Concealed Combustible Spaces
"Limited-Combustible (Material) is referenced in Section 3.3.16 and also
Concealed
Spaces in Section 8.15.1.2.1. Will it be allowed to frame these components out
of "noncombustible" fire retardant-treated framing and sheathing, eliminating
access
to these interstitial areas, and installing the gypsum on non-treated wood
framing
down to the concrete?"
We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal
interpretation is sprinkler protection within the concealed space is not
required.
The omission of sprinklers is allowed by Section 8.15.1.2.11 when all the
exposed
combustible construction (framing and sheathing) consists of wood that is
pressure
treated at the factory with a fire retardant. The annex for this section says
that
the allowance to omit sprinklers for fire retardant-treated wood requires a
pressure-treated
application. It does not apply to coated applications. The Automatic Sprinkler
Systems Handbook commentary indicates that although fire-retardant coatings are
not included in 8.15.1.2.11, nothing in the standard precludes the
consideration
of the use of fire-retardant coatings under the equivalency provisions in
Section
1.5. Note that fire retardant-treated wood construction is not noncombustible
or
limited-combustible. Noncombustible material must be incapable of burning and
fire
retardant-treated wood does not qualify. Limited-combustible material must have
a potential heat value of no more than 3,500 Btu/lb. Wood, even when fire
retardant-treated,
has a heat value around 9,000 Btu/lb.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
NFPA 14 - Comments Close on Nov 14th
The first draft
[http://r20.rs6.net/tn.jsp?f=001vCupDQ0djHkUuwytLdrjaIlJPKZcmOoAEfmpSZp8Sn24CQkbHHtiRygKhmM_jQ6ng-nNkMHNPY756g13f6siqGENpcOwLjO1daUWR9uWUZiHKWWVEN0TAgaSm7MHYo-XSUqlv4rJrh8KnJj-wkm8PdjHNz9MMxwf7pYk8-4V2g5WeX9t8DPb-eXCFuUJ7crNxCqm21AyFY8Z6cuNUeA6v5z-0EQjXLRhOi1vk731r7AjoOHQED1wPjWo5P5SmDCbJ-7meUCuy6g=&c=6RrWNwOxdDhHrzeIc9j4b6G4YgfJIs0XqUWntQH1NbyAxZTDWr7clg==&ch=j-Wo4d7GeHzKp28oSKjpprcRzOwst2nzOCNqRtIhBf97WnzK452Sag==]
for the next edition of NFPA 14 has been published and available for comment.
The Public Comment closing date for Fall 2015 documents is October 10, 2014 for
paper submissions and November 14, 2014 for online submissions.
SUBMIT YOUR PUBLIC COMMENTS ELECTRONICALLY! The Fall 2015 documents are active
and accepting Public Comments electronically through the Electronic Submission
(e-PC)
System. The system will automatically pull in the text and will show changes in
track changes. It will even save your Comments.
e-PC System and Instructions. Submit Public Comments by selecting your document
from the list at http://www.nfpa.org/aboutthecodes
[http://www.nfpa.org/codes-and-standards/document-information-pages],
then Click on the "Next Edition" tab (see screenshot below). You can submit
comments
or just start and save your work in progress. If you would like to review
instructions
on this process, please go to http://www.nfpa.org/submitcomment
[http://www.nfpa.org/submitcomment].
For your information, a list of the Fall 2015 Revision Cycle documents can be
found
at:
http://www.nfpa.org/codes-and-standards/document-information-pages?cycle=Fall%202015
[http://r20.rs6.net/tn.jsp?f=001vCupDQ0djHkUuwytLdrjaIlJPKZcmOoAEfmpSZp8Sn24CQkbHHtiRygKhmM_jQ6nTU8fjFRXlL6QMRDTPyAGtJyPW0XH-JWL3F2oys16l9zhlmg7Fes14TASM9fxYGJOVGJvP4hlT2gXVBSmvLNbvb9CAxshKK9GzzOALRUdkAwR-HXrvLQsiQi2WuzkYiFI9vE3lx6yjVt-nqvv4dET423n7cTgKd0L596yCFb_HuuKhdMof9a0BihjEc7T--Gxm4r5kksuCFw=&c=6RrWNwOxdDhHrzeIc9j4b6G4YgfJIs0XqUWntQH1NbyAxZTDWr7clg==&ch=j-Wo4d7GeHzKp28oSKjpprcRzOwst2nzOCNqRtIhBf97WnzK452Sag==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001vCupDQ0djHkUuwytLdrjaIlJPKZcmOoAEfmpSZp8Sn24CQkbHHtiRxZIs9jeNWyKlwonHluHD7s4gkSBukY100V_w_3sX1u66msrFqbny3C4u1MIeiAOpTzUk2lme7PyCq3EzIRECGAURxSns_QVd9DFIV2IiAVetURstTzK6EfreJ7QwC_76w==&c=6RrWNwOxdDhHrzeIc9j4b6G4YgfJIs0XqUWntQH1NbyAxZTDWr7clg==&ch=j-Wo4d7GeHzKp28oSKjpprcRzOwst2nzOCNqRtIhBf97WnzK452Sag==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001vCupDQ0djHkUuwytLdrjaIlJPKZcmOoAEfmpSZp8Sn24CQkbHHtiR88gXHcfqh0Gifq0MYv9TIdsZjH3oj9PuK0usPYB78aEMxP41yyOJ4LOnDEcSZlq1zC0D7FfH3Eue_Xff2yi4I0u18BUWdQY-GcqowYP2O8Q-QausbN4Wm6DWgm7tjqZwB9Vf9gX5sObfyzXACrN44VfyAlPClbz2LlLlSpoipSGRk8GmmW2fpT9Wu324SYpaXmHB0enOlzTg_3l-YrBRx8=&c=6RrWNwOxdDhHrzeIc9j4b6G4YgfJIs0XqUWntQH1NbyAxZTDWr7clg==&ch=j-Wo4d7GeHzKp28oSKjpprcRzOwst2nzOCNqRtIhBf97WnzK452Sag==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
The 2015 Schedule will be
published soon.
More Information [http://www.firesprinkler.org/education-center/schools/]
Nov. 10 - 21, 2014
SOLD OUT!
2015 Dates Just Released!
January 19 - 30, 2015
March 16 - 27, 2015
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://www.firesprinkler.org/events/].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001vCupDQ0djHkUuwytLdrjaIlJPKZcmOoAEfmpSZp8Sn24CQkbHHtiR-HXsGLtOqDKiJh6sAQ_Ls_tKVZOZhRfNERNZWz4EHD5oQSxokGoQd5a0HGYKIGtqKd8BBQldIXSxrUYWdxIbM4-tXijtb414k4potsgwI0_vM5MsRlh2SOMwIIbmtEdcA==&c=6RrWNwOxdDhHrzeIc9j4b6G4YgfJIs0XqUWntQH1NbyAxZTDWr7clg==&ch=j-Wo4d7GeHzKp28oSKjpprcRzOwst2nzOCNqRtIhBf97WnzK452Sag==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org [http://www.firesprinkler.org]
Join AFSA [http://www.firesprinkler.org/membership/purchase-membership/]
National
[http://r20.rs6.net/tn.jsp?f=001vCupDQ0djHkUuwytLdrjaIlJPKZcmOoAEfmpSZp8Sn24CQkbHHtiRx5jnYgTIqWwyJzNe4u3yEgOnqV8tmiDUaBsFfgbOIsN8-ee77lgmsu9TGG-uKKSsJc3oD4LhRoIyJ7Sj8Be1fxwn6XxBLT57eX7J8_KGsMvF0c9be7wSmar90a_PsaJQQ==&c=6RrWNwOxdDhHrzeIc9j4b6G4YgfJIs0XqUWntQH1NbyAxZTDWr7clg==&ch=j-Wo4d7GeHzKp28oSKjpprcRzOwst2nzOCNqRtIhBf97WnzK452Sag==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001vCupDQ0djHkUuwytLdrjaIlJPKZcmOoAEfmpSZp8Sn24CQkbHHtiRx5jnYgTIqWwyJzNe4u3yEgOnqV8tmiDUaBsFfgbOIsN8-ee77lgmsu9TGG-uKKSsJc3oD4LhRoIyJ7Sj8Be1fxwn6XxBLT57eX7J8_KGsMvF0c9be7wSmar90a_PsaJQQ==&c=6RrWNwOxdDhHrzeIc9j4b6G4YgfJIs0XqUWntQH1NbyAxZTDWr7clg==&ch=j-Wo4d7GeHzKp28oSKjpprcRzOwst2nzOCNqRtIhBf97WnzK452Sag==]
Safety Training
[http://r20.rs6.net/tn.jsp?f=001vCupDQ0djHkUuwytLdrjaIlJPKZcmOoAEfmpSZp8Sn24CQkbHHtiR-K-bF4OgPsOZGhqGO7uRFtn9kzkVMI_wmP5o_cmCmTCn_PpKk5-jYbzvjzlqXNDfM9TedJYYCZgTNGmNzgimQNXGy89iafMLwu6Q0hKfh3lMWZ2wIo-FyjSiDxZHCB2aaMytegdY9nzC2SAUa-isjVo7rWQfNR223yOD2xuZtA9GOdpBqq4DhA=&c=6RrWNwOxdDhHrzeIc9j4b6G4YgfJIs0XqUWntQH1NbyAxZTDWr7clg==&ch=j-Wo4d7GeHzKp28oSKjpprcRzOwst2nzOCNqRtIhBf97WnzK452Sag==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001vCupDQ0djHkUuwytLdrjaIlJPKZcmOoAEfmpSZp8Sn24CQkbHHtiRxGYNdS1WUCfrq7AylUdw4erscEy64cSCBGzNSEeiRPJ-3OSYTFpWTsGGQwNdKR0BVxeJomLtLVizwwvh_BVywmQgM6N8TUmhdAtPcQM51em2EfTOsMTq11UxDwdm5sfbGHFg42vKp0rmAApyrALjFo6Cu4NI9BkHQ==&c=6RrWNwOxdDhHrzeIc9j4b6G4YgfJIs0XqUWntQH1NbyAxZTDWr7clg==&ch=j-Wo4d7GeHzKp28oSKjpprcRzOwst2nzOCNqRtIhBf97WnzK452Sag==]
Informal Interpretation Request Form
[http://r20.rs6.net/tn.jsp?f=001vCupDQ0djHkUuwytLdrjaIlJPKZcmOoAEfmpSZp8Sn24CQkbHHtiRxGYNdS1WUCfewB-ZgAjpBXMrl3vmr3fme29Ap1r5fDJ84wc6WpjK-8ap44zYGf-kNGxAw2ky1_BRrN2IuUFV0Tr9yCqTMXz3VUDbjU3PaciDoXWNHO9VE86zWVh5-YCc6nLZaKhzWoi9f6301t1xySeYS7htV6ubu7cxZxd5bRvE2iGHlZQPBQpE9k0RSE-Ag==&c=6RrWNwOxdDhHrzeIc9j4b6G4YgfJIs0XqUWntQH1NbyAxZTDWr7clg==&ch=j-Wo4d7GeHzKp28oSKjpprcRzOwst2nzOCNqRtIhBf97WnzK452Sag==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1118823970244
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=4d6c908f-a5cb-4bb1-b014-8155d5e3e226
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=4d6c908f-a5cb-4bb1-b014-8155d5e3e226
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org