May 11, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Offset in a Supported Armover

"I have a two foot armover to an elbow.  Off the elbow I have a one-foot armover
 with a drop to a head.  The hanger is on the one-foot armover to the head and 
the
inspector wants a hanger on the two foot arm over also.  Is this correct?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that an additional hanger is not required.

This is addressed as new text in the standard as Section 9.2.3.2.5.  This 
indicates
a single section of pipe shall not require a hanger when the cumulative distance
 between hangers on the branch line does not exceed the spacing required by 
Table
9.2.2.1(a).  The annex provides additional clarification that when a branch line
 contains offsets, sections of pipe are considered adequately supported by the 
hangers
on the adjacent pipe sections when the overall distance between hangers does not
 exceed the requirements in Table 9.2.2.1(a).  The cumulative distance includes 
changes in horizontal direction.  Multiple consecutive sections of pipe should 
be
permitted to omit hangers.  Although this is an armover, the same concept 
applies
as that for a branch line.  Similar wording is provided for mains in Section 
9.2.4.7
along with annex material.  These short lengths of pipe or offsets joined 
together
do not require a hanger on each section of pipe, provided the spacing does not 
exceed
the distances in Table 9.2.2.1(a). As such, each hanger will not have to support
 much more than the weight of a continuous section of pipe.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 25 Open for Public Comments
The first draft report for the next edition of NFPA 25, Standard for the 
Inspection,
Testing, and Maintenance of Water-Based Fire Protection Systems, is open for 
public
comments.

Last Chance!

Public Comment Closing Date for Online Submission: 5/15/2015

Submitting comments via paper submittal has passed.

See nfpa.org/25 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om28wGqCpqH9Qeog_gG0_wWCpNmuhRRYCf0XhmqVFVtrujN_GczwZAAeBZHHOuTWxQe51BkU7ui_emSPgg5dVb0S1asp5hBdyA-HTfjyel7kjEtOtgVXGq9bn8=&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
under the "Next Edition" tab.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Call for Trainers

AFSA continues to grow and evolve in response to the needs of our members. As 
training
development continues, we call out to those in our membership 'family' 
(contractors,
manufacturers, designers, etc.) who can serve as trainers: either as instructors
 or as content developers.

If you, or someone you know, are well versed in any (or all) of the following 
areas:
installation, layout, or inspection/testing/maintenance of fire sprinkler 
systems,
and want to teach or develop courses, let us hear from you!

Please visit firesprinkler.org/trainers 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om28wnCzJsWjHo0xvveBlbkLKsGTAYsVfmCpbWzL1dvMTIeO76_FbEHKp_a2GIVPHyqVzV07nh0KekVnYRs8RgpGF4USVGuXYbAbImrehgWWtT1VZ924DzX9dldo2pcBBWOPW3x_P8ci534&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
for more details.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om28zPvadEZEN9ZCRJl-_8rVGXzH3-Hjttc4PGgiwu1V5DqYtvegAubSc-DO3w8rfOn998C8D1tiOJejXs6Ja0oQjENumViT6oJ4eJ4wOtDiyi0lQfk_mz2V2RLmkknwdBc6w==&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om282y1ZUBDQDvO_osGjJqtS16pauUBkOOZvXOWo8ufvynZvLYAWWGnyuV_UlK0XnewQLBBq25hBSbHBy6IJfBr5oxKTWMH2g2bhd0Cwo9uvexGQIurKkYpMC4Qwgt2MfvYbHd26ezFCAKRko6v3oXcCJ2mcEW3Jh1gcpyQhIQAKcdG&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om289rYbe9SUYJvkCJpoehiA4iojHx9dvv3y-RxIa0ndgAO0hkZ_F8mMM-LWK7hbLIymUzwMfRUmnAOfpuKNgrk9Z1G7f8ZaXLSlPLA6RCOJb43LimRmlItDoa1b2M5H4ZvZQ==&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om285sLQR1_wKIKJ6PjEACWUPQP9HGVb0YGk4RRYOTVi9WQojX8RrmV0n9r3_lr_qLwUDu_-XxgMjp7mjGQwcZaR0th-Kua7G6vTxKSKVrWZS19DS8RPgLJ9HSXm-p2zEyqnWYkqZOU-SzffaZpXrc9GJULaEBO7rf4iCHmBPYxETQPbe_S-z1l_5A=&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om28xgdWLw24aFj4PhRHrxEZJef4cxxcggVbZnlP1BqRo_VmuO7izyUG4eilfUb8pnOi32qa8eGCPCIZCiBQ0Lzbll7RlDdH3rngww6euTDN6KjarssfUlH8vG93CHWYXSCLet6m_yakkUFGXdvl6ShutsI6gcFXVKrIA==&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om28wGqCpqH9QeoELGEueBhLpbP9v4mBJc3KGRNgdIvawMKJ7ORKivHIP_Dizh7dvuvmkGvozzKgjt-B_nlom8wVQtD2SksWFAJbRsVNYe4aA1LwLung-ysrt3e0KqpwR4rCDwgJgkvCbNVYHrjC6x5GtMW8-dBf1dDHYWkXCwKMdbriB22qGgVOmpSdYvG0H5zBbnIYI_rHATJPLGftzZVDEIqm8sXeZwsUIodsM7eHM9g&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om28wGqCpqH9QeoTegrNhLN2JPmok87TPgWrTWs9Ex35_TOiV-wm30_1uGrudAcMJnZPUk2pFQRHmpg8KyUq4zPLSQQTSPB0vHi6ifFsPye6Omb2SOUVEvj4H4_3bzAXGmfhBLv5XjvN5G0WN-Gsh1KHgKqymM2EfjBJsNJXqOo9gSlYi1mvX_DCB5PGhmjt4zyiA==&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
Archives 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om28-hugskbA6KnRAd1SGBZOV-CefjaF2Xge3QUZnvsaE5hKx-97m06s3jkUwCikhhTSIYNFH3npe6cgbyP0kuPTCyqlhmjBJuTOV2kB6AlHxWrMMHASDSkgVxe-NmN4lex58mKb7xIZu3R8vpaPvQISqWx-Jcc_8CX7N9_FOI7GiS5jDNJTlnbHbmedOyaqI0kmw==&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om28-hugskbA6KnryfG-kpQEwXXSPAAI1VIMAx4m3OvXVXCQgkNo5TkN_t2wNJ1NalkhKmtLep8jXN11H48ilMb_9IrOo_7zLz8dFhUzcBrV1-BNKuwvrKoHLpm5nNHKa4vTuaXMOXaHGu9&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
July 20-31, 2015
Sold Out!
September 14-25, 2015
November 2-13, 2015

For additional details, register, or view upcoming training, visit the
AFSA Calendar [http://www.firesprinkler.org/events/].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

SA Cover for TU 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om285sLQR1_wKIK66isv-dvOekRDuZgJFHgs9QJdvzZbQbo35z-wXlPQz9EDMsyJzD4a-1EJYhPwovvKvy3FPjEM3XpFasQrd7iHKh3ZwEjtnxJEPcnjKOhBk57LfsGqA6alnEeeeRdhQhcuK6kdR0XavgwjUkcQxGPTg==&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
Free Subscription
to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om28zbooTWClaFzC1R6kuFDXe892egU1dTj9aMjGX2ne6Fcznnb-VpXU6TGmVUJGY8SYHSZ8hp2kj002NE5d5x6gszSvyUJzsE1yLi7lcrwpy2KLlJ2QRMyRAp5OXBTuxMh8oSm7U3yHDHxeA-f2pfnhpshIXzuA5h4ew==&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

May 18 - 25
Shop the AFSA Spring Sale and SAVE 40% on any AFSA developed courses.
afsa.redvector.com 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om2833BnT26yRrClU0t57YlJ8IwZXIarJYdu0bYG-uHopexk9xff01tMocBF73KsKM0oN3bq_fTMEfXzTG6c3OyO6gp2Z-Qi5_NmRl9fuE_46EPmLSwN5PnTrI=&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001WHyJlXGFq9RWALlynykFpyuN6Q0RSQlK69J0x2gtviyq8Oja1Om282FFuHFbNxgsClVkQI6DsMRl8hNgoJlqU9oV3TIb3eaFkMllPpp97YvS8jD5sX5INVx--wV8pNqbA0MoMUNEdYKJcSWCGg0nEsAIkM166oSDEd2QxQ7Lg5hqq_zlLDd22hBLNflsDNmjBc89X6edPzh6iHIigK_w33b8_z1kgnZ5b47YO9xmNGpw86PAi92y_81hWO-2Qcg7&c=Qh5SXZ2zkV-kAkYbGUUCmM4o8HvYBNrdoCCgfNi3EuJIux33wbVbKQ==&ch=6x75b8Sxqxy2Qv1mTM5-gbE7qSo85CJcRqMBJ_ZEefpNERmX2C9G3A==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1120984453493

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=99b1a425-f02b-440c-a05c-0aac3dc1a18d


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=99b1a425-f02b-440c-a05c-0aac3dc1a18d


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to