sprinklernotes
Standpipes – Fire Hose Valve Connections on Roofs with Stair Access

“We have two stairs that can be used to access the roof. The other standpipe 
risers in the building do not penetrate to the roof level. On a roof with a 
slope less than 4:12, do the standpipes that do not have access to the roof 
need to extend to the roof level?”

We have reviewed the 2019 edition of NFPA 14 and the 2015 IBC as the applicable 
code and standard. Our informal interpretation is all standpipe risers do not 
have to penetrate to the roof level.

The fire hose valve connections provided for a stairway with access to a roof 
meet the intent of the standards. If the stairwells have roof access, both the 
IBC and NFPA 14 allow us to locate the connections at the highest landing in 
stairwells with roof access. The IBC states this in section 905.4 (5), and the 
text is very similar to NFPA 14 section 7.3.2.7. The understanding with this 
requirement is that the fire department will attach to the connection in the 
stairwell at the highest landing and carry the hose to the roof through the 
door or roof hatch to fight the fire. One of the reasons the standards are 
written this way is to avoid having to unnecessarily penetrate the roof 
membrane. If the roof were on fire, the fire department would not stand on the 
burning roof to connect to the connection risking injury or death. Now, if the 
stairwells did not have roof access, then NFPA section 7.3.2.9 would apply and 
require the connections to be provided on the roof.

Regarding the question on both stairwells supplying connections to serve the 
roof, section 7.3.2.7 of NFPA 14 states, “Hose connections shall be provided at 
the highest landing of stairways with stairway access to a roof.” The intent of 
the standard is to provide connections for use on the roof at all stairways 
with roof access. The confusion for supplying only one stairwell having roof 
access with hose connections comes from section 7.3.2.9 of NFPA 14. In closing, 
only one fire hose connection is required at the highest landing with all 
stairs that have roof access.

Reply via email to