May 18, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Area of Coverage in Electrical Rooms

A maintenance office has electrical panels that take up half of the room and 
there
are two sprinkler heads on other half of room but not on the half that has the 
panels.
 Is this room missing coverage or is it done correctly because of the electrical
 panels?"

We have reviewed NFPA 13, 2013 edition as the applicable standard and NFPA 70, 
2011
edition as the applicable code.  Our informal interpretation is that the proper 
spacing of sprinklers is required.

The requirement is that if the piping is located above the dedicated space 
greater
than 6 ft above the equipment, provisions must be made to protect the equipment 
from condensation, leaks, or breaks.  Article 110.26(E)(1)(a) defines the 
dedicated
electrical space as being the space equal to the width and depth of the 
equipment
and extending from the floor to a height of 6 ft above the equipment or to the 
structural
ceiling whichever is lower.  It further stipulates that no piping, ducts, leak 
protection
apparatus, or other equipment foreign to the electrical installation can be 
located
in this zone.  For instance, electrical conduit serving another piece of 
electrical
equipment in the room is not permitted to pass through the dedicated space of 
the
electrical equipment in question.  Then (b) says the area above the dedicated 
space
required by 110.26(E)(1)(a) shall be permitted to contain foreign systems, 
provided
protection is installed to avoid damage to the electrical equipment from 
condensation,
leaks, or breaks in such foreign systems.  Thus sprinkler piping, while not 
permitted
in the dedicated space, are permitted above it as long as protection is 
installed
to avoid damage to the electrical equipment from condensation, leaks, or breaks.
  Subsection (c) clarifies that sprinkler protection is allowed to be provided 
for
the dedicated space, but the piping must comply with this section, which is 
essentially
(a) and (b).  At first glance this appears to say that sprinkler system piping 
is
permitted to run through the dedicated electrical space above the equipment.  
However,
closer examination of the wording reveals otherwise.  It says that "protection" 
is permitted for the dedicated space, not "piping".  So, the sprinkler and 
piping
may be located such that the sprinkler will provide protection (spray water 
into)
for the dedicated electrical space, but neither the piping nor the sprinkler may
 be located in the dedicated space.  They must either be located laterally out 
to
the side or above the dedicated space.  Again, if the piping is located above 
the
dedicated space, provisions must be made to protect the equipment from 
condensation,
leaks, or breaks.  If there is room for sprinkler placement per NFPA 70, 
sprinklers
should be located per Section 8.6.2.2 for maximum protection area of coverage 
and
Section 8.6.3 for sprinkler spacing.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Call for Trainers

AFSA continues to grow and evolve in response to the needs of our members. As 
training
development continues, we call out to those in our membership 'family' 
(contractors,
manufacturers, designers, etc.) who can serve as trainers: either as instructors
 or as content developers.

If you, or someone you know, are well versed in any (or all) of the following 
areas:
installation, layout, or inspection/testing/maintenance of fire sprinkler 
systems,
and want to teach or develop courses, let us hear from you!

Please visit firesprinkler.org/trainers 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H1J31GZkU8D19wwvNOe3rAxad1Plv9sQr6v7QdKKqDvDtN-VjS_4TBhui6jTel9SlMGpDzZ9zZ41VeFyXDukrqriz4Wndwenca44g3gt7lKHDLbJ4RbOgFp4HVbIUVwoa3QrhaHPHy5E&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
for more details.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H8Jh3JcLPCRy1L1_LthIBKkYnsxoXMwr2sr-FI0FfbBu9-evVuxEQvTpjKpYsHR__3R0RYKcr5QzjB-HzUXw0lGQpkgftxYU2ANz5dO3B9j-k1k9EsyEsK189T3ebJwfjA==&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94HzIfXYhbMZRk1qC3LELBefNvG_mEZNEkunlK7t9nYw8kRMB8rCLsDOFNDVReFXW8FifD7NxqxUf2EvBjo6IXRyWHg4VxqSsJ7gxtAjWaDQdJNtihIvIjhFYyjDIreOa_gJWBFbKdcZlb5iak4rAD5kovRysPl-TNpd_xZqNhrYJV&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H1T8ncbE-oXKTg0efZw9woNcq-n98yHMLBlAme-hwB-TVxudjgBudQLXgu9Zy38TJGLMJNHVTnPjdWD824y2OTJNLAByFXuUTUcCGYfayrzTqItqthd6AV5TBWQKN2TmXg==&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H5lXu8e-AuhnLYjxoUrvLWqWzo_d2Cu1c4uuHCR6PjjRd9hs-EkCiT9eL_p3MdV54f7e_VeDaBDjoMcEgnYd-oAE4RFVUi6wqcNv7KSLbsnIGPQucYmB1zsgB-sk8VgkmPOo_JWzZSRyzdd3hq3d74XMJ1wjSw8-y7y3BOZEGN3iTgEWf7fUo4Y=&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94Hzju2zDjU6__WfIjwGd8xDg0xltOugWDgxVDvundu4M-iQ0PDEmh1RrpSI4N7a428iYR941_NvOEhIKk44jzCRHNzHHpbTt75_DbGaQQIbaMqEq0LnRDh1XmlRghv0bhbJKUMYaVXeNI-Jv4njBa0HjDwAo8O2fLkw==&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H0tjQCPKaMHHny4saWP1MVI-Nt1GMnbpjiwOzevFRSfR_KJSEZHEGqIcUm1LYkS_8RGA2QKhNQj27aNd5cJfmdxR7kEwf8NB_HJm36ZNBY-uGWCUc3xtQ6IAIpkjYBYhZ8fptA74wEGx3D-hHpRGo5pS1SxXu6cBIxfu28qpD2KdKK936GQuNPbDgWjLJAvxXUF69CT_kmv3lGc0H_qg5hREjMMn3tI0A2bSV_sN-uW-&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H2sp4S-x9rLSBwqRAzV0hRxxOEUqj2WE6jRHHjtjptAVYXifnCuUw9qGqdlQuv0dbUPUzkP-oNUBBmHR_1PwDjPILtCJ65a1FQhl8qqYDdS8GzdkNI4YLEMq8zHK0W5yBtNYFoH-3NG5Vo7OLPPgweFeMs2HVtSL-eePTr-L2GMD3Ha2DJXxm03ZJYN7YIDtBg==&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
Archives 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H0ttMArjHVpP5Koi3jysQyZIPheNUMjNgSr6NN0e6sRJ1W7zxas8qqRNLfYSkpmOO4SeQywbZgftx_mloiXDGyDH178SVBoEgq3Shs2xxKwH3gKNXFvEcHP3REGGBOZZB-du8rGO23GN3JaaH_aO5Z00UPO3sWRu2b-oDICeJ2jg-1yqRbsCyNwYZlDLLPp8Ng==&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H0ttMArjHVpPKHnDBDe1bvNLI5S1LifPf0FOYNKNXbqj4GzqQ4h2dACy2Rfmtwrohmmeo20chzldpmRpHMg8Y8QZaHJWPyFWpbecsXIiYc1X6-pPEsXeRJyR45j9nisxZ-qVIi3YdIWJ&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
July 20-31, 2015
Sold Out!
September 14-25, 2015
November 2-13, 2015

For additional details, register, or view upcoming training, visit the
AFSA Calendar [http://www.firesprinkler.org/events/].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

SA Cover for TU 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H5lXu8e-Auhn8UXq-evIl8UUGiJDy7iYHef-YmNRT3G1Chlgf9Yb648Urw4_Bx4kSaHjx12li1WsNTcb_emtg7FLpdGAFb2KHI-bpzmc39EEdNMLjjIIbl3uFNL9cDu8gJ5kwJ6VaazVsSuAzhUXOCrm2dfhEkuR4w==&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
Free Subscription
to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H7PlBnoAMNEaUAHIb-YOgcXWZiTCpPNSuf1eUGV0LpX0UqPsmzWTO89dngXh8SdPiH6101zUQS5n1vMT9nz2fd2Qv7ogYlDMFNHEesORiT20aktTP2X8JaTeWdr187TXZx4wp6OFvwV1gZsoUGv3mKmN4IRI8Mb7VA==&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

May 18 - 25
Shop the AFSA Spring Sale and SAVE 40% on any AFSA developed courses.
afsa.redvector.com 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94Hy1kMo08WJRWDk5KhCwK75EJ885VFGex3WtKm2Nj0OUmZpt2sEODhEw2-qJMhCt4art3ulMN69tFMQSPpRy_y9_J5cVt5GrGNTCtP8_KAxndm_bQyh7EGgo=&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001ENHR_297kOjZd7jnrjLAUrZTlU-Lia-8WI9TGCwvdV0NgRX_jY94H7CGcYnC5rNtEbJw6H3YwvFYFofz_HByb-qZVSLAusGvjNnqoww2nfqEcEtjekTKVSXZu2t8euteZmXrnbaW3oBaPcS33Xw3wDTZq9XYYh17BbinXeQdm332XdZGPJIANtXBBXvzmGcS3z41q_N-RbZstJmsZGwKZKFZaQj-f99MfbBe9bGs9HJeSIYlJBOoBsoj2tTa4kZv&c=3TCwZ4liS0MpLP1DVOgV378ad3iCr3Mro4P9skhDkD_Yq30LLLldgw==&ch=3HVJ6Qkadf-xFAkf2ZH68cxCMpEo46UPeiFettXaHhwm5Z7e6OXHyA==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1121041467282

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=86fb0228-6e17-42a5-9152-aa3aecf58351


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=86fb0228-6e17-42a5-9152-aa3aecf58351


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to