Dry System Air Test for Modified Systems
"A tenant improvement in a retail suite consists of seven (7) added and
relocated
fire sprinkler heads. The rest of the suites in the building are occupied. The
building has a dry sprinkler system for the outside courtyard in the center of
the building. There are dry pendent heads installed in the outside courtyard
area
and in the suites (heated area) where the pendent heads are installed on return
bends. Since there are less than twenty heads, no hydrostatic test required,
just
test at system working pressure. Is there a 24 hour air test required?"
We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal
interpretation is that an air test applies when an existing dry pipe and double
interlock preaction system is modified.
There is no exception for air tests for existing dry pipe and double interlock
preaction
systems that have been modified. Section 25.2.1.6 for hydrostatic tests states,
"Modifications that cannot be isolated, such as relocated drops, shall not
require
testing in excess of system working pressure." Keep in mind that a hydrostatic
test is required but it is only at the system working pressure. There is no
equivalent
statement for the air test. As such, the requirement of the air test does apply
for the both new and modified systems. This difference makes sense because a
water
leak at working pressure can be detected immediately whereas a slow air leak
would
not be easily detected. Considering that dry pipe system requires an air
leakage
test every 3 years, ensuring a modified system starts off without leaks is
appropriate.
The NFPA 13 technical committee as yet to discuss whether a full 24-hour test
as
required by NFPA 13 is really warranted or if the shorter duration test by NFPA
25 is adequate.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001JyhLQZAs51FWhdOctV6xotpPnMpb-HS8dXAmltFvKWnVTWypZiSXG_VCgMijwjXYXFKvCKbY7w25V016_Eti6sGNqjs_N6uvVnMBQdKQIJ0C0EkOPZIBudObvYRPxRzXWXqKs9xhLzFzz41btsrrzKMjErqmA_DRf1qIw5T4kbnFvacu0xX4XQ==&c=C-QbWeKMnzPwdto7QRt8Got7XQxv-80W5lcSbdNIeaRHiaH630kX1w==&ch=9P3HMTWJXXBnxJ2OhvrR8xal_Q6XjIkQVjK-3jOsZpd9MdDkxhS0AA==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001JyhLQZAs51FWhdOctV6xotpPnMpb-HS8dXAmltFvKWnVTWypZiSXGyhRtI1nV0v4XiUvLhMINDz4xlHvVpgKe2DDWyyflHUo40XS45cZJadVarxkYtJDt7LB5CTUpRXTiONR3NLStnnTKw2ZDBt7cQBEFzvaJUY6EGwi05K01S00yQpHa1L-SSgNAT0-KsYmi7NA7ACkgo5pV8GaHFyeSZHgVRhLCcipszauxsIx0scgOkxvpzkuNVpM8NwQG8_X6DMCTqL4ajw=&c=C-QbWeKMnzPwdto7QRt8Got7XQxv-80W5lcSbdNIeaRHiaH630kX1w==&ch=9P3HMTWJXXBnxJ2OhvrR8xal_Q6XjIkQVjK-3jOsZpd9MdDkxhS0AA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information [http://www.firesprinkler.org/education-center/schools/]
January 19 - 30, 2015
March 16 - 27, 2015
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://www.firesprinkler.org/events/].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001JyhLQZAs51FWhdOctV6xotpPnMpb-HS8dXAmltFvKWnVTWypZiSXG8KFVhRzx6wWT-XCrVYsEX1bXujpYiDbY9303IWJF_dwab6fhoZ2-zXxQq3MGUnK5gVJ3hcAVMVlnDN3Rmo6DKvpTXoWru77KJcUdLpXrnuW9dpUyWKD-PbCNDJIxBIM4Q==&c=C-QbWeKMnzPwdto7QRt8Got7XQxv-80W5lcSbdNIeaRHiaH630kX1w==&ch=9P3HMTWJXXBnxJ2OhvrR8xal_Q6XjIkQVjK-3jOsZpd9MdDkxhS0AA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org [http://www.firesprinkler.org]
Join AFSA [http://www.firesprinkler.org/membership/purchase-membership/]
National
[http://r20.rs6.net/tn.jsp?f=001JyhLQZAs51FWhdOctV6xotpPnMpb-HS8dXAmltFvKWnVTWypZiSXGzf5CtacQsFATo1J9H2dfC56dHWwJM--ogbfMNYmHvY7Rr6FOoKrtmiZ_EF4XpBzgUA5l9RJH76ukI-UuwYXZAL1dFngyHmbcyJr4F3-cD_xGZaJXRbfZAdi3f520d75ug==&c=C-QbWeKMnzPwdto7QRt8Got7XQxv-80W5lcSbdNIeaRHiaH630kX1w==&ch=9P3HMTWJXXBnxJ2OhvrR8xal_Q6XjIkQVjK-3jOsZpd9MdDkxhS0AA==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001JyhLQZAs51FWhdOctV6xotpPnMpb-HS8dXAmltFvKWnVTWypZiSXGzf5CtacQsFATo1J9H2dfC56dHWwJM--ogbfMNYmHvY7Rr6FOoKrtmiZ_EF4XpBzgUA5l9RJH76ukI-UuwYXZAL1dFngyHmbcyJr4F3-cD_xGZaJXRbfZAdi3f520d75ug==&c=C-QbWeKMnzPwdto7QRt8Got7XQxv-80W5lcSbdNIeaRHiaH630kX1w==&ch=9P3HMTWJXXBnxJ2OhvrR8xal_Q6XjIkQVjK-3jOsZpd9MdDkxhS0AA==]
Safety Training
[http://r20.rs6.net/tn.jsp?f=001JyhLQZAs51FWhdOctV6xotpPnMpb-HS8dXAmltFvKWnVTWypZiSXG9961fSO5Hx90iKv6Yi_W8KhzDu1v8VGAyZs22q32Dyyh4YGtGHKPVZ_0tm_Xit7zNrkDC-dwphE51slcBWY0igrDYjmG-PGuxFVPW5667w8SDyyzEzOXEAwApaaLQoxsCPzbuX_c6Gl4R2hBPfiWWziFW4W-_SI8ReyilW90p0z70HHdvHVVrk=&c=C-QbWeKMnzPwdto7QRt8Got7XQxv-80W5lcSbdNIeaRHiaH630kX1w==&ch=9P3HMTWJXXBnxJ2OhvrR8xal_Q6XjIkQVjK-3jOsZpd9MdDkxhS0AA==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001JyhLQZAs51FWhdOctV6xotpPnMpb-HS8dXAmltFvKWnVTWypZiSXG1MQJaL439jKTwd3wbwJsoKl76-u2SD9ScBiqf7vUL0IhZOx6mK31sm1G5uJKWHBL9gtPl0ZU46y4P4H0YtQCmE-xXFW8P7EwLT4WZWsYHLF7yiMz_2QBNxOqLce1yOmkN2Twhzh_X1C1BisESTnubcnbfzfW6Nf1g==&c=C-QbWeKMnzPwdto7QRt8Got7XQxv-80W5lcSbdNIeaRHiaH630kX1w==&ch=9P3HMTWJXXBnxJ2OhvrR8xal_Q6XjIkQVjK-3jOsZpd9MdDkxhS0AA==]
Informal Interpretation Request Form
[http://r20.rs6.net/tn.jsp?f=001JyhLQZAs51FWhdOctV6xotpPnMpb-HS8dXAmltFvKWnVTWypZiSXG1MQJaL439jKE7_e8iAOBXIA2UWxJoV8-zI_2Bf56CUN90gggVsvjSisxCuh3DFuXSK7-LTdeWhn-MprH_gmJxdtLGXoMpi7MrbcpTrgyWhbss6Jn1YPJWQagAtGwGv8AuWP5O6cf51wCECKlPvh226M1zNDQghBeDfu7aAm0HCU1ZhQIQI27NhxCkL8TjxxMw==&c=C-QbWeKMnzPwdto7QRt8Got7XQxv-80W5lcSbdNIeaRHiaH630kX1w==&ch=9P3HMTWJXXBnxJ2OhvrR8xal_Q6XjIkQVjK-3jOsZpd9MdDkxhS0AA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1119180561769
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=d8567e87-a32f-465d-a7ee-eb7dba1bb7d9
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=d8567e87-a32f-465d-a7ee-eb7dba1bb7d9
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org