Roofs Over a Balcony - NFPA 13R

"We have a building with a flat roof which protrudes (typically no more than 2 
ft)
over just a small corner of the balcony.  Is protection required for the balcony
 per Section 6.6.5.1?"

We have reviewed the 2013 edition of NFPA 13R as the applicable standard.  Our 
informal
interpretation is that sprinkler protection is not required.

The requirement to protect balconies has been part of the International Building
 Code (IBC) for several cycles.  It was not until the 2013 edition that NFPA 13R
 incorporated this requirement (see section 6.6.5.1).  When it first appeared in
 the IBC, it simply said to protect exterior balconies and ground floor patios. 
 AFSA submitted a proposal in an effort to define whether the top floor balcony 
(or patios without a balcony above it) required protection.  The result was the 
added text: "Where a roof or deck is provided above....".  In other words, if 
the
area is not covered such that the heat will be captured, sprinklers are not 
required.
 The question occasionally comes up as to whether protection is required if any 
portion of the balcony is covered.  Answering that question starts with looking 
at the definition from the IBC for roof deck.  Section 202 states that its 
purpose
is for enclosing the story below.  It's obviously meant to predominately cover 
the
area but it also says "or sheltering an area" indicating the entire floor area 
may
not have to be covered.  A more definitive statement is in the NFPA Automatic 
Sprinkler
Systems for Residential Occupancies Handbook (on NFPA 13D & 13R). It states: 
"This
section also is explicit in that if there is not a roof or deck above the 
balcony
or porch, no protection is required; a balcony under an eave with a soffit or 
fascia
board would not be mandated to have sprinklers added."  This confirms that you 
need
a horizontal structure over the balcony that is large enough to collect the 
heat.
 A small protrusion from the side of the building like an eave does not present 
a large enough area to trigger protection.  Although the eave is part of the 
buildings
roof assembly, it is not considered a roof over the balcony.  When only a small 
portion or corner of the balcony is covered by such protrusions, it presents 
even
less of a risk.  Despite the fact that some of the heat from a fire directly 
against
the exterior wall would be captured by a narrow protrusion like an eave, it is 
not
the intent of NFPA 13R for that to trigger the requirement for sprinkler 
protection.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=0013dB7tQuVB2A_viL1NXfJnY7gv8arnVgtqMNf4DGdgv6FwzXvGYQMDHG-P9l6DJZx_LGh7Msbu4QjcBUiO7z8sYV_nG_X5UG61_iDCzldesbkwQywZ9oVrSnJoldUBVMplzWXkQcycnHAqmNW3f7sSXrmN_z3OnmqWmpNPdlEQAeyk_J5R_qfAw==&c=Za5MTZTtwE6MGZijrjUIn7Xtm-4v9ZrFaKClvsTn13GYpKlwyOUn4g==&ch=EfUAlUdRQY4WVN5FO1lN04fuzUXWvoEgg9-L5JNrzAamjiMi7y_VqA==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]    Join AFSA 
[http://www.firesprinkler.org/membership/purchase-membership/]
   National 
[http://r20.rs6.net/tn.jsp?f=0013dB7tQuVB2A_viL1NXfJnY7gv8arnVgtqMNf4DGdgv6FwzXvGYQMDLxlPr14e360L7fVyjY0Hm7tebkWdtzRxudVyGgfrpW-MV3dmd7apJd0Dp7E6Ksf9SJE5xZRv1J6cWc3nxmVls7OyAlM4dGEPDZG5x0eKY-2CHQxtGxe29TF4hMYkVpKtw==&c=Za5MTZTtwE6MGZijrjUIn7Xtm-4v9ZrFaKClvsTn13GYpKlwyOUn4g==&ch=EfUAlUdRQY4WVN5FO1lN04fuzUXWvoEgg9-L5JNrzAamjiMi7y_VqA==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=0013dB7tQuVB2A_viL1NXfJnY7gv8arnVgtqMNf4DGdgv6FwzXvGYQMDLxlPr14e360L7fVyjY0Hm7tebkWdtzRxudVyGgfrpW-MV3dmd7apJd0Dp7E6Ksf9SJE5xZRv1J6cWc3nxmVls7OyAlM4dGEPDZG5x0eKY-2CHQxtGxe29TF4hMYkVpKtw==&c=Za5MTZTtwE6MGZijrjUIn7Xtm-4v9ZrFaKClvsTn13GYpKlwyOUn4g==&ch=EfUAlUdRQY4WVN5FO1lN04fuzUXWvoEgg9-L5JNrzAamjiMi7y_VqA==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=0013dB7tQuVB2A_viL1NXfJnY7gv8arnVgtqMNf4DGdgv6FwzXvGYQMDEO03k99zY5p_ZStr20tEE42u_rNvhUQxpKIx3eC9zQ5VjftNzyJGaKX34FZKyU6AzBM8oGP880_b4Y2-3hVhMBwrn5lvKg5MvS9p5f6p8dOwIXFodD5yV9JdJ9VfNX7u093jF36EVO0fuvmkfxT0ia8Zlgx18xdFxvm_OqoHjljOEQkXprhMF4=&c=Za5MTZTtwE6MGZijrjUIn7Xtm-4v9ZrFaKClvsTn13GYpKlwyOUn4g==&ch=EfUAlUdRQY4WVN5FO1lN04fuzUXWvoEgg9-L5JNrzAamjiMi7y_VqA==]
    Technical Services 
[http://r20.rs6.net/tn.jsp?f=0013dB7tQuVB2A_viL1NXfJnY7gv8arnVgtqMNf4DGdgv6FwzXvGYQMDJSXJwoMg3cGfO0r84M9k88o5IAl8qPHTbbPt8yqTIaeTF_HK1jVJswU7pLnTKufskM52jvnx--dCWH27Dt4NyF_39A6lpuyiUNRUZebGKrNNIfH2UO8LxFyqq6rel-kf2WgDHyhLV6Z5Wckj1naYJLD96u-bMVOYQ==&c=Za5MTZTtwE6MGZijrjUIn7Xtm-4v9ZrFaKClvsTn13GYpKlwyOUn4g==&ch=EfUAlUdRQY4WVN5FO1lN04fuzUXWvoEgg9-L5JNrzAamjiMi7y_VqA==]
    Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=0013dB7tQuVB2A_viL1NXfJnY7gv8arnVgtqMNf4DGdgv6FwzXvGYQMDJSXJwoMg3cG0WzfbOjPDcg7S5nzGgtxGwPu45-O_pSZlvvW2FQvnreRzDN4qSYaE0oxuUpOx093k5XPBtk_5KmLhmtFNHW4VTtPoRM8fN3Bd-HyAGv-GnsOk2OHYMD467aEan7MFF1HkWQvyJnKTKtkaRGH_NcC59GfKdh0ZY2UpRFof5LqtlAzAyamEaKcVQ==&c=Za5MTZTtwE6MGZijrjUIn7Xtm-4v9ZrFaKClvsTn13GYpKlwyOUn4g==&ch=EfUAlUdRQY4WVN5FO1lN04fuzUXWvoEgg9-L5JNrzAamjiMi7y_VqA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=0013dB7tQuVB2A_viL1NXfJnY7gv8arnVgtqMNf4DGdgv6FwzXvGYQMDGrGu9eS8srMPERyVn54Ag3TkeSZJME0Luc7nllCYiaHgc39prm-I_zxMZXW0AwY_txNdvJt8AP4TxpfaTg5OOl41LT_ERgEnlpZB0wMEzChG4evzUmaJgeax5WzgCQhBr-YlrGYdm9bdWNEefOzwXJmqw9fr87WMZ29CHVMpnJK72uxS0qFz32fGYR2fJkVOA==&c=Za5MTZTtwE6MGZijrjUIn7Xtm-4v9ZrFaKClvsTn13GYpKlwyOUn4g==&ch=EfUAlUdRQY4WVN5FO1lN04fuzUXWvoEgg9-L5JNrzAamjiMi7y_VqA==]
Archives 
[http://r20.rs6.net/tn.jsp?f=0013dB7tQuVB2A_viL1NXfJnY7gv8arnVgtqMNf4DGdgv6FwzXvGYQMDNni86QXsLR-WH4X-PTgPJZCk_KF7TL1vRNl6hUtiW-thzACnEjMDfidhavav-RQaYNnGijBb5h5cIzR98EyGCs-JdjOPn9LeT4ngdk0UY4aD1FabnUV3t4jV8WsIUHMMOod-sMiVqxWA1ZKWvGKYpgKPoXrGn9zrYK1yvt-eMg-AG3YhnooGfFfCXlc1o-KMA==&c=Za5MTZTtwE6MGZijrjUIn7Xtm-4v9ZrFaKClvsTn13GYpKlwyOUn4g==&ch=EfUAlUdRQY4WVN5FO1lN04fuzUXWvoEgg9-L5JNrzAamjiMi7y_VqA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=0013dB7tQuVB2A_viL1NXfJnY7gv8arnVgtqMNf4DGdgv6FwzXvGYQMDNni86QXsLR-euvOxPRf_H9nFujwNYQisHCLMWVbSPs2rN0ghCs32IacDIzH-fmFVeocN4AJycggWPK-Jv-q90qRf-8BcmMeLXTSItCy38SWxtsh3GdhJvaZXC87OGUReYkaN0F8OtPH&c=Za5MTZTtwE6MGZijrjUIn7Xtm-4v9ZrFaKClvsTn13GYpKlwyOUn4g==&ch=EfUAlUdRQY4WVN5FO1lN04fuzUXWvoEgg9-L5JNrzAamjiMi7y_VqA==]
May 11 - 22, 2015
March 16 - 27, 2015
Sold Out!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=0013dB7tQuVB2A_viL1NXfJnY7gv8arnVgtqMNf4DGdgv6FwzXvGYQMDMNIOWCw8chH9bXDItlM1tL4sgsDt_ebcPRxzNQDGVqr1VNPKv0KxksDA2yDd1lWfMCv2pi1kLVNt7_CoTd_OZ0g6BJ3VlVtBPKp8e4vVWHhhnCqpmSHkxqECY7gIBb1wg==&c=Za5MTZTtwE6MGZijrjUIn7Xtm-4v9ZrFaKClvsTn13GYpKlwyOUn4g==&ch=EfUAlUdRQY4WVN5FO1lN04fuzUXWvoEgg9-L5JNrzAamjiMi7y_VqA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1119970384761

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=c35c5a78-086d-46d6-b7fa-5fb8bf148a9d


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=c35c5a78-086d-46d6-b7fa-5fb8bf148a9d


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to