bCyp9BBsDfO7xT39jNFp5UXp4i3KKb1HbUwtTnJGI-3X6NH8FoinDbhhSnP68i0WXL083D_4KWg9KGkXjp7BA_o6UD0jKeWTE95pDtJ_CnGCXrqns=&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
for the next edition of NFPA 14 has been published and available for comment.

The Public Comment closing date for Fall 2015 documents is October 10, 2014 for 
paper submissions and November 14, 2014 for online submissions.

SUBMIT YOUR PUBLIC COMMENTS ELECTRONICALLY!  The Fall 2015 documents are active 
and accepting Public Comments electronically through the Electronic Submission 
(e-PC)
System.  The system will automatically pull in the text and will show changes in
 track changes.  It will even save your Comments.

e-PC System and Instructions.  Submit Public Comments by selecting your document
 from the list at  http://www.nfpa.org/aboutthecodes 
[http://www.nfpa.org/codes-and-standards/document-information-pages],
then Click on the "Next Edition" tab (see screenshot below).  You can submit 
comments
or just start and save your work in progress.  If you would like to review 
instructions
on this process, please go to http://www.nfpa.org/submitcomment 
[http://www.nfpa.org/submitcomment].
 For your information, a list of the Fall 2015 Revision Cycle documents can be 
found
at: 
http://www.nfpa.org/codes-and-standards/document-information-pages?cycle=Fall%202015
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOPsnPJiJWdZclh_iH5Zut71Tomx92G8nAgf9INn13iqAvCrVSjwh6eptg-8zrkvveYvh5slluK368R5-PPwS3lIP0fQEY85Bp4EgQguOrk0-Dwu5dzXoZHfpQFbFndZcWmdCGmEcnHbYgEW1DPgDmVcBkNjRawP7pZmRnaUkEt3bfuVJB_lkkPvqRX6cuYRh_FTbqg0x9FyrvsVJN1KmhyE=&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOI6YIeCqYt5DF4wV4yCAFAySJBDPhSAu5JWUW_sB_i7wPakpAm9rSSK0ebTcKrWnMxWGirEjbFMd5eEqWpCHO_Fms4iKknwL94g5Rdzgd7PcSH-BHFA9H4RV_DhLlkeONQ==&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqON--3657_Q0b5Xk9YLafA7Ow9GYNq-yo2aKrSybRKYzOoQd3QHgngFnJFBRBvvRaAjJKLPjrFuj5kDOCO5H5j4A_R7ynx3NlohNin-LOWaJZRacP-iVdCNgsujexyadl-UzLxqBDEslk0tLSYi-4sMQNLorhKm88LQKCflBHzqGVqLDEShQMEukjU2JBLgKGv4WTdVlnHhJZnhPsUt3fpms=&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
The 2015 Schedule will be
published soon.
More Information 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOCjBMuKsdEFqlJf11rrcJHA2z-jzYUmEFlm4qnD_ydWXR5QVyxUvbvwTKrSQUEbBFk016E10orbdKi1hk5bEt5Qlp_gsP_-hM7GsTcCq3GlN25mZe9-iJp1zg7EPak3vrrQWqgsV7xrpv5GbmB0jodtKUeBQeJ8h2hO1hCIrvbXdFS6NvUvd7To=&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
Nov. 10 - 21, 2014
SOLD OUT!
Oct. 13 - 24, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOPR9eJ95OAYk8i3mEkFxP8QGSb_fGas0cmw4pzwAnpPc1A8iFsdnbAT9OV4iA-CZTJt1Xrd9wxwRqHBLJOoYmFAFPi38VYPKL90m7DcxlJdp6BR8HFWcyYnRSIpOnuej3wkMR6XpbgPa7r9KxyVzLFvNRACOnJtj7y4kDBF8EWJn2lsmcENoTYWUd93qY_rH08o1w3ADbKX-6llfMIx8wjs0C3vcilVjSDZlwV0_WFKZeJZfi4WxoP8s5vPRNNofxiHTukOmxJO-i8ZX1VXCdOq5-73fHveuWA==&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqON5ibMRLZrGaTOSvYkCbNfXFcZEfM0KAbANkNIphmHhjka0BS3OafiGBWSt-vJNI-LSVgJRZgY1klOh-GDactGQnmyRfOU8znWWspUWaKMkbKgs2YKQ9i1QI7I4aLm7BKg==&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqODmYXRuzs9kiMZHb-7sI5GdgdRbFU62EFShryITVwVuIX3tSmLXxjSgFVqhLhx-2vncTBENDQ2vgv_YVtR27PryLWjmsiUKo_bBR2zwwtqfr2cWA_X2OHfqloXuc1moZ_y0C6eCuGz_SCD5awxwU17VUtg1QPwIejzk_9RCGB-ye&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOOr_BacWfHTslnalmv1ZBjdFoBofdaIY-wT3Q4lH6FQVjbhKJvVbjd3nAPjwVqVQpqj-BkZoKcfv5D14xFErCwhQ4c9WwJP07KT5VENRGFNjOoLXY8gFEGnuSxlYyZEhTKeT44uuyOZtcpAn6_h4brI5EVEI5Abij4C1cfDn1G2K&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOI6YIeCqYt5DF4wV4yCAFAySJBDPhSAu5JWUW_sB_i7wPakpAm9rSSK0ebTcKrWnMxWGirEjbFMd5eEqWpCHO_Fms4iKknwL94g5Rdzgd7PcSH-BHFA9H4RV_DhLlkeONQ==&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOPR9eJ95OAYk8i3mEkFxP8QGSb_fGas0cmw4pzwAnpPc1A8iFsdnbAT9OV4iA-CZTJt1Xrd9wxwRqHBLJOoYmFAFPi38VYPKL90m7DcxlJdp6BR8HFWcyYnRSIpOnuej3wkMR6XpbgPa7r9KxyVzLFvNRACOnJtj7y4kDBF8EWJn2lsmcENoTYWUd93qY_rH08o1w3ADbKX-6llfMIx8wjs0C3vcilVjSDZlwV0_WFKZeJZfi4WxoP8s5vPRNNofxiHTukOmxJO-i8ZX1VXCdOq5-73fHveuWA==&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOI6YIeCqYt5DBA7dP9Cm42zDsPBIffbXXQi7lC65DbniYC0verc72ZZjyQ_7eJPXkL-V194eCKEMaoTOtzURR9YZ9k4aDR5wC8hoAVw1ifax9cuLECT-NaTRzCqkrDDDqoWtsDFJLB4ACyUeiYdeP3UT7AjD-RuH6g==&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOI6YIeCqYt5DumG3ENQkGrsrjs1N-Sw_-D-qcRdsGlHsHGeVJbs8LXNKvP0Eyn7-O9E6PzlYi3IaPgevEpkhs7mpsxJ5H4W28BUHTmI2uComTM6IjTXTfSz8sHJ8C5hxnkSRwih-glpFUGCZZHG1BH63G6Isrhhh1A==&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
National  
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOGEM8LqLXrFaSG9MT2ArpFq_YjKfoyCDeWQ_EjDq9JeVlHuNtgVNeF1tstRxZbLRJJ5uz-67scmvtkdTDGjzJczfvhUDCZiVCw_JWl7W-ZS_mkuSev6GwM4XRZTkZBTaVw==&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOGEM8LqLXrFaSG9MT2ArpFq_YjKfoyCDeWQ_EjDq9JeVlHuNtgVNeF1tstRxZbLRJJ5uz-67scmvtkdTDGjzJczfvhUDCZiVCw_JWl7W-ZS_mkuSev6GwM4XRZTkZBTaVw==&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOI6YIeCqYt5DgFoW4--N8nffT_VCKpnIBf9k2g9-5byFAQD-Vx8rWmPkIF_kpUAYpmzUAIDt-2qnYzECWIiOSJwMliGfKNNCFjYgg2p9cmriprsuMptUNvb4SyaLf1KLwjeCinjlnnpOpAcHAdlKHbQ0kJKO3KGBXw==&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
Technical Services 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOMZXaYh_4PqLq48XGT739ocbEb6vmWKyZiLcYQ-860p_d9y9DxtWxfeHZBeZiem66OY4srSGR1uYLY6SgXpYuW_atGPCNZw7qVd1StD9k7UkFNnpK-vEQolzxYll-szmzwnqCaf_DU3s&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?f=001WUYuCnEBNwxhNosUKKGjcHFuIqshO8KdzWc5enkxgz8RlUgJdAcqOBnhbKm7TqFcr9s76WQeLFkQZePaQTp8xuIr1ZVBMZg5maa-NJwbXZSFo2N2McRW91XuY6fHt2nc2m3k25xf7i3PB3PRDxdeHbH3hcTubfBgnpVykkpFakNRmRE7B6rVnDeO3oDrx8xeD8S7Am225lWFkrKbjacgHtlnWFPC1XS6&c=XDx_xkimYBIaGggENGycoJnrBqR4AVSF1qD2URM7V4_cy0VCdhg-NQ==&ch=aatR9cWcYKR2qEPefiekONE3WBosdjCBvjCTxpZfQTDFERHYdrPJfQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1118669315132

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=804e48d3-ffb1-4370-98bd-26329793094f


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=804e48d3-ffb1-4370-98bd-26329793094f


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to