Location of Residential Sprinklers with Beamed Ceilings—NFPA 13D

“In a room 25 ft x 25 ft and a flat ceiling with beams that are 8 in., 10 in., 
and 12 in. deep, can the sprinklers be placed on the bottom of the beam? The 
beam pockets are 4 ft x 4 ft. We are being told that this isn’t allowed by the 
ceiling pocket rule?”

We have reviewed NFPA 13D, 2016 edition that you indicated as the applicable 
standard. Our informal interpretation is that sprinklers are placed under the 
beams.

It is not an uncommon mistake to attempt to apply the ceiling pocket 
restrictions to beamed construction or to wood joist construction for that 
matter. This is understandable since the space between the structural members 
is literally a pocket. What they need to understand is that beam and joist 
assemblies are separately addressed as obstructed construction and ceiling 
pockets is an indentation in a smooth ceiling. This is better understood by 
those applying NFPA 13 where there is explicit criteria for obstructed 
construction. NFPA 13D, though, was historically applied to just smooth 
ceilings. Not long ago, if it was sloped, beamed, or pitched, NFPA 13D 
suggested increasing the density and/or increasing the number of sprinklers to 
be calculated. Then a residential sprinkler was listed for beamed ceilings but 
the only criterion in NFPA 13D was that the sprinkler must be listed for the 
ceiling configuration. The installation and design guidance for ceilings with 
beams was left up to the listing criteria and defined by the manufacturer’s 
data sheets. A significant change occurred with the 2013 edition when guidance 
on multiple configurations on beamed construction was added. In particular, 
paragraph 10.2.1(2) says:

“A flat, horizontal beamed ceiling, with a maximum ceiling height of 24 ft (7.3 
m), with beams up to 14 in. (355 mm) deep with pendent sprinklers under the 
beams. The compartment containing the beamed ceiling shall be a maximum of 600 
sq. ft. (55 m squared) in area. The highest sprinkler in the compartment shall 
be above all openings from the compartment into any communicating spaces.”

Just like in NFPA 13, we now have obstructed construction with its own 
criteria. The ceiling pocket criterion still exists but it applies just to what 
would otherwise be considered smooth construction. Also, just like in NFPA 13, 
this is not stated but assumed to be understood. The criterion is the same in 
the 2016 edition. As such, the ceiling pocket restrictions do not apply to 
beamed construction.

As for the placement of the sprinkler in relation to beams, it’s explicitly 
identified as being under the beam. As learned from the research project 
completed in 2010 (identified in NFPA 13D: 10.2), it’s interesting to note that 
the activation time of the sprinklers is adversely affected when they are 
located at the ceiling in small pockets.