sprinklernotes
Omission of Sprinklers in an Independent Care Residence of an Assisted Living 
Facility

You asked the following question: “Can sprinklers be omitted from bathrooms 
less than 55 sq ft in the independent living area of an assisted living 
facility based on the description provided above?” 

Our informal interpretation is that sprinklers are permitted to be omitted from 
these bathrooms.

NFPA 13 permits sprinklers to be omitted from bathrooms in dwelling units that 
do not exceed 55 sq. ft.

9.2.4.1 Bathrooms.

9.2.4.1.1* Unless sprinklers are required by 9.2.4.1.2 or 9.2.4.1.3, sprinklers 
shall not be required in bathrooms that are located within dwelling units, that 
do not exceed 55 ft2 (5.1 m2) in area, and that have walls and ceilings of 
noncombustible or limited-combustible materials with a 15-minute thermal 
barrier rating, including the walls and ceilings behind any shower enclosure or 
tub.

9.2.4.1.2 Sprinklers shall be required in bathrooms of limited care facilities 
and nursing homes, as defined in NFPA 101. 

In addition, occupancies defined as limited care facilities and nursing homes 
do not permit this omission. Per NFPA 101:

3.3.93.2* Limited Care Facility. A building or portion of a building used on a 
24-hour basis for the housing of four or more persons who are incapable of 
self-preservation because of age; physical limitations due to accident or 
illness; or limitations such as mental retardation/developmental disability, 
mental illness, or chemical dependency. (SAF-HEA)

3.3.148.2 Nursing Home. A building or portion of a building used on a 24-hour 
basis for the housing and nursing care of four or more persons who, because of 
mental or physical incapacity, might be unable to provide for their own needs 
and safety without the assistance of another person. (SAF-HEA) 

As described, the independent living portion of the project does not meet the 
definitions of limited care facility or nursing home above. As such, sprinklers 
should be permitted to be omitted in bathrooms less than 55 sq. ft. located 
within those dwelling units. It should be noted that NFPA 101-2018 does not 
require blanket classifications of occupancies. Portions of occupancies can be 
classified individually per section 6.1.1.1.

6.1.1.1 Occupancy Classification. The occupancy of a building or structure, or 
portion of a building or structure, shall be classified in accordance with 
6.1.2 through 6.1.13. Occupancy classification shall be subject to the ruling 
of the authority having jurisdiction where there is a question of proper 
classification in any individual case.

 

 

Reply via email to