Furniture as Partition Obstruction

 

You have asked the following question: “The owner has installed a desk in many 
of the units in a hotel. Top of the desk frame is 18.5 in. (or more) down from 
the ceiling and 8 ft-9 in. from sprinkler. We're protecting these units using 
extended-coverage sidewall sprinklers (14 ft x 26 ft coverage) in a 24 ft 6 in. 
room. Are furniture obstructions permitted?” In response to your question, we 
have reviewed NFPA 13, 2016 edition as the applicable standard. Our informal 
interpretation is that furniture is not typically viewed as obstructions to 
discharge.

 

Furniture is temporary and can be moved around. The furniture or desk does 
appear as a floor-mounted partition but would not create extensive shadowing. 
Table 8.9.5.2.2 indicates that when a floor-mounted obstruction is located more 
than 30 in. away, the minimum allowable distance below the deflector is 
18-inches, whereas 14.5-in. is provided above the desk. The desk unit would 
also be limited in width (approx. 5-ft to 6-ft wide) and would not span the 
entire width of the room. NFPA 13 does recognize that obstructions to sprinkler 
discharge are difficult to avoid and usually have very little impact on the 
sprinkler's ability to control a fire. A common example is the fact that 
sprinklers are not required under obstructions less than 4-ft wide illustrating 
that the entire floor is not always directly wetted. The primary question is 
will a fire in the room be controlled? Considering that the sprinkler discharge 
will not be cleanly cut-off at the corner (like a ray of light) due to the 
turbulent flow of the water droplets and that the floor area is small, this 
situation should not have a discernible impact upon activation of the sprinkler 
or its ability to quickly control a fire. This is of particular value since one 
of the main objectives of the sprinkler system is to keep the upper layer cool, 
thus preventing flashover and controlling the fire. In your scenario, the 
intent of NFPA 13 for providing protection throughout the area is satisfied 
without covering every square inch of floor area.