American Fire Sprinkler Association

Monday's Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A weekly newsletter dealing with codes and other technical issues

October 27, 2014
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Dry Pipe System Water Delivery

"Do dry pipe systems require the use of a calculation program to determine the 
time
required for water delivery?"

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that the use of the calculation program to determine initial 
water
discharge from all dry pipe systems is not required.

The use of this calculation program is an option, but is not required for all 
dry
pipe systems.  Starting off with Section 7.2.3.1, it says, "The system capacity 
(volume) controlled by a dry pipe valve shall be determined by 7.2.3.2, 7.2.3.3,
 7.2.3.4, 7.2.3.5, or 7.2.3.7."  Thus, the standard is providing five (5) 
different
approaches to verify initial water discharge.  Since the "or" statement is used,
 only one approach has to be met.  If the statement included an "and" statement,
 then all would apply.  The five (5) different options for determining initial 
water
discharge are outlined below:

1)   7.2.3.2 Initial water is discharged from the test connection within 60 
seconds.

2)   7.2.3.3 No time requirement for initial water delivery from the test 
connection
for system sizes not more than 500 gallons without a quick opening device.

3)   7.2.3.4 No time requirement for initial water delivery from the test 
connection
for system sizes not more than 750 gallons with a quick-opening device.

4)   7.2.3.5 Size of the system is based on the calculation method and program 
for
water delivery at the maximum times listed in Table 7.2.3.6.1 for the hazard 
shown.

5)   7.2.3.7 System size is determined from initial water discharge from the 
system
test connection or manifold outlets (1-4 outlets) is not more than the maximum 
time
of water delivery specified in Table 7.2.3.6.1.  The use of the calculation 
program
is not required for this option.

Dry pipe systems protecting dwelling unit portions of any occupancy are required
 to have water initially discharged from the system test connection in not more 
than 15 seconds.  The options outlined in 7.2.3.2, 7.2.3.3, or 7.2.3.4 are not 
permitted
for systems protecting dwelling unit portions of an occupancy.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 14 - Comments Close on Nov 14th

The first draft 
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmjX4NTsOAtER_zpPUe2ngUKO9KbgBsxxiyTp4VX_WfkuKbtds5--3U0_J7tvu38M4lBO7C-3yjsnn4vRFMiiUJOHV4F6w7DRbX5tnG5xscTOoKET-prnAQlJy9CQpKLoDh8j2ZW4rcO18s6mJqvIiE0tJzQRS2oubZU2FTQS7cllbAKUTvBjI4uvPDYI9sD_NKjjq0idqgxUKdBXjboA0To=&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]
for the next edition of NFPA 14 has been published and available for comment.

The Public Comment closing date for Fall 2015 documents is October 10, 2014 for 
paper submissions and November 14, 2014 for online submissions.

SUBMIT YOUR PUBLIC COMMENTS ELECTRONICALLY!  The Fall 2015 documents are active 
and accepting Public Comments electronically through the Electronic Submission 
(e-PC)
System.  The system will automatically pull in the text and will show changes in
 track changes.  It will even save your Comments.

e-PC System and Instructions.  Submit Public Comments by selecting your document
 from the list at  http://www.nfpa.org/aboutthecodes 
[http://www.nfpa.org/codes-and-standards/document-information-pages],
then Click on the "Next Edition" tab (see screenshot below).  You can submit 
comments
or just start and save your work in progress.  If you would like to review 
instructions
on this process, please go to http://www.nfpa.org/submitcomment 
[http://www.nfpa.org/submitcomment].
 For your information, a list of the Fall 2015 Revision Cycle documents can be 
found
at: 
http://www.nfpa.org/codes-and-standards/document-information-pages?cycle=Fall%202015
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmjX4NTsOAtER5r-bfIO7iH33YG2bglR32lltJE1LoATSSXVCX5ziwTlysAqbpO5hU-aQIGRA8H8Y3RFoLGIKMJYqe07mPw-SGeIXPxchcECDnB6ZD6d5daXhsTE3kDcD4h00IQVGfh698dl7i18b9407_sv9RoyPEM_MENrKkVB9KtkYeytSGBXc7_U9e4BRH7jG7cSUnpNWJpNfopk_nN8=&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmoCVBZ3qaj-9zDr193rweIhYkn04uOzDs0-4fVY5G3_ajUX0Sv79GOLJKvwFJE7Xxvm3rML-ZIxJAxqgCV3dUos5sF34blK1tUV_x_MRRbkB7sh7QCk7rXvblsOMAzQ6ig==&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmjtWaoD2I20KJNvTf3dWMU_wH75UoAgPxwIyAGTFNjFvpjqooHjlVYoAqSzexD6BOxJyH3fd0hPSbmBlKsuUHeTvZ5eLWaolZezMxXH7Dbt5Uqt_APRDFhEBt8x_FklR_Qqv337qr9P5ZcLTi-bAas5Iur0vSH25k4iV7-cYe7MWHF6AzQDYa7IV4cgKuYwFjA69ZyVX5KrCDrLWN3ieMQA=&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Webinar
Advanced Technologies in Clean Agent Systems
November 19
11:00 am - 12:30 pm CDT
1.5 CPD and 0.15 CEU for a $15.00 fee
Register Button 
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmtihEhlodOP-4BuVGwq7JXByu2-h5UMByLh6Pbo4JFUR0hx8R4lXnGFlFiFgXilj68kgxSxEs775JLHHqMTy-stik2ozCRUzjvzJfX5d-EdTNFXZ0iq6e8kVkjU9c520Qyltv-rEiQ6iHJVp6gQghrZdG09qRSunnDb_sCJPsHWU&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
The 2015 Schedule will be
published soon.
More Information [http://www.firesprinkler.org/education-center/schools/]
Nov. 10 - 21, 2014
SOLD OUT!
2015 Dates Just Released!
January 19 - 30, 2015
March 16 - 27, 2015

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmmI7Zp3q0mpKGJR79duvs0z-MjDtWRbbx2jJBkMQQRn7FeIqMynTvcKcMn93chaf_IfBSv5ODUexiISmmTOxuLHy2x4mJMNf83xmYM8KdYYd3tKPttQ4NMXlpQFNAzpbhA==&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]
Join AFSA [http://www.firesprinkler.org/membership/purchase-membership/]
National  
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmvb9uB4ek9vNJl4xZAo96-CpGjc__CXAkJHM3k2QrjX7xBS2rp77Qi4qwTHBVTVQ4KjDjg7RvIszTwykRXJQGjPMrK0cIBzKdtTvH9xTkaj4IpCPuFyZ2J6d4WwoBNwS7A==&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmvb9uB4ek9vNJl4xZAo96-CpGjc__CXAkJHM3k2QrjX7xBS2rp77Qi4qwTHBVTVQ4KjDjg7RvIszTwykRXJQGjPMrK0cIBzKdtTvH9xTkaj4IpCPuFyZ2J6d4WwoBNwS7A==&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmtihEhlodOP-m8O2srmIx689o-OwFeXUyS-KYvqDll33vyb0ZDEwMuWnV-YuUcI3_zRHYvvJUSN6dAVEhNBZITY7irqUDWU-U2FnNycgqZ4ah-l-SyGsCE7XG7sfyXjBr2bc2PA550nePoR8LTmfsrvTIWithRDCVmeUrdWtGm7p4NqV6zmgZxc=&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]
Technical Services 
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmsmByvRqwDKLRgRdNlzLnhbRL5Zu3gAmdmzHSTa4ddIaD1BDpbgUH_KJk7gLRVKOeRI11TjmAJ5QTV1woNizx_AqOAztJEWeLeYwJd_2YwojcJWtnz_0DGufpZyXZomQdoQz0M5NcvFsE_PGVASAyM9nR1f2aIzfrw==&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?f=001SVYag5mmFz5WuZxx6gtxFjk8u4aF9Q36iXMXj5ePvt-YW0yLG0wFmsmByvRqwDKLg-aN_4czOYodaKHDiPeOKHBaLdEzM2-MQgBeSnmMg3skrrUd-U39WuAD60_qOjdMQsFCFhwkNpU6k5st6HobEiBF4I2uT7WM-ek729Rm18gnJWfD-mLtPWtuxlII4epSEkO8r8f7O2McAcOTKgt1vOE2BoL7tCEMIVbbN33KUyMlgaHMP5VVmg==&c=B9yzO0ruhUztice7fvVpQ94lBzkflKWp3VFwyj4tAHzPn234fQcCxw==&ch=jyi4Z_RI4iDj9XRQdWcjbaQdIekyw9A2rJt2GEHj4U5IHNcQvEcSSg==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1118953100771

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=0da7dab7-2141-4c53-a283-4679b4e81ec4


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=0da7dab7-2141-4c53-a283-4679b4e81ec4


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to