Ceiling Pocket Volumes

 

You have asked the following questions: “NFPA 13D limits the total volume of 
all unprotected ceiling pockets in a compartment to no more than 100 ft3 
whereas NFPA 13 is limited to 1,000 ft3.  Typically, NFPA 13 is more stringent. 
 Please confirm the above references are accurate and, if so, please explain 
the intent of the wide variation between the volumes.”  We have reviewed NFPA 
13, 2013 edition and NFPA 13D, 2013 edition as the applicable standards.  Our 
informal interpretation is that these volumes are as intended.

 

You’re right that NFPA 13 is typically a more stringent document but that 
primarily means that it provides a longer-lasting, more robust system along 
with the extent of protected areas to provide life safety and property 
protection.  It doesn’t mean that all aspects are more stringent.  Ceiling 
pockets are a good example.  The allowance for ceiling pockets was first added 
to NFPA 13 back in the 2002 edition based on fire modeling performed by AFSA.  
It was shown that large ceiling pockets (bigger than 1,000 ft3 and much deeper 
than 3 ft) could be unprotected, and the adjacent quick response (QR) 
sprinklers in the lower ceiling would activate at least as fast as a standard 
response sprinkler in a flat ceiling. The requirement for QR sprinklers in a 
light hazard occupancy was only added in the 1996 edition, so the acceptance of 
a standard response activation time was not an issue (keeping in mind that the 
reduction of the remote area for using QR sprinklers is not allowed). 

 

On the other hand, NFPA 13D’s use of residential sprinklers (as well of NFPA 13 
section 8.10) has always been based on a fast response element.  As such, they 
can’t tolerate a significant delay in activation times.  Considering that 
ceiling pockets have become a prevalent feature, it’s desirable that it’s 
addressed by the standards.  The technical committee accepted a proposal 
allowing 100 ft3   as a small enough volume to have minimal impact on the 
activation time.  Don’t forget that an indentation of no more than 12 inches is 
not considered a ceiling pocket.  NFPA 13 usually remains a more stringent 
standard, even with larger ceiling pockets. As stated in section 1.2.1, the 
purpose of NFPA 13 is to provide a reasonable degree of fire protection for 
both life and property.