Assigned Area of Coverage

"We have an area that has a standard spray sprinkler spacing layout of 8 ft x 12
 ft.  The design density of this area is a 0.20 gpm/ sq. ft.  So, with an 8 ft x
 12 ft = 96 sq. ft. per sprinkler x 0.20 gpm/sq. ft. = 19.2 gpm per sprinkler, 
with
a K-factor of 5.6 we end up with a head pressure of 11.76 psi.  Our calculation 
is based on a minimum of 19.2 gpm/sprinkler at a minimum pressure of 11.76 psi. 
 The mechanical engineer disagrees and is telling us with a spacing of 8 ft x 12
 ft that we need to figure our minimum head pressure and flows as if the head 
spacing
is 12 ft x12 ft which results in a minimum flow of 28.8 gpm at a pressure of 
26.45
psi.  She believes that the coverage area defined by the S x L method is 
different
from the calculated area because the sprinkler can't discharge in an 8 ft x 12 
ft
rectangle.  It must be calculated as a 12 ft x 12 ft square.  Can you provide 
your
informal interpretation as to which way the design density should be 
calculated?"

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that the coverage area defined by Section 8.5.2 (the S x L 
method)
is used in the calculation for standard pendent/upright spray sprinklers.

I understand that there is concern that the sprinkler can't discharge in an 8 ft
 x 12 ft rectangle because it is true.  It is also true that it can't discharge 
in a 12 ft x 12 ft square.  In reality, the sprinkler discharge is a circle that
 is 21 ft to 24 ft in diameter (depending on pressure and ceiling height).  In 
truth,
reality has little to do with the hydraulic calculation method of NFPA 13.  Some
 of the more significant facts in fire dynamics and sprinkler operation compared
 to the design methodology are: the pattern of sprinkler activations would be a 
fluke if it were a rectangular shape as assigned by NFPA 13 for the remote area 
(1.2√A), the already mentioned discharge in a circle instead of a 
rectangle
or square, the density hitting the floor is not 0.2 gpm/sq. ft. in your design 
(considering
that the discharge is over a larger circle than the assigned box and even IF one
 accounted for that aspect, the density is not uniform throughout the circle of 
discharge), and the friction loss calculation is not academically pure.  The 
hydraulic
calculation method is nothing more than defined steps that allow different 
parties
to create a similar layout that are conservative (that is it exceeds the true 
minimum
demand necessary to control the fire as shown by over 100 years of experience). 
 As stated in Section 23.4.4.5.3 under the Calculation Procedures, the area of 
coverage
for each sprinkler used in the hydraulic calculations is the measured distance 
between
the sprinklers and the branch lines in accordance with Section 8.5.2 (the S x L 
method).  It goes without saying that extended coverage and residential 
sprinklers
do not apply Section 8.5.2 but are driven by their listing.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001O8c_gL_-R8vVhkL4e169EAAfxMEMPBkvRnGvp5PkKuMxFPjRY1eMbvX5gbhNKsqQFqFNkT9eHzKKxBmz_VF93f2lV_jcDK85ohkGxLvCtX0DN_oIdlwR373ESa-3nOv94rjgeqUsgM22GJHakyLjXicZ-tbYZfiCC85TJgjcEPAudwR1q-5q7Q==&c=XcBPO4pTcO4mOU7GB0Dneb7BqWv136KicB-kSXr_dr1EJ32wXTLB2A==&ch=h8f4tFe0Xwgt55TI_aED4qwnLWqfVe6IrDAiLHpXUDAQeaZtrLk_5Q==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001O8c_gL_-R8vVhkL4e169EAAfxMEMPBkvRnGvp5PkKuMxFPjRY1eMbinVTISULynxFjjU_PAHYkO1Ai-fOX3HIWwGfbDEz3SbghbnaSTMimcqPFx_kaeVtasBst2AgLtxoeBPOZZJOiRFsDErBcXEbo3SsGP84vi6EiMisWGFKZjFWQZ79SwuXOU2IkJuXvSBZUAjJ4iiEJa_mA2RywV98LPjbwuA7tYSyN_lDT4BjUL8vrsgSQluP6DT4CacPUCZYvsIQioPelk=&c=XcBPO4pTcO4mOU7GB0Dneb7BqWv136KicB-kSXr_dr1EJ32wXTLB2A==&ch=h8f4tFe0Xwgt55TI_aED4qwnLWqfVe6IrDAiLHpXUDAQeaZtrLk_5Q==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information [http://www.firesprinkler.org/education-center/schools/]
January 19 - 30, 2015
(Sold Out!)
March 16 - 27, 2015

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001O8c_gL_-R8vVhkL4e169EAAfxMEMPBkvRnGvp5PkKuMxFPjRY1eMbhRC665XERhahAf2g48RkVDBCb1GlXrsAHOgJ46-R8zZNnwseQA32_U9q1OtC9I3B4mSFmFs7bzmU25uhebuMYGYqK06kXofJIIVxaKpMBE3n0DOYRuwyoeOs9IBnOaTng==&c=XcBPO4pTcO4mOU7GB0Dneb7BqWv136KicB-kSXr_dr1EJ32wXTLB2A==&ch=h8f4tFe0Xwgt55TI_aED4qwnLWqfVe6IrDAiLHpXUDAQeaZtrLk_5Q==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Webinar
Sprinkler Pipe Corrosion: Mitigating It With a Nitrogen System

January 28

11:00a - 12:30p (CST)
This webinar offers 1.5 CPD and 0.15 CEU for a $15.00 fee.
AFSA MEMBER BENEFIT
This webinar is free to all AFSA member companies and their employees!

Register Button 
[http://r20.rs6.net/tn.jsp?f=001O8c_gL_-R8vVhkL4e169EAAfxMEMPBkvRnGvp5PkKuMxFPjRY1eMbsKAqOE0gPZ1iW_6xYkPuH1rUcMPB_8Ejh7TheWKHcSoMOKgKhaLdlGhnYjzMOvWVDkKwe_3N0OeLRvWADsonNaYRiQgO99OIht74pATcFS8cOxKeOhpt-4oCeYiaX9OISN-lbhkJENbmmxgeTCzPv3EcboShK4Xsg==&c=XcBPO4pTcO4mOU7GB0Dneb7BqWv136KicB-kSXr_dr1EJ32wXTLB2A==&ch=h8f4tFe0Xwgt55TI_aED4qwnLWqfVe6IrDAiLHpXUDAQeaZtrLk_5Q==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]
Join AFSA [http://www.firesprinkler.org/membership/purchase-membership/]
National  
[http://r20.rs6.net/tn.jsp?f=001O8c_gL_-R8vVhkL4e169EAAfxMEMPBkvRnGvp5PkKuMxFPjRY1eMbvzaPCZ60aQrzY3mw3sXP5h0R_Ta4RQrgeEJ2i6udS9mgZ6otMOhVjApaSNvVMMjGazmkGoc3TOEYdjGBfJ6_3T5u2b_2In4kyYmfSqPOUqhjFLWEdqKtCRUVz-EnuumAA==&c=XcBPO4pTcO4mOU7GB0Dneb7BqWv136KicB-kSXr_dr1EJ32wXTLB2A==&ch=h8f4tFe0Xwgt55TI_aED4qwnLWqfVe6IrDAiLHpXUDAQeaZtrLk_5Q==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001O8c_gL_-R8vVhkL4e169EAAfxMEMPBkvRnGvp5PkKuMxFPjRY1eMbvzaPCZ60aQrzY3mw3sXP5h0R_Ta4RQrgeEJ2i6udS9mgZ6otMOhVjApaSNvVMMjGazmkGoc3TOEYdjGBfJ6_3T5u2b_2In4kyYmfSqPOUqhjFLWEdqKtCRUVz-EnuumAA==&c=XcBPO4pTcO4mOU7GB0Dneb7BqWv136KicB-kSXr_dr1EJ32wXTLB2A==&ch=h8f4tFe0Xwgt55TI_aED4qwnLWqfVe6IrDAiLHpXUDAQeaZtrLk_5Q==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001O8c_gL_-R8vVhkL4e169EAAfxMEMPBkvRnGvp5PkKuMxFPjRY1eMbvQWhBDYcxTl9OCVCmKTj4obwInmJu3IU7Z76QXmeWA3LI3M1jxouBqjXDTT-DSS9B7CFYreJj4ZLknqGhIypLFSnAjBBqDU05FLL54PwIvcdhjvT4M65fMhI4RIjEPc0jFssNNWDu3wj9_kDIN8djAOWjzYZ3-IVhYeNEkdfaEwJ1z9NpqtiSM=&c=XcBPO4pTcO4mOU7GB0Dneb7BqWv136KicB-kSXr_dr1EJ32wXTLB2A==&ch=h8f4tFe0Xwgt55TI_aED4qwnLWqfVe6IrDAiLHpXUDAQeaZtrLk_5Q==]
Technical Services 
[http://r20.rs6.net/tn.jsp?f=001O8c_gL_-R8vVhkL4e169EAAfxMEMPBkvRnGvp5PkKuMxFPjRY1eMbhJVU06Lw_iQ_ygtbfqCDAwl0GK3vpqPMB-g-q_g4kPKyWiPdtAup0RBvNvikWPTcqJqYlaY07BFjKN08F9NTfdu9VTJHsGxOKml6epx2t5Me_ak6M3DOCDutgmtGaEByuog4541LM9ZWXxZldN7Kx0-RfLJ9re3Mw==&c=XcBPO4pTcO4mOU7GB0Dneb7BqWv136KicB-kSXr_dr1EJ32wXTLB2A==&ch=h8f4tFe0Xwgt55TI_aED4qwnLWqfVe6IrDAiLHpXUDAQeaZtrLk_5Q==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?f=001O8c_gL_-R8vVhkL4e169EAAfxMEMPBkvRnGvp5PkKuMxFPjRY1eMbhJVU06Lw_iQISPX6zuRmbEzABtjCJhZeS6NHrMjN93HU5uABuSs6_BL3w6PkvX1rct34hLWe8fmwb_wxVc_fHjlGJrrEFZ30gdo0znn47IsqUn4HYRnQLcvzw2je5q07VgDq1-i5NczOMWEHM4YqOy3wdBD85endw_bjEvE3Mcoom3jB8FsFus_2T-XH1Y79g==&c=XcBPO4pTcO4mOU7GB0Dneb7BqWv136KicB-kSXr_dr1EJ32wXTLB2A==&ch=h8f4tFe0Xwgt55TI_aED4qwnLWqfVe6IrDAiLHpXUDAQeaZtrLk_5Q==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1119568465214

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=92ad79b9-d35a-4fea-8dda-0850f499589b


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=92ad79b9-d35a-4fea-8dda-0850f499589b


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to