Having trouble viewing this email
click here
http://campaign.r20.constantcontact.com/render?ca=ce9a9759-45f4-4a56-9482-6267a30d092e&c=9f129e90-caf6-11e3-83cb-d4ae5284205e&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A weekly newsletter dealing with codes and other technical issues

February 2, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Protection of Concealed Spaces with Access Hatches

"An apartment portion of this building is Type V-A construction.  The corridors 
have a metal-framed dropped ceiling that creates a noncombustible concealed 
space.
 The AHJ is fine with allowing no sprinkler protection in the space above the 
dropped
ceiling, acknowledging that NFPA 13 includes clarification that some minor 
amounts
of cabling and other combustibles is acceptable without sprinklers.  However, 
once
any access panel is installed in the dropped ceiling for access to standpipe 
isolation
valves or plumbing valves, the AHJ considers the space accessible for storage.  
These access panels are small and certainly do not create allowable storage in 
that
space.  The AHJ has required noncombustible partitions be added on both sides of
 the access panel in the dropped ceiling area and a single head added to cover 
that
space.  If the partitions were not added, they would require the entire corridor
 length to have coverage above the dropped ceiling area.  Are sprinklers 
required
for this particular situation?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that sprinklers would not be required in the concealed spaces
 when an access hatch is installed.

It was a common interpretation that if a space was accessible through a door, it
 could be used for storage and should be sprinklered.  This alleviated the 
concern
and worry about enforcing a "no storage" policy, restricting access, and how 
well
the enforcement would be carried out.  But, if a space was accessible only 
through
an access panel, making it difficult to use it for storage, then it was unlikely
 to be used for storage and could be left without sprinklers.  Sections 
8.15.1.2.1
and 8.15.1.2.2 allows noncombustible and limited combustible concealed spaces 
with
no combustible loading and limited or no access to be without sprinklers.  The 
problem
here is that "limited access" is not defined leaving the interpretation to the 
AHJ.
 A space having access through a door is commonly thought of as readily 
accessible,
while one that is accessible only through a panel is thought of as limited 
accessible.
 Access hatches are not usually used for storage since one would have to use a 
ladder
to gain access.  There is more of a potential for storage when access for 
concealed
spaces is provided with large panels that enter wall cavities from the floor.  
Even
that is not considered a likely occurrence.  The Sprinkler Systems Handbook does
 have some commentary regarding this issue under Section 8.15.1.3 where it can 
cause
some confusion.  It states, "The intention of 8.15.1.3 is not to require 
sprinklers
in a concealed noncombustible space that contains mechanical equipment made of 
noncombustible
materials.  Nor is the intent to require sprinklers simply because an access 
panel
is installed to gain entry to the equipment.  The existence of an access panel 
to
a concealed space could lead to the space being used for storage or other 
purposes.
 However, if the size or arrangement of the access is such that the space cannot
 or will not be utilized, and the combustibility is limited to combustible 
construction,
sprinklers can then be installed according to the requirements for light hazard 
occupancy."  For such an application as this, it would not normally require 
sprinklers
where there is limited access and not permitting occupancy or storage of 
combustibles.
 However, an access hatch incorporating a ladder such as those provided for 
attic
access commonly used in dwellings, such access would permit storage.  On the 
other
hand, the simple possibility that a person could put some combustible material 
in
a concealed space is not intended to trigger installing sprinklers in the 
concealed
space.  If the intended basis for when protection was required was that 
conservative,
the technical committee would require all concealed spaces with an access panel 
to be protected.  The situation that you describe not only has a very low 
probability
for such use but the amount of combustibles would be minimal thus posing little 
actual risk.  As such, it is not the intent of NFPA 13 to require protection 
within
the described concealed space.  One last comment is for you to review the 
building
code for any local written amendments regarding this issue.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001cW1XAJbAaEN7xP1eMIQ5hssEoUOu-4nHH4yrEApMCIUycmasY2CCnkS9r4hZNTh4ZMbytR6e3H2WRLmQFT8a-DnpkEeNNuZ09spy-JjNU-RExmWK_1LMUet3srwkhfh2Q6zZt8K_FYTj5UwSOyjsjg4pEvkIGHY1yzZnTsGmjShw-gu4a1U--A==&c=JbezytfLGGLxNMPTlcC7VfRFY7ilkSvB5BYT1axvZXPruFXqi-ozKw==&ch=7MTERAfwRC6jrgK_48xMsAegoEBystjzBMpSsT4G3vXFuO220MsXlw==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]    Join AFSA 
[http://www.firesprinkler.org/membership/purchase-membership/]
   National 
[http://r20.rs6.net/tn.jsp?f=001cW1XAJbAaEN7xP1eMIQ5hssEoUOu-4nHH4yrEApMCIUycmasY2CCnv4ltMKUSqghU4cD9rqKF-928SiJZxmgKiprNYFaVQJmHx-8-Rz7I-CMaANSEYIio_sBCQ8Vzt5hY9vYM2dQXVILa1DhTkwm_o_30A54sVoCI3RVmXeC3rRfrAHM-MNEhA==&c=JbezytfLGGLxNMPTlcC7VfRFY7ilkSvB5BYT1axvZXPruFXqi-ozKw==&ch=7MTERAfwRC6jrgK_48xMsAegoEBystjzBMpSsT4G3vXFuO220MsXlw==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001cW1XAJbAaEN7xP1eMIQ5hssEoUOu-4nHH4yrEApMCIUycmasY2CCnv4ltMKUSqghU4cD9rqKF-928SiJZxmgKiprNYFaVQJmHx-8-Rz7I-CMaANSEYIio_sBCQ8Vzt5hY9vYM2dQXVILa1DhTkwm_o_30A54sVoCI3RVmXeC3rRfrAHM-MNEhA==&c=JbezytfLGGLxNMPTlcC7VfRFY7ilkSvB5BYT1axvZXPruFXqi-ozKw==&ch=7MTERAfwRC6jrgK_48xMsAegoEBystjzBMpSsT4G3vXFuO220MsXlw==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001cW1XAJbAaEN7xP1eMIQ5hssEoUOu-4nHH4yrEApMCIUycmasY2CCnhCjAaFTAoMZ__IWWp0Flhqy_z0NwwjQehQQcVQSoRzG_UgNqSeLhYoqmwviXRFDXB_CDXgi_Tky_dooDZ0zigVEd-dHQ4u1f4j11qQzQ9TiWI2S0MYNsmVpBQto6ChIDH74jom77NDL0-5uZ6TxAqCTZqpb1gVJDQw5QPMNNYrbJTbh5-bkBp8=&c=JbezytfLGGLxNMPTlcC7VfRFY7ilkSvB5BYT1axvZXPruFXqi-ozKw==&ch=7MTERAfwRC6jrgK_48xMsAegoEBystjzBMpSsT4G3vXFuO220MsXlw==]
    Technical Services 
[http://r20.rs6.net/tn.jsp?f=001cW1XAJbAaEN7xP1eMIQ5hssEoUOu-4nHH4yrEApMCIUycmasY2CCnploFxZKt1nNLTn7tDo-zT6GpRfb-HkWRNZVnf9raW3PtamI173TX_4GBwk1dEoX7CnhmA8QWdBUFFEocXmxV8bmhccArpXCffIJ0mt7VlmWjbAeXVs3omYDY5-Q9bO0KKwzkyEwPbN5uPN3JTQeVqruRGTrzS1iEg==&c=JbezytfLGGLxNMPTlcC7VfRFY7ilkSvB5BYT1axvZXPruFXqi-ozKw==&ch=7MTERAfwRC6jrgK_48xMsAegoEBystjzBMpSsT4G3vXFuO220MsXlw==]
    Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001cW1XAJbAaEN7xP1eMIQ5hssEoUOu-4nHH4yrEApMCIUycmasY2CCnploFxZKt1nNQL0X7i-of2-N6PY8RVzQlrm_8IsT9B4cyOtIoXMAr0w7-GzAg4sTA6BcWUpllcsa78t6Dk-2BGLTwh5-LmWnbjS7l060z-r5--gjz_PXxExz53JmbEU2w91b6ruxy-gTXRpcZWRlywMHB-JglQ4vacruXKukxgmHX8hfvc8GtudQ0noq4-oN9A==&c=JbezytfLGGLxNMPTlcC7VfRFY7ilkSvB5BYT1axvZXPruFXqi-ozKw==&ch=7MTERAfwRC6jrgK_48xMsAegoEBystjzBMpSsT4G3vXFuO220MsXlw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001cW1XAJbAaEN7xP1eMIQ5hssEoUOu-4nHH4yrEApMCIUycmasY2CCnlIsOsHqpdyIjLBriVCxLfL8ND_c8Pbzc4KLh0aFZ2yG9WqjcCJhAOAHzjnfod5p_CHC35zK14Aa5QSJhfE2L1lvGtW5nGcZhetSajbGzwNQWlmpu-7fGcMoEAbQE2wsJmUf2MsX7VCiUszqMvQwkMdHMtNMO2LZDEQb41QcfzUrTmH5gCX__s6PyppOCInReA==&c=JbezytfLGGLxNMPTlcC7VfRFY7ilkSvB5BYT1axvZXPruFXqi-ozKw==&ch=7MTERAfwRC6jrgK_48xMsAegoEBystjzBMpSsT4G3vXFuO220MsXlw==]
Archives 
[http://r20.rs6.net/tn.jsp?f=001cW1XAJbAaEN7xP1eMIQ5hssEoUOu-4nHH4yrEApMCIUycmasY2CCnh-9a6puda_N5bAly5qX1pm6NPGxNnYjgAFnvExTfPWjqZsCMIXL3PxaYaZLZJ6uqi1HsUJROmhlq3GhgyOCpHi947sHWNBvQUCNBf2NtbS2psiqkRoBy0c6wdteItM8HjkB8SxV74xk6DJM4ey8ePngnXGiHgDSMYDPuSsOB3n0tMOOUEuAyJNrZ8ggjls6ng==&c=JbezytfLGGLxNMPTlcC7VfRFY7ilkSvB5BYT1axvZXPruFXqi-ozKw==&ch=7MTERAfwRC6jrgK_48xMsAegoEBystjzBMpSsT4G3vXFuO220MsXlw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001cW1XAJbAaEN7xP1eMIQ5hssEoUOu-4nHH4yrEApMCIUycmasY2CCnh-9a6puda_NjZctvRH58erpxUQL0bs2eqS5cPmkS7r-oJnhEM5BTZ3OA9Of7LK1k7aW1KJZeMnciD2ejMKE8P6hoVDeAVwad9-TbR1ZCPwqf0cGifxKvVHlZG8mCJPAwpdrfj5qBTp1&c=JbezytfLGGLxNMPTlcC7VfRFY7ilkSvB5BYT1axvZXPruFXqi-ozKw==&ch=7MTERAfwRC6jrgK_48xMsAegoEBystjzBMpSsT4G3vXFuO220MsXlw==]
March 16 - 27, 2015
May 11 - 22, 2015

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001cW1XAJbAaEN7xP1eMIQ5hssEoUOu-4nHH4yrEApMCIUycmasY2CCngVpkbGjdOEj-usrWZcjlUCOd2_Sbs9ad0975skz0QqTHeO7i-Tx-Hq1GMLB35QZ3YvJf9kq_ORFWJAd7dlG5e_jEhM0wgc4kvm0c96ejMOWVKkEspuIaaLVyYs0PyeTFQ==&c=JbezytfLGGLxNMPTlcC7VfRFY7ilkSvB5BYT1axvZXPruFXqi-ozKw==&ch=7MTERAfwRC6jrgK_48xMsAegoEBystjzBMpSsT4G3vXFuO220MsXlw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1119916293061

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=ce9a9759-45f4-4a56-9482-6267a30d092e


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=ce9a9759-45f4-4a56-9482-6267a30d092e


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to