Commodity Classification

"I need to determine the correct design criteria for protecting synthetic iron 
oxide
for palletized and rack storage.  What criteria do I use for the product?"

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that we cannot provide engineering or design services, such as
 saying this a specific classification, but we can elaborate on the criteria to 
help you make a decision.

Manufacturers generate a Safety Data Sheet (SDS, formerly Material Safety Data 
Sheet
- MSDS) for powders, liquids, or chemicals they produce as part of OSHA's Hazard
 Communication (HazCom) requirements.  This document can be used to determine a 
commodity class or protection criteria.  A SDS has 16 different sections to 
address
the characteristics and identifiers of chemicals.  Regarding this application, a
 synthetic iron oxide is a pigment used for coloring of different items.  The 
SDS
has different sections and refers in Section 2 "Hazards Identification" a yellow
 to black solid that poses little or no immediate hazard.  Also, the SDS 
includes
Section 5 for "Fire Fighting Measures" that shows the Flammability Properties as
 "Noncombustible.  Not considered to be a fire hazard."  Thus, the material 
alone
could be considered a Class I commodity.  What can affect the commodity class is
 the packaging of the product.  Annex material A.5.6.1.1 says the commodity 
classification
is governed by the types and amounts of materials (e.g., metal, paper, wood, 
plastics)
that are a part of a product and its primary packaging.  However, in a storage 
or
warehousing situation, classification is also affected by such factors as the 
primary
storage or shipping container material, the amount of air space, and the 
location
of the hazardous materials within the container.  For example, a Group A plastic
 product enclosed in a five- or six-sided metal container can be considered 
Class
II, while a ceramic product heavily wrapped in tissue paper and placed in a 
corrugated
carton could be Class III.  With that said, there are examples provided in Table
 A.5.6.3 to narrow the commodity classification.  The table for Bottles, Jars 
filled
with noncombustible powders gives seven (7) examples to determine commodity 
class.
 Use that information for the appropriate storage chapter at the specified 
storage
height.  Section 12.5.1 indicates that for dry pipe systems and preaction 
systems,
the area of sprinkler operation shall be increased by 30 percent without 
revising
the density.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 14 - Comments Close on Nov 14th

The first draft 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a7R7Whv--13eU9CMZZQQZVz4sCViNVlyqlRoVA8ogrTyFwt2JwmAQ7VV5gQhTY2GdTNSs9MkS687kzKdqCfI9rh6QaaaUPJfSW0xX0oLCXUcUnYPWl41Cf1nZ0tUyGDVDFiihYt2O1Zf1gqqwUuR2h8RihTEhfvuQg_PybbJJ4Kr38Nq878nbk_Tjbx7x4XmftTv0yndbuE9Xz0cXudKMlA=&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
for the next edition of NFPA 14 has been published and available for comment.

The Public Comment closing date for Fall 2015 documents is October 10, 2014 for 
paper submissions and November 14, 2014 for online submissions.

SUBMIT YOUR PUBLIC COMMENTS ELECTRONICALLY!  The Fall 2015 documents are active 
and accepting Public Comments electronically through the Electronic Submission 
(e-PC)
System.  The system will automatically pull in the text and will show changes in
 track changes.  It will even save your Comments.

e-PC System and Instructions.  Submit Public Comments by selecting your document
 from the list at  http://www.nfpa.org/aboutthecodes 
[http://www.nfpa.org/codes-and-standards/document-information-pages],
then Click on the "Next Edition" tab (see screenshot below).  You can submit 
comments
or just start and save your work in progress.  If you would like to review 
instructions
on this process, please go to http://www.nfpa.org/submitcomment 
[http://www.nfpa.org/submitcomment].
 For your information, a list of the Fall 2015 Revision Cycle documents can be 
found
at: 
http://www.nfpa.org/codes-and-standards/document-information-pages?cycle=Fall%202015
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a7R7Whv--13eh5TCzVyPe_680m9yoR6Dx2nUswuSeDZCwSExkU9kdjDpiyL7Wx-cpBvBAaf8RPzyuVV8-A40669bUU7NtYDNE7-3VxfxOwU6ryQamOOfliF6txvONoXY1oIbtFABiP-hEC-2qJS7QB4v9b9YkbyuK8ZZ-iMG3S89tLA6mLOdPtVF5qef24Uu8Djg5UZWcySYVeMCb82a1CM=&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a82nFbjc82-JoCmUcYnfekg_ZkjlXSJim50TdDB94mrHw9HsbDwo68Xgztoeq-HcGJa6PXdOBnokmO5djbk4MdJQSbs4VRONs4tCTk6r6Ga2Zd-LL0B87Y_lttjc9MeliA==&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a_lk4wA0OnKvumjzaKLWYutDLGzIsismyqQbwZCfC7GDtebvjc5qh0OF5I8ZZCi7nbaNIPqzk4b67kvBGUGLpNxHwj6hFxfiymxUyrrvuXrKz7i2_g3ozpc_l2TsIRcY_rjuTkxtdx-3ZwASwHInTUOJTHM9O6pwssdo8dberH9SipcnPRv-t8H905HO_cXjRcVla2iJ5v7eXdruvQsUqOg=&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

More Information on OSHA's
Safety Data Sheets 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a_lk4wA0OnKvg5Fw5eyOeHREfw6oMnU9YaINL38T95UJ-ZP5e8HIyG0yzRLmDdqWEgqv3R9eL6qdgQMRizjy0B3PEjr2XhhR_zDABFm64nN9wBzgofrkLcRDZoyDVLOZyyujmf0YOAPguTV9PDeTA3ewO7eqO_80IKqzIuCAXMRxkRj503wBrdw=&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
The 2015 Schedule will be
published soon.
More Information 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a1nktwtnZuUl95h0VTaVrAYkI912sHR0t0Ee_lOT7RX1wbmfCoZSw5GlMtiBbAn59LKJw_co9IP8eMgmafWLWZKCDzPH5zI_jpRJfxLBnF5h7cFsKUzctzdQH0NXbb-_yokxysUZnbwEc_Wm4o5mOaZBW5YcvhwZLINBW3Ka818HgLwe2qF0SjM=&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
Nov. 10 - 21, 2014
SOLD OUT!
Oct. 13 - 24, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a8nQkxO4UYu0mxFJqf9PlR0hLX2FoHA5Z7wDIupSyx9RGm4mcM5CNQtRo5W-dNV2ZmAh0gfzev-IqPbWPslNlalBYC3vxxm9nef8yH5OhJTIwERbgt53FHe-LZJe0E5B_cHl4LJcrt7kI8P4C0xQ6AvnuFH-NakcdHUseP348b1XlNiYNgvqd5jp_6o6srJjnYUb6_f3vxWV4OtbQ8RWX0FoM59n0LRCHHnxHZpufh1tnktn9Zi9qCKmw64efD_bO26-uD6L1GRpLdqWDLbmC9z_X2IjJIomSQ==&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a9M35mQPprUNdDP0ZyRtBuu-DfF0eZV2vfkGXStoN2f35630vko5OzyKZLhBsbxXbwhPkr8ORsfF4Mj-SkBjRD4QC2H3zT0D17u-i4AX-Pfo_8vy9BKXUBB78100Oe5TNg==&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a3bblBoNocL8f-blRKEiK6iyDl7vpwUfCvJu39BcQ-kR7CLVfE7R75DKOdwXvQ2HSaCClaFSusU2X0nqoWzVN4rO1yphjJ6wBZfLqCklgFELlhaWVrsnq_sjyPcRxgpU5ZMKNiMSWJ1lZx68wh6kul08ftr9e3BzG60Ap7QXUeiz&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a3t2D-aQ1fjCGPaspZw5rhmJtnf0iH4kr6356Rs9wDWrRjdGrt-aK2T-ckr1qgm1-WUCnO7Sic5cHcrUpiTSi67v3gd1Txw0d_Wxc1JgcsHKrYiIj3534xxsS-3TPfLU-kwbl6GKKLZQBR_jJ4_TzjtnAMMLDvSCqJkKutBmQd90&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a82nFbjc82-JoCmUcYnfekg_ZkjlXSJim50TdDB94mrHw9HsbDwo68Xgztoeq-HcGJa6PXdOBnokmO5djbk4MdJQSbs4VRONs4tCTk6r6Ga2Zd-LL0B87Y_lttjc9MeliA==&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a8nQkxO4UYu0mxFJqf9PlR0hLX2FoHA5Z7wDIupSyx9RGm4mcM5CNQtRo5W-dNV2ZmAh0gfzev-IqPbWPslNlalBYC3vxxm9nef8yH5OhJTIwERbgt53FHe-LZJe0E5B_cHl4LJcrt7kI8P4C0xQ6AvnuFH-NakcdHUseP348b1XlNiYNgvqd5jp_6o6srJjnYUb6_f3vxWV4OtbQ8RWX0FoM59n0LRCHHnxHZpufh1tnktn9Zi9qCKmw64efD_bO26-uD6L1GRpLdqWDLbmC9z_X2IjJIomSQ==&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a82nFbjc82-Jk-y7P1ZEhPvKAAnZb5HfjSeETqaJ529-vUX5gmn2gFHsY0620wqULx66aJVHm1x08NV17bnxZxhSh-P_4Lcfd5ol7LvZaW_h36khgU8ubsBgwP5Bn9q89Lk700jYX-YuA76FfoUagdHrOOIrzfqVdg==&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a82nFbjc82-JWrG8-UvS1qyEy08BYqh9g_Y0de5mtsMJwGoPW85pumvLNLT9MFV4hmPG4r1OCR75T8xBoTE5YMFqGc5kEJNn5Vl1bLbV0kfmSX51r9Xr0pqNweOCqSHfMoz5gb5awjomtpgHihRp3aUj6LbFi8KXug==&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
National  
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a2r-PsqitTrnuWBNXI2KbzuqlG-443D5di6OcXP3s_ciD4oXmKh8fmOdoY8KDpizHBu8fLQGXmVKdHU517d1fP5ermBKUdCT6fIlK4nVwXZX5ViAMKr5XLmrRwIW4uvg6w==&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a2r-PsqitTrnuWBNXI2KbzuqlG-443D5di6OcXP3s_ciD4oXmKh8fmOdoY8KDpizHBu8fLQGXmVKdHU517d1fP5ermBKUdCT6fIlK4nVwXZX5ViAMKr5XLmrRwIW4uvg6w==&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a82nFbjc82-JSeGpGS0IpncRhOt22Xts1Q4ImUcHJIMtzNAGCpXY0k1fURwH3YUo5fLDvmkok6eD6LWgqHskjLaqtxAdTRtXwfmMyFiQYuxyoH0Qk62hSNBlzahdK8y0I2nhj4f1W4h7E0lOGjzTruWy63r6Ziw-UQ==&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
Technical Services 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_axDsmtZd4UHKH7rWO9SZywmAyOOh7ZY-0LLk4wmcREgzHuPpSdzFpJRPKLD8_zOC1B5J5zjQbqgQAJ9J1Hnimq0LpfV56UXH7Awg6BuNmxTS6sAjEv-4QhOpUfJDFm2FIcf4Ddb6jXti&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?f=0013IbWxd2wFQqVOD4GFMgEgq5n5LnY8bzMbmIfH6Ujl5tjtaqEtCX_a2RF-dNRA3DLMyMcZssxapgsMIyFxo0dx3u7Wxw4I-YemCvGO6Nw41L_YoYgLGs3rzCB3UqL2QG7Mp9PbAGfgGAu4rRb7uKCC5rqvwRmaswCA4HRrhcv8qWmtUSmkRpv2Be3AsudxgzPMmSNbTVgjZx1dvxTf20VpZo0v6PCbxqs&c=js__0_TKB9EM5NoUBzhwbuBGyf40hEAzDNW53xINOfKmCxS0CAVOjQ==&ch=o1w00WvkjjmSHeiVHD0u__2sFEsiTLLOFMrwVxOPRLtUqAROvOYYIQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1118719540506

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=8b3fdfff-6055-46e3-bbc7-0f5e3f5bc0e9


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=8b3fdfff-6055-46e3-bbc7-0f5e3f5bc0e9


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to