Having trouble viewing this email
click here
http://campaign.r20.constantcontact.com/render?ca=09bc853d-97c2-417b-b76a-bd8b388a34fd&c=9f129e90-caf6-11e3-83cb-d4ae5284205e&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
June 22, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Dry Pipe Remote Area Minimum Size
"I have a overhang at a dealership that I need to hydraulically calculate a dry
system. The remote area has two rows of sprinklers fed by a single row of
sprinklers.
Can the room design method be used for this application (like a corridor)?"
We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal
interpretation is that the room design method cannot be used for the canopy.
Section 11.2.3.3.3 says that in order to utilize the room design method, all
rooms
shall be enclosed with walls having a fire-resistance rating equal to the water
supply duration indicated in Table 11.2.3.1.2. This application is outside and
not enclosed by rated walls so it is not applicable. A single line of
sprinklers
feeds two branch lines containing four sprinklers each. The remote area
includes
these eight sprinklers along with sprinklers on the single line. It is not
feasible
to calculate a 1,000 sq. ft. of single line of sprinklers to attain the minimum
remote area of 1,950 sq. ft. A single line is a special design area and
shouldn't
be mixed together with a density/area approach. The sprinklers on the single
line
have already been addressed by another remote area. Thus, calculate the eight
sprinklers
in remote area and apply Sections 23.4.4.1.1.4 and 23.4.4.1.1.5. Section
23.4.4.1.1.4
indicates that where the available floor area for a specific area/density design
criteria, including any extension of the area as required by 11.1.2 and Section
12.3, is less than the required minimum design area, the design area shall be
permitted
to only include those sprinklers within the available design area. Thus, you
calculate
the eight sprinklers that you have available. Next is Section 23.4.4.1.1.5 that
indicates where the total design discharge from these operating sprinklers is
less
than the minimum required discharge determined by multiplying the required
design
density times the required minimum design area, an additional flow shall be
added
at the point of connection of the branch line to the cross main furthest from
the
source to increase the overall demand, not including hose stream allowance, to
the
minimum required discharge as determined above. Annex material in
A.23.4.4.1.1.4
provides an outline for the five-step procedure for the calculations. This was
an attempt to provide an overage of water delivery or adequate water supply to
account
for an extension of fire from the smaller design area into an adjacent area.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Call for Trainers
AFSA continues to grow and evolve in response to the needs of our members. As
training
development continues, we call out to those in our membership 'family'
(contractors,
manufacturers, designers, etc.) who can serve as trainers: either as instructors
or as content developers.
If you, or someone you know, are well versed in any (or all) of the following
areas:
installation, layout, or inspection/testing/maintenance of fire sprinkler
systems,
and want to teach or develop courses, let us hear from you!
Please visit firesprinkler.org/trainers
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N17udMgBI6BnB1-1HaHvDeqWi2nP8eeqksvwQv5mYZuml3PquGOPxPbraPtkhCDOrsCbiFAkkKddYYrRG_mATvp_uB9kNXAjT5Z467GMpseNot1ROl5iOopJVE1hSYQSa2YEkY4F1RTF&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
for more details.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N-KuTikKFwO6S4-VcLnoXdRvAVXbtGn8Cwi0rA2U8GMsjyB9TRrMRf9DVQrEjS_ZEA1-UkR7FPU933R0pN-tr7_V-xHCVZX1p8P7aMw-aLtPuALsN1lDIbgqMs-PgSIEFQ==&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
Join AFSA
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N1nlYYL_9ilF5LGeFmGgYEY-DDNntG2Dq024tWwwEt5NDtpVO3uQ-f9FQNEcmdZBFT61BSgK-zkprIhYxMImLV1Y6wEeK94yUekiIHH8i_0zzWM_OMZS_kKMewQBc0dfEExt4Q--KwcxvwqqosZsbdznD3rFLgvfqWMn-Um0px8P&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
Scholarships
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N4jK0Xi_rrmdSauQDV33nERwAcQwAvl0jLcN1BZcaLaC97yyX9n7uHbEVeIMunoj3mPz5fWGR2XzwNLvPOSdnfFdiHCGNOmqMZ7j3nd_y7KxgvnsqcmPSdtGlB3vmebXjw==&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
Safety Training
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N-ieM_yFHmoYhNyO-1BQacxFC9v0A41J4JnBqEreCDaZ4svJEsYJEYGHqvoETlqC8pTj4Azqn42vRUyqHQFuOYKccKwtMbiFhX6_baMJWnzgzeeoE-SRpMqJick-XN7oTkZlpvhErcSzgDANU1a8fO_uCR8bgFLclVY1toIJ4msZ3RnDT4GI1Jg=&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N79nHFYFGVv-7hf8DYYqn7ywfwf9jGWVOaimAxWvFwn8xXW3oVqB7Wcc6crcDKhCRzRUktTJUNTU2ioy0Mp5XOjLBkud2sBFdTEmppnjdV9lZBQMtuav4Z0cPNoCVJARJTt-EC0GdYgJlvMdKFaOIQ2ot0a5PATcxA==&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
Informal Interpretation Request
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2Nzc-CBcN3XwwZK2QagQ-sQk-3VXI9ESXDh240dJJPwmNQAzQYKdvmGrY96ZbuV9ppe-Pk6BWuMGS4KG4O80P3B7Reb0IaW3OAPszX3CLaPExXspai7e3vUykjNtqSvBRBtrEuazW70EcRA9e6K12NXSiyQgOxqb5QKHkQNIfwp0tkN-wnTV8hSiQF4fo5oquMxJWRNDRnDq_WlXuMPn0Gy79rA8Q1rdkfUFds3rr9FKV&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2NzzXveQkjSCxVyhZxh8DT9bfOtj6a_YQWLd_7Eymgdq2H1bum-ciHcRo7Ml1N-wkVnS9o5FcITXg_2Plfe1Cd-uTTPJmkU5-zsAyKUduJvgrMZP4Nz1UpvnoIxGs0M8Aztg8IKgAd1ufVqJ7Dkh1xaD7mrCJOso9pn8e_Bn1Ij7eqEcWamMlqMNozofrX4BcAA==&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
Archives
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N3oq0BCtMQQZG3_yTaZc8qZTosFtEsV8aRAvzwkcc5mSmhEZjHbzP4mfZQkwoqR0lHaPHzeg32qBv03_0LQ6iDZEGDm9hITOIu5BcKdjbfvQwM3y0-qEsiwFBym1HmaQ1bWQPBQGEPhLplJerBdjTU9EvS9pI6PVLP3l8w0iKGzA8onmqfx6iESkVLsYOJM0_w==&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N3oq0BCtMQQZCtS10kLac-0JtqD9P7DF1iVZe0TZ2N9QxMyws_eWJ8_DparSdRhplOTcVKTTwlpNmvWJLRkU9OGy7KysyDr2SANGZNfiqXLl6RuwqJf6WzNGd_2b4IolcSwgQCTMqjvs&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
July 20-31, 2015
Sold Out!
September 14-25, 2015
November 2-13, 2015
For additional details, register, or view upcoming training, visit the
AFSA Calendar [http://www.firesprinkler.org/events/].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
SA Cover for TU
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N-ieM_yFHmoYBrqvLBwIoTole7yXHzo0x-52wqxmeDjedDiYI4G5Dqcnj9f7EBRQriXXDXGPKHdWPIyhI0qLeiXPGXyfm3ZjRnzamJpWRJ8SxL_K3PPN0Hi-9wp7pnxntlp_KYy-JEHAx9qwcpxIVNWuQlqnNlhklA==&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
Free Subscription
to Sprinkler Age
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N3L-5_e5eb2F4725xMJVC4QCHtDFND0yPUBVSNmmVol2j7lBl_oIosv_Fiaocl2zT-pachFqrJv1bPB13SBBff_yZVVkq6c2TJMLKIBMyNy7if-_DskHzumF3npkd3IjrfkAd-Mrgnjym28cgSXM4N-FuOHLQwo3jw==&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition
[http://r20.rs6.net/tn.jsp?f=001NhouHNZ-69xri9rgE9hvDWvTOgvkJk9YpAPrRA4b6isuejC9tvH2N148H_-M0RZYu6vTB4gpy8bZvK9ucEdvPHTfNVEwoxDG8xOL5iLbJNYmhUNGbVp_gQTWof_RkPVzc1LmTCHywoAxzuB4_ULCyhyhKxg9Lfxd7dw4D2FdsQmARXzg9iijgKHnRKZlxy6fvl_tgihD_p_uUVQVi0J2fSwqF4x8Hc3hIpvMBPkGJ4xStisIkONHkXh1l-OaPmSE&c=WvGM-OjSgngTG78C6z6T5DBLQR_Nb84cialODIQ_zQ1HrQyDf6l2RQ==&ch=inkdy_MvvQllhAKlkCHj_0iqx2aulA4quyCSssnjYUw5URQ4bFboCA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1121328149332
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=09bc853d-97c2-417b-b76a-bd8b388a34fd
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=09bc853d-97c2-417b-b76a-bd8b388a34fd
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org