sprinklernotes
Drum Drips in Freezers

You asked the following question: “We have a project where we are installing a 
dry system in a freezer. Is there a specific reference in the standard that 
would exempt the drum drips from being located inside freezers?”

In response to your question(s) below, we have reviewed NFPA 13, Standard for 
the Installation of Sprinkler Systems, 2019 edition. 

Our informal interpretation is that auxiliary drains are required to be 
installed on dry pipe systems per section 16.10.5.3. For trapped portions in 
excess of 5 gal, a drum drip would be required. The only additional provision 
for areas subject to freezing is that the drum drip has to be accessible per 
section 16.10.5.3.1.

For a dry system installed within a freezer, the chance that moisture would 
make it from the discharge of the air supply to a drum drip before freezing is 
minimal; however, the current prescriptive requirements dictate that a drum 
drip must be installed. With that being said, manufacturers such as AGF 
Manufacturing, Inc. make drains with insulated and heated enclosures to prevent 
freezing of the water to facilitate draining. AFSA technical staff has flagged 
this issue and intends to pursue a change for the 2025 edition of NFPA 13 to 
require the drain, but omit the drum drip assembly in areas that are maintained 
below 32 °F.

 

Reply via email to