sprinklernotes
Pump Capacities and Supply Pipe Size

You have asked the following questions: “I am working on a project for a 
6-story hotel with 2 stairwells. As there will be a standpipe, in each 
stairwell the system demand should be 750 gpm (500 for the most remote 
standpipe and 250 for the 2nd). The civil drawings indicate a 4-inch fire line 
to the building. With a pump rating of 750 gpm, NFPA 20:4.14.3.4 states that 
within 10 pipe diameters of the suction flange, piping shall be a minimum of 6" 
(see Table 4.26(a)). I have calculated the system using 4-inch to 1'0 AFF and 6 
inch down the corridor to the fire pump room and it appears to work with a 
110-psi pump. My question is whether this is practical or if the 4-inch 
underground will be too restrictive when flowing the pump at 150% (1125 gpm). 
The engineer has suggested using a 500 gpm pump so the piping can remain 4 inch 
and the 150% point will be 750 gpm, however this is the system demand. 
Therefore, any degradation in the pump will cause it to be unable to meet 
system demand. Can the 4-inch underground remain, will 6-inch be required, or 
is it reliant on the hydraulic calculations?”

In response to your questions, we have reviewed NFPA 20, 2016 editions as the 
applicable standard. Our informal interpretation is you have asked multiple 
questions I’ll address them below

There are a couple of interrelated aspects to this question. The first is 
should you design to a 150 percent of the pump capacity? While NFPA 20 will 
allow you to design to 150 percent of the pump’s rating, they suggest you don’t 
exceed 140 percent. There is annex material that supports this in A.4.9 by 
stating, “The performance of the pump when applied at capacities over 140 
percent of rated capacity can be adversely affected by the suction conditions. 
Application of the pump at capacities less than 90 percent of the rated 
capacity is not recommended.” There is also handbook commentary that suggests 
selecting a pump so that the system demand falls between 90 percent and 140 
percent of rated capacity to ensure that the pump is not oversized and, 
conversely, is not operating at its maximum output. Using a pump with a rating 
of 750 gpm is appropriate for the situation you have described.

The next question is do you have to flow 150 percent of the pump capacity? 
During acceptance testing, you are not required to achieve 150 percent of the 
pump’s flow to pass the test. NFPA 20:14.2.6.2.4 allows testing below 150 
percent of the rated capacity, but it must be greater than either 100 percent 
of the rated flow or the maximum flow demand of the fire protection system 
served by the pump. Now, 14.2.6.2.4.1 states that the reduced capacity shall 
constitute an acceptable test, provided the pump exceeds the fire protection 
system design and flow rate. Additionally, NFPA 25 supports not having to test 
to 150 percent of the pump’s rating to prevent damage to the pump or 
underground supply. It states in section 8.3.3.1.1, “If available suction 
supplies do not allow flowing of 150 percent of the rated pump capacity, the 
fire pump shall be tested to the maximum allowable discharge.” So, you are not 
required to flow 150 percent of the pump rating. That value is simply guidance 
to the manufacturer on what the pump must be capable of providing.

The last question is whether it is acceptable to have a 4-in. supply main 
especially if that main does not support flowing 150 percent of the rated flow. 
We’ve already determined that you do not have to reach 150 percent of the rated 
flow, but it’s worth saying it applies regardless of the reason. The primary 
question on main size is whether it is allowed by NFPA 24. It is allowed as 
long as the main is not serving a fire hydrant(s), is serving only fire 
protection systems, and the size is supported with hydraulic calculations. It 
is worth noting that NFPA 13 points out it can be a combined main also 
providing domestic water and that water shall be included in the calculations 
when the main is less than a 4-in. diameter. So, you can have a 4-in. main. The 
last aspect is the 6-in. pipe size required by NFPA 20. As you already 
identified, this applies only to the portion of the pipe within 10 pipe 
diameters of the inlet to the pump. Beyond that point, it can any size allowed 
by the other driving standards.

In conclusion, the intent of the standards is that you use a 750-gpm pump (you 
could use a 500-gpm pump but you shouldn’t) and the 4-in. main is acceptable.

Reply via email to